Dear Jeff,
 
in fact this cannot be done straight forward. In order to do it correctly,
you have to run three simulations:
 
1. Simulation without internal and solar gains:

S Q_heat_1 = S Q_inf (if Q_heat>0) + S Q_vent (if Q_heat>0) + S Q_trans   (Eqn.1)

(Ntype 30)               (Ntype 4)                        (Ntype 5)

from Eqn. 1 you otain the transmission losses:  S Q_trans

 

2. Simulation without solar but with internal gains:

S Q_heat_2 = S Q_heat_1 - S Q_gains,useful   (Eqn.2)

from Eqn. 2 you otain the useable internal gains: S Q_gains,useful  

 

3. Simulation with internal and solar gains:

S Q_heat_3 = S Q_heat_2 - S Q_solar,useful  (Eqn.3)

from Eqn. 3 you otain the useable solar gains: S Q_solar,useful 

 

Regards,

Marion

 

 

-----Ursprüngliche Nachricht-----
Von: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] Im Auftrag von [EMAIL PROTECTED]
Gesendet: Dienstag, 30. Mai 2006 21:43
An: [email protected]
Betreff: [TRNSYS-users] Output

Hi All,
I would like to known which part of solar and internal gains really participate to heating during winter for a zone.
I mean with a heating system using a temperature threshold, a part of these gain only contribute to increase temperature above the setting. Then they don't participate to heating.
If you have an idea....

Regards,
JeFF