sprinklernotes
Area Limitations for Standpipe Systems

You have asked the following question: “The state fire marshal is asking us to 
add an additional system riser in the fire pump room due to the first floor 
being 54,000 sq. ft. Our current arrangement consists of one 6 in. feed main 
coming out of the pump room and feeding four vertical standpipes in the 
stairwells with two zone control assemblies feeding approximately half of the 
building each. We are identifying the zone assemblies as our system risers, not 
the feed main coming from the pump room. Would we need to split the standpipe 
system into areas less than 52,000 sq. ft. by splitting up the standpipe feed 
main into two separate mains in the pump room?” In response to your question, 
we have reviewed NFPA 14, 2016 edition as the applicable standard. Our informal 
interpretation is the single feed main is an acceptable arrangement.

Typically, the system size for standpipes is only limited by the building’s 
footprint. NFPA 14 places no limits to a supply pipe supplying standpipe system 
unless the standpipe systems is dry automatic or semi-automatic where the 
volume controlled by one dry pipe valve cannot exceed 750 gallons per Section 
5.2.1.2.1. Now, Sections 7.10.1.1.3 and 7.10.1.1.3.1 will require adding demand 
per each standpipe to the calculations depending on whether the floor area of 
the building does or does not exceed 80,000 sq. ft. With that being said, 
nowhere does it require additional supply or feed mains for the standpipe 
system to be broken into areas smaller than 52,000 sq. ft. The area limitation 
of 52,000 sq. ft. comes is from NFPA 13 and is a requirement for sprinkler 
systems only.