sprinklernotes
Sprinkler Requirements for Mechanical Enclosures

 

 

You asked the following questions: “Mechanical enclosure. Is a sprinkler head 
required within a non-combustible concealed space that has an HVAC unit inside 
of it? The concealed space has an access panel and the space is not intended 
for occupancy. Is this considered a mechanical enclosure, or would this be 
considered a non-combustible Concealed Space or both?” In response to your 
question, we have reviewed NFPA 13, 2016 edition as the applicable standard. 
Our informal interpretation is sprinkler protection would not be required 
within the concealed space.

 

The main concern here is the area considered a concealed space or a mechanical 
equipment closet. Since there is an access panel, which traditionally requires 
screws to be removed to open, instead of a side-hinging door, the area is a 
concealed space. With the area being a concealed space, Section 8.15.1.2.2 can 
be reviewed to determine if sprinkler protection can be omitted. Section 
8.15.1.2.2 states: Concealed spaces of noncombustible and limited-combustible 
construction with limited access and not permitting occupancy or storage of 
combustibles shall not require sprinkler protection. The concealed space is 
built of noncombustible construction and has limited access; thus, sprinkler 
protection can be omitted.