sprinklernotes
Pipe Size for a Hose Valve Located on the Roof


You have asked the following question: “What size piping and control valve are 
required to supply a single 2½ in. hose connection on the roof to be installed 
per Sections 7.3.2.9 and 7.3.2.9.2.1? Section 7.6.1 requires standpipes to be 
at least 4 in. but Section 7.6.3 requires branch lines to be not smaller than 
2½ in.” In response to your question, we have reviewed NFPA 14, 2016 edition as 
the applicable standard. Our informal interpretation is the piping and control 
valve for a roof hose connection are to be 4 in.

Even though this is not explicitly stated in Section 7.3.2.9, the piping and 
control valve for a roof hose connection are still part of the main line and 
are to be at least 4 in. This is stated in Section A.7.3.2.7 and shown in 
Figure A.7.3.2.7. For vertical standpipes, branch lines are typically 
horizontal piping from the vertical standpipe not serving more than one hose 
connection. The purpose of a branch line on a vertical standpipe system is to 
meet the travel distance requirement when it is not practical to install an 
additional standpipe and can be covered by one additional hose connection. In 
this instance the hose connection on the roof is not an additional hose 
connection being installed to meet the travel distance requirement, thus the 
piping and control valve are required to be at least 4 in.