I'm having a hell of a time with UL. 

A piece of equipment I'm having tested is 
powered with -48vdc from the power grid 
in a CO.  That power grid takes in AC from 
the street, steps it down to 48 VDC rectified, 
then passes it across the batteries, finally 
distributing it out to the racks in the CO. 

That 48 VDC is SELV for there are fuses all 
over the place in the CO right up to where 
the equipment in the racks plug into it. 

Under UL1950 3rd Edition, Table 18, page 125, 
I'm declaring that the 48vdc is secondary and 
I asked to have my equipment tested operationally 
at 500V. 

I have had 48vdc equip tested at another 
lab and approved to UL1950 3rd Edition 
under the same claim above. 

UL says no way.  It must be tested under 
the PRIMARY heading of Table 18 page 125. 

It is important to note here that I WANT 
the hi-pot testing to be done. 

Well, now I'm told that if I demand this 
to stay as I originally asked, then I only 
get UL1950 2nd Edition until the year 2000. 

I don't understand.  I've had this done 
before without a problem. 

Also, the power supply people, more than 
one, find this to be news to them. Most 
of the hockey puck DC-DC converters out 
there (that I've dealt with) aren't able 
to withstand 1414VDC operational. 

Am I alone here?  

Are other mfrs of 48vdc and 24vdc equipment 
intended for COs running into the same thing??? 