Joe,
Thanks for your very understandable explanation.
I have read the sections you described in UL1950_3, however I still don't
have a clear understanding of the difference between "basic" and
"supplementary" insulation.
John

-----Original Message-----
From: [email protected] [mailto:[email protected]]On
Behalf Of [email protected]
Sent: Wednesday, October 14, 1998 10:06 AM
To: [email protected]
Subject: Re: Ground on Tip & Ring


In a message dated 98-10-13, John Honeycutt writes:

<< It is unclear to me if connecting the midpoint of the series connected
 capacitors to the ground etch which connects to the PCB mounting bracket,
 which ultimately is attached to the computer chassis, violates safety in
 certain countries,  i.e. Norway. >>

John:

If you connect the midpoint to chassis ground, your capacitors will bridge
the
safety isolation barrier.  For equipment that is not permanently grounded
(i.e., a typical PC), most countries require "basic" insulation per clause
6.2.1.2 of IEC 950.  You can meet this requirement with a 1000 volt rms
rated
cap whose leads meet the creepage and clearance requirements.

Norway and Sweden both require "supplementary" insulation, which imposes
more
stringent requirements.  A conservative choice here would be to use a
safety-
rated Y1 cap, which IEC 950 specifically allows in clause 2.2.8.1 for
bridging
"reinforced" insulation.  This would be overkill, but it would get the job
done.  Alternatively, I believe you could use a Y2 cap, which IEC 384-14
defines as suitable for bridging supplementary insulation.

Y1 and Y2 caps are readily available in through-hole, ceramic disk form with
radial leads.  They are used in almost all switching power supplies that
connect to the AC power mains, to reduce emissions.  The only vendor I know
that makes a surface mount Y1 cap is Murata Erie.


Joe Randolph