Calculating ESFR Sprinklers Located Below Obstructions

You asked the following question: “Is it required to calculate up to fourteen 
(14) ESFR sprinklers when ESFR sprinklers are added below a continuous 
obstructions?”

In response to your question(s) below, we have reviewed NFPA 13, Standard for 
the Installation of Sprinkler Systems, 2019 edition and have answered each 
question individually. 

Our informal interpretation is only twelve (12) ESFR sprinklers are required to 
be calculated.

27.4.4.4 ESFR Sprinkler Method. For ESFR sprinklers, the design area shall 
consist of the most hydraulically demanding area of 12 sprinklers, consisting 
of four sprinklers on each of three branch lines, unless other specific numbers 
of design sprinklers are required in other sections of this standard.

The 2010 edition of NFPA 13 previously required an additional two ESFR 
sprinklers to be calculated under the obstruction in section 22.4.4.6.4.1; 
however, ESFR design criteria is based on FM Global testing data. During the 
revision cycle for the 2013 edition of NFPA 13, FM informed the committee that 
they do not include the additional two sprinklers in their fire test and the 
committee removed the requirement from the standard. ESFR systems have only 
required a twelve-sprinkler calculation since the 2013 edition. This 
requirement was also removed from corresponding sections 14.4.4, 15.4.4, 
16.3.3.6, 16.2.3.5, 17.3.3.5, and 17.2.3.4. It should be noted the FM pass/fail 
criteria for storage sprinklers allows 6 sprinklers to activate. The 12 
sprinkler calculation is an added safety factor.

 

 