You have asked the following questions: "I have a noncombustible stair shaft, 
and the AHJ is requiring sprinklers under the stairs going from the first floor 
to the intermediate landing and also under the stairs going from the 
intermediate landing to the second-floor landing. This is in addition to the 
sprinkler under the first intermediate landing required by 8.15.3.2.1. Are the 
sprinklers under the stairs required? Would section 8.15.3.2.3 be considered in 
this situation? 8.15.3.2.1 does not say anything about sprinklers under 
stairs." In response to your question, we have reviewed NFPA 13, 2016 edition 
as the applicable standard. Our informal interpretation is that a sprinkler 
should be in one of the noted locations but not both.

The base requirement in Section 8.15.3.2 indicates that in noncombustible stair 
shafts having noncombustible stairs with noncombustible or limited-combustible 
finish sprinklers shall be installed at the top of the shaft and under the 
first accessible landing above the bottom of the shaft. The concern is the 
storage of materials in stairwells under the first landing or a large landing 
at the top of the stairs. As such, sprinklers are required at these locations. 
For stairs that have an intermediate landing, a sprinkler would be located 
under this landing. The area under the first intermediate landing is used quite 
often for storage. Some buildings provide walls or other types of barriers 
installed to prevent storage under the first landings where sprinkler 
protection would not be necessary. This is explicitly stated, starting with the 
2013 edition of NFPA 13, in section 8.15.3.2.3.1: Sprinklers shall be permitted 
to be omitted from the bottom of the stairwell when the space under the stairs 
at the bottom is blocked off so that storage cannot occur. In defining where to 
place the sprinklers, Section 8.15.3.2.3 explicitly says to sprinkler beneath 
the landings OR the stairways where the area can be used for storage. Beneath 
the stairways often require protection, but not in both locations provided the 
spacing limitations have not been exceeded to the wall under the landing. Even 
though a portion of the area beneath the landing may be shielded, it would not 
negatively affect the ability of the sprinkler in controlling a fire. NFPA 13 
allows shadowing of the sprinkler discharge, and with a single sprinkler 
operating you will have an over-discharging situation due to the excess 
pressure available. Additionally, with the sprinkler over-discharging, you will 
have water that could reach the shadowed areas due to bouncing off the other 
surfaces in the area reaching the fire indirectly.