Jon,

The standard that I commonly use for the EU is EN 50178.  It is "Electronic 
equipment  for use in power installations".  On the table minimum creepage 
distances there is a note that says:

"Values for Voltages above 10 kV shall be determined according to IEC 71-1 
to -3".

I have never reviewed IEC 71 so this is all I can tell you.  And I cannot 
tell you which directives are applicable.  Thankfully, to date I have never 
had to certify any of our high voltage products.

Doug Powell
Advanced Energy Industries, Inc.
[email protected]

 ----------
From: Jon D Curtis
To: [email protected]; [email protected]
Subject: Products outside LVD range
List-Post: [email protected]
Date: Wednesday, February 04, 1998 4:10PM


This one's more appropriate for the EMC-PSTC List :) -JDC.


From: "D. E. Smith" <[email protected]>
Subject: Outside the LV Directive Range


  What do you do it your product has a working voltage outside the LVD
range?  While the LVD has a range of 50 to 1000 volts DC or 75 to 1500
volts AC a product like a high voltage test probe may not fall into
this range because they measure voltages from 6 to 40 KV.  What
happens if someone would use one of these probes to test a circuit
that falls within the LVD?  Can we test to IEC 1010 Category III and
if it passes can we claim compliance?