Hal Murray writes:

> I'd expect an ADEV type pattern.  For long tau, the wander in the system will 
> dominate.  We have lots of long term data so should be able to plot that part 
> of the graph.

I did that some years ago:  The Nordic grid bottomed out around 1e-10, with
a frequency error less than 2e-11 measured over 45 years.

> How much energy is in the rotating turbine and generator?  That should 
> provide 
> a lower limit on the time constant of the control loop.

Answer A: Surprisningly much (do the math on 50 tons of iron, 1m diameter at 
3000 or 3600 RPM)

Answer B: Not enough to keep modern grids stable (Google term: "Low inertia 
conditions")

-- 
Poul-Henning Kamp       | UNIX since Zilog Zeus 3.20
p...@freebsd.org         | TCP/IP since RFC 956
FreeBSD committer       | BSD since 4.3-tahoe    
Never attribute to malice what can adequately be explained by incompetence.