Filippo,

Myself i set the parameters very simply, (in order from the first to the sixth) my values are:
5
1
40
26
45
43

the fourth parameter of Type8 is the cooling set point and the fifth parameter is the 1st stage heating set point. If the room temperature goes above the cooling set point, the controller turns the cooling system on and if the room falls below the heating set point, the controller turns on the heating system. The controller doesn't allow the cooling set point (16C in your case) to be lower than your heating set point (45C) because then both the heating and the cooling system would be on at the same time.

Cheers,
 David


****************************************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY                           2916 Marketplace Drive - Suite 104
Partner                                        Madison, WI 53719
Phone: (608) 274-2577 USA
Fax: (608) 278-1475
E-mail: [EMAIL PROTECTED]
Web Pages:  http://www.tess-inc.com     and      http://www.trnsys.com

"Providing software solutions for today's energy engineering projects"
****************************************************************************************