Joe, If you use Amendment 4 of IEC 950, and fall into the TNV-1 category, you can use operational insulation and a dielectric test between SELV and TNV. Of course amendment 4 is not universally accepted (i.e. Australia), but UL will allow the TNV 1 conditions when evaluating to UL-1950 3rd Edition.
Jim ---------- From: treg-approval To: treg Subject: IEC 950 / UL 1950 creepage and clearance requirements List-Post: treg@world.std.com Date: Thursday, May 08, 1997 3:01PM To any and all safety gurus, I am in the midst of trying to minimize the creepage and clearance requirements between TNV and SELV called out in IEC 950. My interpretation of tables 5 and 6 in sections 2.9.2. and 2.9.3 are that minimum clearance is 2.0mm and minimum creepage is 2.5mm. This is based on a global design using up to 250V mains, pollution degree 1 & 2 and Material Group IIIa + IIIb. The application is for Class I as well as Class II systems. I could not find a reference explaining the definition of the Material Groups and would appreciate any insight into a clause, etc. which I could reference to reduce these spacing requirements. Please also advise if you are in need of further details. Thx, Joe ********************************************************************** Joe Finlayson Manager, Compliance Engineering Microcom, Inc.