> From: "Nick Evans" <[email protected]>
> Subject: US supply Voltage questions
> 
> I wonder if anyone can help me with a couple of practical questions
concerning 
> USA supply voltages.
> 
> 1.  Does anyone know what the normal maximum current rating is on a 110V 
> supply for a domestic socket outlet.

The US outlets I'm looking at in a catalog are 
all rated  NEMA 5-15R or  15 amps. 
You should always look for NEMA rated plugs 
and sockets for anything. 

> 2.  Are there any situations (for example in commercial installations)
where a 
> single phase supply of greater than 110V can (would normally be
supplied)? 

It depends and it's not really 110VAC.  
It could be as high as 120VAC in some circumstances. 
Somewhere I believe I saw the US line voltage 
available to the consumer (you and me) listed 
as officially 117VAC. 

Fairly slow high line conditions can occur 
depending upon what your power grid is 
connected to.  I believe there was a situation 
where the power grid for a community had an 
electric foundry attached.  At about 1 am in 
the morning, the foundry would shut down. 
Since the power company had tried to adjust 
for the increased load while the foundry was 
running, the line voltage was driven above 
150 VAC for a brief period of time. At a much 
lower level, this type of thing happens in 
your house all the time. 

> If so what would be the normal maximum current 
> supply for this increased voltage. 

Roughly the more voltage, the less current. 
But, I'll probably get nailed on that one. 

Power in equals power out.  So if you need 
115 watts from the line, that requires 
1 amp of current for roughly 115VAC. Drop 
the line voltage up or down and the current 
should run in the opposite direction. 
Going to 120VAC the current should drop 
to 115W/120VAC = approx. .95 amps. 

What you really want to be concerned about 
are brownout conditions. If the voltage 
drops, the current should rise. Say our 
115VAC drops to 105VAC. To maintain the 
115 Watt requirement the current should 
rise to 115W/105VAC = 1.1 amps. 

If the line powering the motor in your 
air conditioner or frig begins to brownout 
or droop, the motor can stall. Thus, the 
motoring effect drops to zero. Now, the 
only resistance through the motor is the 
wire itself. 