Dear All,

A telecom rack subsystem has two power entry modules (for 
redundancy); two cables, one for each power entry module, each 
consisting of 3 leads (+, - and earth), are terminated by means of a 
3-pole connector to each power entry module; the other end of the 
cables are terminated to one 5-pole connector where two of the 
earthing leads are terminated together in one terminal of the 
connector and the other four leads (supply) are terminated to each 
of the remaining terminals of the connector. This 5-pole connnector 
is the connection to the power distribution unit which has the main 
earthing terminal, power supply connections and circuit breakers.

1. Do you see a problem with UL1950/EN 60950 of terminating two 
earth bonding leads to one terminal? I should state that the 
connector is Recognized but most likely evaluated to accept one 
wire per terminal. 

2. Assuming that the combination of connector and two leads in 
one terminal was submitted for a separate investigation (to one of 
the connector standards), is there some clause in the standard 
which will not allow me to use this type of termination?

3. In lieu of 3 leads/cable, can manufacturer use 2 leads/cable and 
use the shield of the cable as the earth bonding "conductor"? 

4. For wire terminations in general, I find that more and more 
manufacturers like (for manufacturing reasons) to terminate their 
leads to insulated bullet type pressure terminal connectors prior to 
terminating them to connectors and/or terminal blocks employing 
pressure wire terminals. However, even though the 
connectors/terminal blocks are Recognized, these bullet type 
connectors are not Approved. 

Is anyone using the same technique in manufacturing? If so, do 
you use Listed and/or Recognized bullet-type pressure wire 
connectors? If so, can you supply with some manufacturer's 
names of such connectors?


Thanks in Advance,





PETER S. MERGUERIAN
MANAGING DIRECTOR
PRODUCT TESTING DIVISION
I.T.L. (PRODUCT TESTING) LTD.
HACHAROSHET 26, P.O.B. 211
OR YEHUDA 60251, ISRAEL

TEL: 972-3-5339022
FAX: 972-3-5339019
E-MAIL: [email protected]
Visit our Website: http://www.itl.co.il

---------
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to [email protected]
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to [email protected],
[email protected], [email protected], or
[email protected] (the list administrators).

Reply via email to