Insulation on Combustible Upper Surfaces

“We have a horizontal concealed space above the ceiling with a wood upper 
surface and 2x6 in. wood joists. The joists are filled with noncombustible 
insulation. It is less than 36 inches between the deck and the ceiling. The 
materials below the joists are limited or noncombustible. Am I required to use 
sprinklers listed for a horizontal concealed space?”

We have reviewed the 2016 edition of NFPA 13, Standard for the Installation of 
Sprinkler Systems, you indicated as the applicable standards. Our informal 
interpretation is that standard spray sprinklers can be used.

Technically, this space is not required to be protected per section 
8.15.1.2.17. The insulation is an acceptable covering for the wood material 
negating it being classified as “exposed” combustible construction. In other 
words, the insulation is considered the outer boundary of the assembly. I 
understand that this jurisdiction still requires such spaces to be protected. 
This leaves the question as to whether sprinklers are listed for horizontal 
spaces per section 8.15.1.6. This section requires a special listing when three 
conditions exist. These are:

(1) a shallow concealed space less than 36 inches in depth,

(2) the space is horizontal (slope not exceeding 2 in 12), and

(3) a combustible upper surface.

All three conditions have to be present (just like the attic requirements in 
section 8.6.4.1.4). Although the upper deck is wood construction, it is not the 
upper surface. That would be the insulation. Although it is a different 
allowance, section 8.15.1.2.17 explicitly defines insulation as an acceptable 
covering, removing the wood from the evaluation. Since all three conditions do 
not exist, the requirement to use sprinklers listed for shallow combustible 
concealed spaces does not apply. As such, standard spray sprinklers can be used 
to protect this shallow concealed space. However, while not required, it would 
be appropriate to use a sprinkler listed for concealed spaces as the sprinkler 
discharge characteristics are specifically designed to protect narrow spaces. 
This should be discussed with the local AHJ to determine a proper course of 
action with which o proceed.