> I am using Type 121b as a preheater for the outdoor air. I combined the 
> heater with a controller (type2) that
> makes sure the air is heated whenever the outdoor air temperature is below 
> 16°C. This controller gives a control function to type 121b. I've put the 
> setpoint of the heater to 16°C.
> (I ignore heat losses), but every time the outdoor temperature is already 
> 16°C before heating up, 
> the heater heats still heats up the air and the temperature becomes > 50 or 
> 60°C. 
> Can someone help me with this?

Without seeing your input file it's impossible to tell you what's happening in 
your simulation, but you do not need a Type 2 controller if you're using the 
furnace.  Simply set the setpoint to 16 C, with a large capacity, and leave the 
control signal set to a constant value of 1.0. The internal controls will keep 
the outlet at 16 C if the inlet temperature is below 16 C.

Jeff


****************************************************************