Hi Eric:


You ask what spacings are necessary for a circuit
rated at less than 30 V and "isolated" for 250 V.

Unfortunately, you did not tell us what the circuit
is isolated from.

I am going to assume that your isolated circuit is
a "floating" circuit, meaning that it has no connection
to ground or any other circuit.  I further assume that
the circuit is functionally derived from an SELV circuit,
e.g., transformer-coupled to an SELV circuit.  I further
assume that it is isolated from all mains (primary) 
circuits by the SELV circuit (so that we do not need to
consider spacings between the isolated circuit and the
mains).

The first thing we must decide is that this is a 
secondary circuit being isolated from another secondary
circuit.  In this case, we can ignore the spacings 
required for mains circuits as secondary circuits are
not subject to transient overvoltages.  Another way of
saying this is that the circuits are subject to 
Installation Category I spacings requirements.

However, in IEC 1010-1, the spacings requirements apply
to Basic, Supplementary, and Reinforced insulations.
My definition of the problem says that the construction
only has functional (operational) insulation, since all 
voltages are less than 30 V.

So, there are NO spacing requirements for the construction
as I have defined it.  Use anything you want!

I would choose the value, for design purposes only, from
Table D.1, for 300 V, namely 0.5 mm clearance and 0.7 mm
creepage.


Best regards,
Rich


    "The word 'impossible' is not in my dictionary."
     -- Napolean Bonaparte



-------------------------------------------------------------
 Richard Nute                             Quality Department 
 Hewlett-Packard Company           Product Regulations Group 
 San Diego Division (SDD)          Tel   :      619 655 3329 
 16399 West Bernardo Drive         FAX   :      619 655 4979 
 San Diego, California 92127       e-mail:  [email protected] 
-------------------------------------------------------------


Reply via email to