Treggers,

Does anyone know by practical experience/experimentation what is the
minimum OPERATIONAL creepage and clearance distance required for the
following conditions:

Circuit type              - Secondary Circuit
Electric strength         - 1000V 50Hz for 1 minute (i.e BS EN
60950/A4                              : 1997 clause 6.4.2.2)
Pollution degree          - 2
Material Group            - IIIa (CTI 200)
Maximum transient         - 1.5kV
Transient repetition rate - very low (lightning, TNV-3)

I realise that in BS EN 60950/A4:1997 table 6 for a TNV working voltage
of 125V d.c the creepage distance stated is 1.5mm and from table 5 for a
TNV working voltage of 140V d.c (transient overvoltage of 1.5kV) the
clearance stated is 0.7mm, but after reading BS 7822:1995 (IEC
664-1:1992) it would appear that the creepage distance is based on long
term stresses whereas the flash test requirement of EN60950 clause
6.4.2.2 is for one minute only.

BS 6221:1991 (IEC 326-3:1991) section 6.4.1 gives a graph of "voltage
against spacing between conductors" that differs greatly from BS EN
60950 even after derating by a factor of 11 and doesn't appear to take
the material group into account. Does anyone know the source of this
graph?
 
BS EN 41003 : 1991 in Annex F (informative) gives a clearance distance
of 0.5mm (inhomogeneous field) for the 1.5kV impulse test of BS EN 60950
clause 6.4.2.1 which ties up with BS 7822:1995 (IEC 326-3:1991) table 2
and a creepage distance of 1.5mm which ties up with BS 6221:1991 (IEC
326-3:1991) table 4.

I have always used 1mm per 1kV for clearance through air but does anyone
know the formula for creepage?

Any help or pointers to other specifications is welcomed.

Regards

Richard Steele