NFPA 13D Domestic Demand 

You asked the following question: “NFPA 13D-2016 section 6.5.2 requires a 5-gpm 
allowance to be added to the hydraulic calculation when the water supply serves 
multiple dwelling units and the fire protection water is not separate from the 
domestic. On this project there are seven townhouses attached to a common 
combined (fire/domestic) 1-1/2 in. shared main. Is the requirement to add 5 gpm 
to each building individually or a cumulative 35 gpm for all seven buildings 
required?” 

In response to your question, we have reviewed NFPA 13D, Standard for the 
Installation of Sprinkler Systems in One- and Two-Family Dwellings and 
Manufactured Homes, 2019 edition.

Our informal interpretation is that the 5-gpm demand needs to be added at each 
connection to the common water supply accounting for incidental domestic use 
during a fire event in one of the townhomes.  





Per section 6.5.2:
6.5.2 In common water supply connections serving more than one dwelling unit, 5 
gpm shall be added to the sprinkler system demand to determine the size of the 
common piping and the size of the total water supply requirements where no 
provision is made to prevent flow into the domestic water system upon operation 
of a sprinkler.

This principle was first introduced in the 1996 edition of NFPA 13D with the 
acceptance of public input 13D-7. In their statement, the committee said, “If 
NFPA 13D is used in a multi-family environment, then the 5-gpm flow should be 
added in at each additional point of connection.” The committee stated “each 
additional point of connection” in their statement!

For one- and two-family homes, this would constitute a 5-gpm allowance and 
limit; however, the standard did not consider townhomes (many one-family homes 
grouped together) and their shared infrastructure. A single domestic fixture 
can use up to 5 gpm and it would be difficult to halt domestic use in adjacent 
units as they might not even be aware of the fire in another unit – NFPA 13 
does not require an alarm. For the 2025 edition of NFPA 13D, AFSA intends to 
submit public input to the residential committee to address the ambiguities in 
this requirement.