“Our local AHJ has recently told us that bushings are not allowed to be 
installed on the outlet of the branchline where the fire sprinkler is 
connected. I feel that he is confused the way he is interpreting the code: NFPA 
13 2010 edition 6.4.6. The term "not available" in 6.4.6.2 he stated does not 
make sense since 1" x 1/2" or 1" x 3/4" reducers should always be available. 
Does this rule apply to bushings to connect a fire sprinkler to a branchline or 
only to bushings used to reduce pipe sizes on the run of the branchline?” 

We have reviewed NFPA 13, Standard for the Installation of Sprinkler Systems, 
2010 edition as the applicable standard.  Our informal interpretation is the 
use of bushings is allowed.

Sections 6.4.6 and 8.15.9 govern the use of bushings. One-piece reducing 
fittings are required for pipe changes except when standard fittings are not 
readily available or new installations are expected to potentially supply 
sprinklers below a ceiling. For these installations, bushings are allowed, as 
indicated by the third bullet point in the “Coffee Break Training” document 
that was included in your email. The primary issue is a concern about leaks, 
since the number of threaded connections is increased. It is also recognized 
that it is desirable for ease of modification to allow bushings when a system 
is installed prior to the finish work where the area and ceilings are expected 
to be installed. The term “expected” was intentionally used to reflect it 
recognized that the plans for areas can change, particularly for leased 
buildings. This exception is expected to be applied to an entire floor. If, 
after the system is installed, a portion of the floor is identified as not 
receiving a drop ceiling, the standard does not require the bushings to be 
removed. Actually, if there is a potential for the area to change hands, such 
as a lease, one could still expect a ceiling to be installed. Starting with the 
2007 edition, section 8.15.19.2 was changed to reflect that bushings are not 
only acceptable but beneficial in regard to allowing future modifications. This 
allowance is not predicated upon the presence of a drop ceiling. It’s worth 
noting these requirements have remained unchanged for the 2013 through 2019 
editions of the NFPA 13.