Jim,

The category description is what tells the user/installer what factors were 
considered as part of the Listing or need to be considered as part of the 
product's use or installation. It would seem to me that this is important. 
For example, the category "guide" information for NWGQ includes not only 
that UL1950 is the standard that is used but also that the equipment is 
intended for installation in accordance with the NEC. It also has info 
regarding installation in "computer rooms", use and testing of equipment 
that might be installed in environmental air space, etc.

The category guide for primary protectors (i.e. carbon blocks, etc.) 
includes information concerning codes that are used to identify the fusing 
bridal wire that must be used at the installation to afford adequate 
protection. The "custom-built" category guide includes codes and 
information that can be used by installers or inspection authorities to 
help make sure the equipment is compatible and installed correctly. The 
"Communication Service Equipment" category guide includes a reference to 
the NESC as well as the NEC, since this equipment might be used in areas 
not covered by the NEC, such as up on shared facility utility poles, 
pedestal sites, etc..It also talks about the minimum outdoor environmental 
conditions that are considered (temperature range, rain, etc.), protection 
issues (since some devices incorporate primary protection) and the like.

CSA has a similar system in place that describes the certification category 
as does UL's c-UL program for Canada. I'm not sure about the other labs. 

UL has a Canadian category for Communication Service Equipment (DUZO7). We 
have a number of Listings in this category and I have not heard anything 
about it not being accepted. (We have also issued (at the mfrs request) 
some IEC950 CB reports on equipment that was covered under this category 
and included the additional requirements we considered important as an 
addendum to the basic report!)

There is nothing unusual about another specification (such as a Bellcore 
GR) referencing a standard rather than a category. In fact, this would be 
the right way to do it. If the entire standard is referenced then by right 
the equipment must meet the entire referenced specification to comply with 
the clause in the basic spec. Sometimes, like for the AC Power Fault Tests 
in GR-1089-CORE , 4.5.13 note 10, only a portion of the spec is relevant to 
the AC power fault tests (the UL1459 overvoltage tests) and I would say 
that this type of reference would not require or imply complete compliance 
with everything else since the note is specific to this section. The GR is 
only looking for the data and an indication of compliance with the 
overvoltage test. (This is also a good example of what I talked about 
earlier where a spec is referenced but modified....GR-1089 requires one of 
the UL1459 tests to be modified up to 277 Volts.) 

R4-5 of 1089 states "shall be listed for the purpose". For most customer 
premises equipment, WYQQ or  NWGQ would be appropriate since the equipment 
is on the protected side of the NI and the resulting "listing" would show 
compliance with UL1459 or UL1950. However, an SIU that provides the network 
interface, isolation and primary protection would be  "listed for the 
purpose" if it were covered under DUZO since this category covers the 
relevant safety issues while a listing under WYQQ or NWGQ would probably 
not be appropriate "for the purpose" of its actual usage.


Randy Ivans