The North American "curves" are

@ 110%, essentially continuous operation (last I saw, there was a
minimum finite time factor involved, but I don't remember what it is)

@ 135%, must open within 60 minutes

@ 200%, must open within 120 seconds

So, for a 5A rated fuse, 

5.5A must be carried continuously

6.75A must cause the fuse to open within 60 minutes

10A must cause the fuse to open within 120 seconds

I don't know where your 8A for 90 minutes comes from, unless the UL198
Series of standards has been revised while I wasn't looking.  Unless, of
course, you're talking about performance of a specific fuse.  Such a
fuse would at best be accepted by UL as a Recognized Component and by
CSA similarly, with limitations on its use and application. 


Regards,


Peter L. Tarver
Nortel
[email protected]

>----------
>From:  George Stults[SMTP:[email protected]]
>Sent:  Monday, October 27, 1997 2:17 PM
>
>Greetings,
>
>In an recent conversation I was suprised to learn that a 5AMP fuse 
>could last as much as 1 hour (1-1/2 hours?) at 8AMPS per the North
>American Curve (for power dissapation?).
>
>Is this correct?  What about Europe?  
>Thanks in advance for any comments.
>
>Regards
>George Stults
>Cellular Techinical Services
>(new EMI/EMC/Safetey draftee)
>

Reply via email to