sprinklernotes
Combustible Concealed Spaces and the 3000 sq. ft. Design Area Increase



You asked the following question: “Can you use the 3,000 sq. ft. design area to 
omit sprinklers in the concealed space in between floors on a hotel that is 5 
stories? There are no fire/smoke barriers and no insulation. The attic will be 
sprinklered. The floors are constructed of open web wood trusses.” In response 
to your question, we have reviewed NFPA 13, 2016 edition as the applicable 
standard. Our informal interpretation is a 3,000 sq. ft. design area cannot be 
used to omit sprinklers from a concealed space.

The 3,000 sq. ft. design area per Section 11.2.3.1.5.2 cannot be used to omit 
sprinklers from concealed spaces. This is because a design area is required to 
be increased to 3,000 sq. ft. in certain circumstances due to the omission of 
sprinklers in combustible concealed spaces. This is stated in Section 
11.2.3.1.5.1:
When using the density/area or room design method, unless the requirements of 
11.2.3.1.5.2 are met for buildings having unsprinklered combustible concealed 
spaces, as described in 8.15.1.2 and 8.15.6, the minimum area of sprinkler 
operation for that portion of the building shall be 3000 ft2 (280 m2 ).
This is also explicitly stated in the commentary for Section 11.2.3.1.5.1 in 
the NFPA 13 Handbook. The NFPA 13 Handbook commentary states: “The intention of 
11.2.3.1.5.1 is not to permit the omission of sprinklers from combustible 
concealed spaces but, rather, to compensate for the anticipated delay of 
sprinkler operation for a fire originating in an unprotected, combustible 
concealed space. As noted, 8.15.1.2 describes the conditions under which 
sprinklers do not have to be installed in concealed spaces.” Hence, before it 
can be determined if the 3,000 sq. ft. design area is required by Section 
11.2.3.1.5.2 we have to start by determining if sprinklers can be omitted in 
the combustible concealed space, and for that we need to look at Section 
8.15.1.1:
Concealed spaces of exposed combustible construction shall be protected by 
sprinklers except in concealed spaces where sprinklers are not required to be 
installed by 8.15.1.2.1 through 8.15.1.2.18 and 8.15.6.
Section 8.15.1.2 provides 18 conditions as subsections where sprinklers can be 
omitted. Only one of the 18 conditions from Section 8.15.1.2 has to be met to 
omit sprinkler. If Section 8.15.1.2 is met, at this point we can go back to 
Section 11.2.3.1.5.1 to determine if a larger remote area can be avoided. From 
here we have look at Section 11.2.3.1.5.2 to see if we can avoid the penalty of 
increasing the design area for not sprinklering the combustible concealed 
space. Section 11.2.3.1.5.2 give us 10 conditions where we are not required to 
increase the design area. If any of the listed conditions are met the penalty 
can be avoided. There are no situations in Section 8.15.1.2 for this 
arrangement that we can apply with the information provided. Now if you had 
qualified to omit sprinklers, Section 11.2.3.1.5.2 would have applied and could 
force you to pay the penalty of larger design areas on multiple floors if rated 
construction is not provided.

Again, the intention of 11.2.3.1.5.1 is not to permit the omission of 
sprinklers from combustible concealed spaces. Rather, it is to compensate for 
the anticipated delay of sprinkler operation for a fire originating in an 
unprotected, combustible concealed space as well as the potential for the fire 
to break-out in multiple locations.


Reply via email to