Unless all of your ground rods are bonded together, you are inviting disaster.

If you have two ground systems, one at the tower and the other at the house, you have a very dangerous situation.

If you have a unified (bonded) ground system and take a lightning strike every thing elevates to to same level, be it 10 Volts or 100 KV. There is no difference in potential between equipments and everything is happy. If there are two ground systems, they will not elevate to the same level at the same rate. In this case, you have differences in potential between equipments and damage.


MIL-HDBL-419 is a very good grounding reference and is available for free download.

To do the grounding correctly, all connections exterior to the building are to be welded.
The cable to ground rod welds are to be 18 inches below grade.
The exterior cable is to be number 2 copper or larger.
To bond numerous ground systems together, a number 2 copper cable is to be buried at 18 inches and welded to each ground system. If using eight foot ground rods, a ground rod is to be driven every 16 feet along the connecting cable and the cable welded to the rod.

I did lightning mitigation for seven years for a tower site monitoring company. When these steps were followed, lightning damage was very minimal or non-existent.

You stated that the GPS antenna was on a tower.
To correctly install an antenna on a tower the feedline is to be bonded to the tower near the base of the antenna. The feedline is again bonded to the tower where to leaves the tower heading for the building. Prior to entering the building, the feedline is bonded to a copper plate called a ground window.
This ground window is bonded to the ground system.
The feedline goes through a surge suppressor the is bonded to the ground window prior to entering the building.

All equipment in the building should be bonded to a ground buss made of number 6 copper and bonded to the ground window.

A lot of work, but, cheaper, in the long run, than continuing to repair/replace equipment.

73
Glenn
WB4UIV




On 6/18/2018 2:29 PM, Dan Kemppainen wrote:
Hi,

I have (or had, I guess) a GPS antenna on a tower that took a lightning hit yesterday.

You can tell it's going to be a bad day when you walk into your shop, and smell burnt electronics. Still have to troubleshoot exactly what got hit, but the GPSDO was flashing no GPS signal, the 5V supply for the antenna to the GPS splitter was dead, the data logging computer had rebooted and the data logging computer monitor was dead. Other network hardware was dead also.

This is a bit surprising since the tower itself is grounded with 4 ground rods and bonded to a 150 foot deep well casing near by. The antenna is on the end of 250 ft run of RG6. The GPS antenna cable shield has a grounding block bonded to two ground rods driven down below the basement foundation where it enters the house. I'm guessing the surge ran the coax into the splitter, then through everything connected to it, despite the grounding block.

So, I'm wondering if there are better surge protectors for lightning protection? Maybe something that actually protect the center conductor also? Hopefully something that will pass GPS signal reasonably and let DC power through. If so, can you recommend some starting points? Other suggestions also welcome.


Also, If you are considering upgrading your own lightning protection, hopefully this will be some inspiration to get started. As I said earlier, it's a bad day when you smell burnt electronics in the shop.

Thanks,
Dan

_______________________________________________
time-nuts mailing list -- [email protected]
To unsubscribe, go to https://lists.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


--
-----------------------------------------------------------------------
Glenn Little                ARRL Technical Specialist   QCWA  LM 28417
Amateur Callsign:  WB4UIV            [email protected]    AMSAT LM 2178
QTH:  Goose Creek, SC USA (EM92xx)  USSVI LM   NRA LM   SBE ARRL TAPR
"It is not the class of license that the Amateur holds but the class
of the Amateur that holds the license"

_______________________________________________
time-nuts mailing list -- [email protected]
To unsubscribe, go to https://lists.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

Reply via email to