With UPS you have to consider both the power consumption in standby mode and in 
operational mode.  Typically, though, unless you have a generator, you won’t 
have any HVAC running when the UPS is in operational mode (and if you have a 
generator, your equipment shouldn’t be running off the UPS) so that probably 
won’t be a factor for most schools.   Related to UPS you also need to factor in 
any PDU’s – again for most school settings this would be negligible, but they 
do generate a slight amount of heat.  If you have a system that also provides 
line conditioning, that, too will generate extra heat.   I saw a formula – I 
think from APC – for calculating the power/heat load from UPS/Power 
conditioning equipment.

Higher voltage is slightly more efficient, but again, in a typical school 
environment the difference would be negligible.  A central DC feed is, indeed, 
more efficient in a data center because it eliminates the need to convert power 
individually in each piece of equipment.  Each power supply consumes power in 
the process of conversion, thus generating more heat – directly fed DC 
eliminates the need for these extra power supplies.  I have not seen too many 
servers of the type used by schools that have this option, but the Cisco gear 
has had the option for DC power for quite a while.

If truly trying to get as accurate as possible, you can also subtract any power 
used by PoE devices from the cooling load since the heat is dissipated by the 
device which is most likely outside of the data center.  Based on current PoE 
specs, this would typically be anywhere from 1W per device to 15W per device.

One other thing… if the electrical engineers decide to put step down 
transformers inside the data center, you will have a whole lot more heat to 
dissipate.  We were fortunate enough to have that happen in two of our network 
closets.

If you want to go with the most efficient design, localized cooling inside the 
rack with exterior venting is the best option (if you have the design 
flexibility).

-TS

From: tech-geeks-boun...@tech-geeks.org 
[mailto:tech-geeks-boun...@tech-geeks.org] On Behalf Of Jim Flanagan
Sent: Saturday, October 02, 2010 11:02 AM
To: Tech-Geeks Mailing List
Cc: Tech-Geeks Mailing List
Subject: Re: [tech-geeks] Server Heat Load

Also, don't forget the UPS's.

And, if doing a big server room, other's more knowledgable please correct me, 
but aren't their advantages to be had in minimizing heat Load by looking 
closely at how you power everything.

I don't remember the details but 110AC I think is the least efficient. One one 
end 220V and at the other DC, although I guess DC is bleeding edge.

This site looks really useful for reference materials and design tools

http://www.thegreengrid.org/library-and-tools.aspx

Jim



Sent from my iPad
Cell 773.396.4638
Chicago 773.463.5494
Beaver Island 231.448.2109

Privacy Notice:  The information contained in this electronic message is 
intended only for the use of the individual or entity to which it is addressed. 
 This message is private and may contain information that is privileged, 
confidential and/or inside information and exempt from disclosure under 
applicable law.  If you are not the intended recipient, you are notified that 
any dissemination, distribution or copying of this communication is strictly 
prohibited. Please contact the sender by reply e-mail and destroy all copies of 
the original message

On Oct 2, 2010, at 9:41 AM, "Steele, Thomas C" 
<tste...@manteno5.org<mailto:tste...@manteno5.org>> wrote:
We had to do this during our 2007 construction project.  You could get 
extremely technical, but for the most part a simple calculation will be 
sufficient.


1)      Add up the total rated watts drawn by all IT equipment (servers, 
switches, etc).  If the wattage is not given, multiply the Amps x Volts (i.e. 
if it is rated at 2A at 120V, multiply 2 x 120, resulting in a power draw of 
240W)

2)      Multiply the total watts by 3.41 to arrive at the total BTUs/hr 
generated by the tech equipment

3)      To convert to tons, divide the total BTU’s by 12000

4)      This represents the ADDITIONAL cooling required by the IT equipment 
above and beyond what would otherwise be required for the room.

