Michael Royer wrote:
> Doug,
> Part 68 makes no minimum clearance.
> UL 1950 3rd edition requires clearances much greater than what you have
> written.  The path to your exact clearance is complicated, and there are
> exceptions for permanently earth grounded hosts and pluggable type B 
> equipment.
>  These exceptions are often used by rack mounted commercial gear.
> 
> For most PCB's UL 1950 requires creepage and clearance of 2mm = 0.079" T-G,
> R-G, T-GSELV, R-GSELV.
> 
> Michael Royer
> Senior Agency Compliance Engineer
> BABT Approvals Liaison Engineer
> N.E.T.  (Network Equipment Technologies)
> 800 Saginaw Drive
> Redwood City, CA 94063
> Voice: 415-780-4218
> Fax:     415-780-5004
> [email protected]

Ouch!  Thanks Michael.  

That makes sense now. 
I've done creepage calculations by using 3M volts = 1 meter for air breakdown. 
Therefore, 3,000V = 1mm, or, 1mm = roughly 0.040".
To be doubly safe, 2mm = roughly 0.080" through air!

Funny how that science stuff works. 

*******************************************************
Doug McKean
[email protected]
-------------------------------------------------------