Hi George:


Here is what I sent to this group a week or so ago:

>5.  What are the IEC 950 enclosure flammability class requirements?
>
>    In Sub-clause 4.4.4, enclosure flammability class is specified
>    depending on the function of the enclosure:
>
>        Mechanical enclosure:            HB or better.
>        Electrical enclosure:            HB or better.
>        Fire enclosure (<18 kg)          V-1 or better.
>        Fire enclosure (>18 kg)          5V or better.
>

Jasmine Wong and Jim Eichner are correct:  IEC 950 DOES (today)
have a "sweeping generalization" that electrical enclosures need 
only be rated HB.  See Sub-clause 4.4.4, third paragraph.

Your associate quotes Sub-clause 4.4.5 which identifies COMPONENTS,
not circuits, which require a fire enclosure,  (It also identifies
those COMPONENTS which DO NOT require a fire enclosure). 

Jasmine is wrong in identifying SELV circuits as the criterion for 
not requiring a fire enclosure.  Rather, as your associate stated,
it is the COMPONENTS in "limited power circuits" which do not 
require a fire enclosure.  (Often, but not necessarily, SELV 
circuits also qualify as limited power circuits.)

These are fine points, distinguishing between circuits and
components.  IEC 950 permits primary and secondary wiring comprised 
of PVC, et al, wire insulation, enclosed switches and relays, and 
certain motors to be within an HB enclosure.  Indeed, if one reads
further (Sub-clause 4.4.1), an HB enclosure can be used for circuits
which are NOT limited power by performing extensive fault testing!

The issue of fire from electrical energy is that of electrical 
heating resulting from power dissipation in a resistance or impedance.
The trick is to identify the resistances that can dissipate power
for an extended time -- long enough to heat the plastic material to
ignition temperature.  The resistance can't be too low or too high.
For each power source, there is a range of resistance that can 
dissipate sufficient power.  Usually, this is in the 0.5 to 5 ohm
range.  So, we have candidate components such as contact resistances
in switches and connectors, forward resistances of semiconductors,
and the dc winding resistances of transformers and chokes.

So, it is really not out of the question to do fault testing that
would qualify a circuit and its components for an HB enclosure.


Best regards,
Rich



-------------------------------------------------------------
 Richard Nute                             Quality Department 
 Hewlett-Packard Company           Product Regulations Group 
 San Diego Division (SDD)          Tel   :      619 655 3329 
 16399 West Bernardo Drive         FAX   :      619 655 4979 
 San Diego, California 92127       e-mail:  [email protected] 
-------------------------------------------------------------