Rich Nute wrote:

> Hi Georg:
>
> You pose an interesting question, "Is a GFCI allowed on
> an IT system?"
>
> I will answer a different question:  "Will a GFCI work
> on an IT system?"
>
> I will answer yet another question:  "Does a GFCI provide
> a protective function on an IT system?"
>
> A GFCI measures the difference current between the two
> supply conductors.  Under normal load conditions, the
> difference current is zero.  If the difference current
> exceeds the GFCI setting, usually 5 to 20 mA, then the
> GFCI disconnects the supply.
>
> The GFCI requires that one of the two supply conductors
> (i.e., the neutral) be grounded.  Or nearly grounded.
> This provides a current path AROUND the GFCI such that
> a difference current is created and thereby causes the
> GFCI to operate.
>
> The IT system has no direct connection to ground, i.e.,
> the neutral is not grounded.  The "I" in IT means the
> neutral is grounded through an "I"mpedance.  I understand
> that the value of the impedance is 1000 ohms or greater.
>
> This impedance has the effect of setting the maximum
> difference current in the system.  The maximum difference
> current for a 230-volt system would be:
>
>             230 V
>     I  =  -----------  =  230 mA
>            1000 ohms
>
> Clearly, if the impedance is 1000 ohms, then the GFCI
> will work.
>
> If the impedance is 100,000 ohms, then the maximum
> difference current is 2.3 mA, and the GFCI will not work.
>
> So, whether or not the GFCI will work depends on the value
> of the grounding impedance of the IT system.
>
> However, if the IT system is grounded through 100,000 ohms,
> then the maximum current that can flow through a body
> connected between one pole and ground is 2.3 mA.  While
> unpleasant, it is not unsafe!
>
> So, if the value of the impedance of the IT system ground
> is high enough to not allow the GFCI to operate, then the
> IT system does not reguire a GFCI to be safe!
>
> Best regards from San Diego,
> Rich
>

Hi Rich

Thanks for your comment.

You're right:
     So, if the value of the impedance of the IT system ground
     is high enough to not allow the GFCI to operate, then the
     IT system does not require a GFCI to be safe!

According to HD384.4.41 S2:1996 (I only got copies of 2 pages) RCD
(GFCI's) are
allowed as protection.

They are right, under following circumstances:
  - each consumer (or consumer group) is connected via GFCI
  - there is one fault on one consumer.

If now a person would touch an active wire (or you would have a second
fault)
BOTH GFCI's would trip.

I.e. GFCI's could offer a protection in case of two faults.

Best regards


George
--
**************************************************************
* Dr. Georg M. Dancau             *  HAUNI MASCHINENBAU AG   *
* [email protected]             *  Manager EMC Lab         *