sprinklernotes
Spacing Deviations with ESFR Sprinklers

 

You asked the following question: “When designing an ESFR system for a building 
of beam and girder construction where the solid roof beams are spaced at 30 ft 
6 in. with 9-in. deep purlins and a maximum roof elevation of 45 ft, is it 
allowable to apply the “shift rule” by spacing the branch lines at 10 ft 2 in. 
intervals within each bay while spacing the sprinklers along the branch lines 
at 9 ft 10 in.; maintaining a maximum 100 ft² coverage?”

In response to your question, we have reviewed NFPA 13, Standard for the 
Installation of Sprinkler Systems, 2019 edition. Our informal interpretation is 
that the proposed arrangement would not be permitted.  

While the exact arrangement proposed would not be permitted per the 
installation standard or the sprinkler’s listing, there are other options that 
would minimize the necessary revisions to the design of the sprinkler system.

The “shift rule” refers to the requirements of sections 14.2.8.2.3 and 
14.2.8.2.4 in NFPA 13 and permits the maximum spacing requirements to be 
exceeded. In this case, since the ceiling height exceeds 30 ft, ESFR sprinklers 
are limited to 10-ft spacing before applying the “shift rule.” 

14.2.8.2.3* Deviations from the maximum sprinkler spacing shall be permitted to 
eliminate obstructions created by structural elements (such as trusses, bar 
joists, and wind bracing) by moving a sprinkler along the branch line a maximum 
of 1 ft (300 mm) from its allowable spacing, provided coverage for that 
sprinkler does not exceed 110 ft2 (10 m2) per sprinkler where all of the 
following conditions are met:
(1)  The average actual floor area protected by the moved sprinkler and the 
adjacent sprinklers shall not exceed 100 ft2 (9 m2).

(2)  Adjacent branch lines shall maintain the same pattern.

(3)  In no case shall the distance between sprinklers exceed 12 ft (3.7 m).
14.2.8.2.4 Deviations from the maximum sprinkler spacing shall be permitted to 
eliminate obstructions created by structural elements (such as trusses, bar 
joists, and wind bracing) by moving a single branch line a maximum of 1 ft (300 
mm) from its allowable spacing, provided coverage for the sprinklers on that 
branch line and the sprinklers on the branch line it is moving away from does 
not exceed 110 ft2 (10 m2) per sprinkler where all of the following conditions 
are met:
(1)  The average actual floor area protected by the sprinklers on the moved 
branch line and the sprinklers on the adjacent branch lines shall not exceed 
100 ft2 (9 m2).

(2)  In no case shall the distance between sprinklers exceed 12 ft (3.7 m).

(3)  It shall not be permitted to move a branch line where there are moved 
sprinklers on a branch line that exceed the maximum sprinkler spacing. 

While the provisions of sections 14.2.8.2.3 and 14.2.8.2.4 permit sprinklers 
and branch lines to be shifted 1 ft, the application of the rules only allows 
for a single sprinkler or a single branch line to be moved. Since this is the 
case, having all of the branch lines spaced at 10 ft 2 in. would not be 
acceptable. To conform with the requirements of these two sections, a single 
branch line may be spaced at 10 ft 6 in. with the other two spaced at 10 ft to 
cover the 30 ft 6 in. bay. The spacing of the sprinklers along the branch line 
would have to maintain maximum spacing requirements. The proposed 9 ft 10 in. 
spacing would be allowed as the area of coverage on the 10 ft 6 in. branch line 
does not exceed 110 ft2.

Another issue with this proposed spacing deviation is that it does not conform 
with the charging language of sections referenced above. Both section 
14.2.8.2.3 and 14.2.8.2.4 premise their requirement by stating that the intent 
of the provision is “to eliminate obstructions created by structural elements.” 
Again, that is not the case for this installation as the lines are being 
shifted to provide coverage for the bay.

In a footnote to the maximum spacing requirements of Table 10.2.4.2.1(c), 
standard spray uprights and pendants maximum spacing requirements are permitted 
to be exceeded in 25 ft bays so that an additional branch line is not required 
to be installed: 

*In buildings where solid structural members create bays up to 25 ft (7.6 m) 
wide, maximum spacing between sprinklers is permitted up to 12 ft 6 in. (3.8 m).

While this note is not applicable to ESFR sprinklers, a case could be made that 
the basis for this allowance for extra hazard occupancies should also be 
considered for ESFR sprinklers to eliminate the need for a fourth branch line 
to be installed in this bay that exceeds 30 ft by a small margin.

Notwithstanding the arguments of this interpretation, the sprinkler must still 
be installed per its listing and the manufacturer’s recommendations. It is 
suggested that this deviation is discussed with the specific sprinkler 
manufacturer as ESFR sprinkler requirements are derived from specific fire 
modeling and full-scale testing. If acceptable to the sprinkler manufacturer, 
the deviation should then be approved by the AHJ prior to install.

 