sprinklernotes
Groove Couplings in Dry Systems

You have asked the following question: "What is the purpose for Section 6.5.3.2 
requiring a gasket listed for dry service in grooved couplings for dry 
systems?" In response to your question, we have reviewed NFPA 13, 2016 edition 
as the applicable standard. Our informal interpretation is gaskets listed for 
dry service are required due to potential failures of non-listed gaskets.

Section 6.5.3.2 does require gaskets listed for dry service in grooved 
couplings. This is because dry systems are traditionally exposed to extreme 
conditions, thus the gaskets need to be evaluated per UL 213, Standard for 
Safety: Rubber Gasketed Fittings for Fire-Protection Services, for their 
ability to hold air and water pressure. The gasket's ability to maintain three 
or four times their rated pressure (depending on the pipe size) for five 
minutes, degree of flexibility at a rated pressure, ability to maintain 40 psi 
when exposed to -40 degrees for 24 hours followed by 24 hours of ambient 
temperatures, ability to withstand fire conditions, and effects on friction 
loss are evaluated. The product data from different manufacturers state 
different materials are used in their grooved coupling gaskets for dry systems 
as well as lubricants that won't freeze at the lower temperatures. Manufacturer 
installation requirements should always be consulted and followed when 
installing these syst
ems. Being exposed to extreme cold could cause the gasket to become brittle and 
not keep the appropriate seal, allowing air and water to leak past the gasket. 
Air leaking could potentially cause enough drop in pressure to allow the dry 
valve to open and charge the piping, and in a system installed in areas subject 
to freezing could have drastic consequences. If the leak is not large enough to 
open the valve, it could potentially cause the air compressor to cycle more 
frequently to maintain the required air pressure causing it to fail 
prematurely. Another possible failure is during trip testing when water could 
potentially get behind the gasket and when the system is exposed to freezing 
temperatures the coupling could fail.