Narrow Ceiling Pockets

 

You asked the following question: “We have a ceiling pocket at the edge of the 
room that contains the drapes for the exterior windows. It very narrow (only 1 
ft) and well below the 1,000 ft3, but the depth is 3 ft 5 in. Are sprinklers 
required within this pocket?”

 

We have reviewed NFPA 13 Standard for the Installation of Sprinkler Systems, 
2016 edition as the applicable standard. Our informal interpretation is that 
sprinkler should not be required.

 

While a literal interpretation of the standard would require sprinklers to be 
installed because the depth exceeds 3 ft, that is not the intent of the 
standard. A standard ceiling pocket captures the entire fire plume and delays 
the activation of sprinklers installed below. AFSA did the fire modeling that 
the criteria are based on and that study told us that a much deeper pocket will 
still provide acceptable activation times, but the committee was uncomfortable 
with accepting pockets with larger depths. An arbitrarily maximum depth of 3 ft 
was assigned. Slightly exceeding 3 ft will not affect the performance. The 
pocket will actually have the same impact on the heat flow as a skylight. We 
ignore skylights because the air within them is heated by the sun, and the 
buoyancy of the pre-heated air will limit the amount of smoke that will 
actually make it into the skylight – this is why deflector distances are 
measured to the imaginary plane at the bottom of the skylight and not up to the 
glass or plastic cover at the top.

 

Since this allowance is not explicitly identified in the standard, it should be 
discussed with the local AHJ and a written agreement with this interpretation 
should be obtained before proceeding further with the project.