You might be shocked by the results.  It turns out I have more cooling in our 
8x10 server room than I have in my whole house!   Also, when doing your 
calculations, try to anticipate future needs.  A rack full of 1RU servers will 
generate a whole lot more heat than a rack of 5RU servers so consider what you 
*might* eventually have in the room.  On a related note, if you have to size AC 
for a computer lab, follow the same formula, but add an additional 100W per 
person to compensate for additional body heat – this is something most 
architects/engineers seem to overlook when designing labs.  It cracks me up 
when I see people trying to “cool” their labs using 5000BTU window air 
conditioners – do the math!

Thomas C. Steele
Technology Director
Manteno CUSD #5
250 N Poplar
Manteno, IL 60950
ph: (815)928-7006  fx: (815)468-6439



From: 
tech-geeks-boun...@tech-geeks.org<mailto:tech-geeks-boun...@tech-geeks.org> 
[mailto:tech-geeks-boun...@tech-geeks.org] On Behalf Of Egolf, Ron
Sent: Saturday, October 02, 2010 8:46 AM
To: tech-geeks@tech-geeks.org<mailto:tech-geeks@tech-geeks.org>
Cc: Richard Mann
Subject: Re: [tech-geeks] Server Heat Load

ICN had to do this when we started racking up the LTC cloud.  Give Ben or Rich 
an email call.


On 10/1/10 11:16 AM, "Eric Roemer" 
<roem...@woodland5.org<mailto:roem...@woodland5.org>> wrote:
Anyone ever had to calculate the heat load for your server room? We are in need 
of upgrading the cooling system in our server room and our AC vendor has asked 
me to get him the heat load from my servers. I have 10 servers in the server 
room. Any info on getting a quick, usable estimate of the heat load of the 
servers would be very helpful.

Thanks!
Eric

THIS TRANSMISSION IS INTENDED AND RESTRICTED FOR USE BY THE ABOVE ADDRESSEE 
ONLY. IT MAY CONTAIN CONFIDENTIAL AND/OR PRIVILEGED INFORMATION EXEMPT FROM 
DISCLOSURE UNDER FEDERAL OR STATE LAW. IN THE EVENT SOME OTHER PERSON OR ENTITY 
RECEIVES THIS TRANSMISSION, SAID RECIPIENT IS HEREBY NOTIFIED THAT ANY 
DISSEMINATION, DISTRIBUTION, OR DUPLICATION OF THIS TRANSMISSION OR ITS 
CONTENTS IS PROHIBITED. IF YOU SHOULD RECEIVE THIS TRANSMISSION IN ERROR, 
PLEASE CALL WOODLAND CUSD#5 IMMEDIATELY AT 815-672-5974, DELETE THE FILE FROM 
YOUR SYSTEM, AND DESTROY ANY HARD COPIES OF THIS TRANSMISSION. THANK YOU.

THIS TRANSMISSION IS INTENDED AND RESTRICTED FOR USE BY THE ABOVE ADDRESSEE 
ONLY. IT MAY CONTAIN CONFIDENTIAL AND/OR PRIVILEGED INFORMATION EXEMPT FROM 
DISCLOSURE UNDER FEDERAL OR STATE LAW.
IN THE EVENT SOME OTHER PERSON OR ENTITY RECEIVES THIS TRANSMISSION, SAID 
RECIPIENT IS HEREBY NOTIFIED THAT ANY DISSEMINATION, DISTRIBUTION, OR 
DUPLICATION OF THIS TRANSMISSION OR ITS CONTENTS IS PROHIBITED.
IF YOU SHOULD RECEIVE THIS TRANSMISSION IN ERROR, PLEASE CALL WOODLAND CUSD#5 
IMMEDIATELY AT 815-672-5974, DELETE THE FILE FROM YOUR SYSTEM, AND DESTROY ANY 
HARD COPIES OF THIS TRANSMISSION.
THANK YOU.
| Subscription info at http://www.tech-geeks.org |
| Subscription info at http://www.tech-geeks.org |
| Subscription info at http://www.tech-geeks.org |

Reply via email to