> Ticket Number: 20010912-2                  Ticket Status: UPDATE
> Ticket Type  : Unscheduled                 Ticket Source: TEN-US NOC
> Ticket Scope : Site                        Site/Line    : New York
> Ticket Owner : TEN-US NOC                  Problem Fixer: Telehouse NY
> Ticket Opened: 20010912 12:08 UTC          Problem Start: 20010911 20:35 UTC
> Ticket Update: 20010918 05:13 UTC
> Ticket Closed:                             Problem Ends :
> 
> 
> Ticket Summary: Status of 25 Broadway
> 
> Problem Description:
> 
> This ticket is being issued to track the status of the infrastructure
> at the DANTE World Services PoP in New York.  Individual circuits
> will be dealt with separately.  Updates will be in the "actions" section
> below.
> 
> Affected:
> 
> DANTE World Service
> 
> Actions:
> 
> cziarhe       20010918 05:13 UTC
> Load was switched from the Con Ed generator to the critical generator
> as planned.  Unfortunately, after about 45 minutes the generator
> again began to overheat and the load was switched back.  This was
> achieved without interruption to service.  It is now believed this
> could be due to limescale build-up in the radiator.
> 
> This is to be rectified by using an acid wash through the cooling
> system and again running the generator under load at 22:30 UTC
> tonight (Tuesday).
> 
> A plan is also being developed to bring in a new generator should
> the situation with the critical generator persist.
> 
> 
> 
> Time to Fix: (Hours:Mins)
> 
> 
> 
> Fix:
> 
> 
> 
> History:
> 
> cziarhe       20010917 21:53 UTC
> Telehouse NY believe the problems with their "critical" generator
> have been caused by faulty thermostats.  These have now been replaced
> and the generator has been spun up for a basic test.  The next
> step is to try a load test, which will begin at 22:30 UTC.  If
> this is successful, then load from the "essential" generator, which
> supplies the air conditioning will be transferred to the Con Ed
> generator for maintainence to take place on this generator, which
> has also been running overtemperature.
> 
> Assuming all this works successfully, Telehouse plan to run the
> Con Ed generator in conjunction with either the essential (Air
> Con) or critical (equipment) generator to make the best use of
> available fuel.  Further fuel supply problems are not thought to
> be likely as there are 17 tankers in the city, and a further 30
> generators are available.
> 
> The IP NOC will monitor the initial switch to the critical generator
> to ensure equipment remains in operation, and reinstall the workaround
> with KPN should it be needed.
> 
> cziarhe       20010916 14:59 UTC
> The latest update from Telehouse reports that an extra 2000 gallon
> fuel tank is expected to be connected to the Con Ed generator soon
> to allow for longer refuelling intervals.  in addition, Con Ed's
> refuelling process to all buildings in the area has now settled
> down, so it should be as reliable as possible in the circumstances.
> 
> An engineer is currently onsite investigating the problems with
> Telehouse's own generator.
> 
> cziarhe       20010916 12:05 UTC
> Regular fuel deliveries appear to have been secured for the Con
> Ed generator.  There were deliveries at 02:00 UTC and 11:30 UTC,
> and another is scheduled for 21:30 UTC.
> 
> The status of the Telehouse generator is currently unknown.
> 
> cziajom       20010915 20:16 UTC
> Contacted Telehouse NY. Informed that Con Ed generator is now up,
> with enough fuel until Tuesday (18 Sep). Engineers are still working
> on the Telehouse generator. NY Routers are starting to come up.
> 
> cziarhe       20010915 18:25 UTC
> Despite what we were informed of earlier, the Con Ed generator ran
> out of fuel at 16:45 UTC.  Telehouse's generator then started up,
> but overheated again.  There is a fuel truck just outside the cordoned
> area, but it is not being allowed through, and unfortunately we
> have no ETA for the fuel, or time-to-repair for the Telehouse generator.
> 
> cziarhe       20010915 18:15 UTC
> Power was lost again at 17:45 UTC, we are contacting Telehouse for
> information.
> 
> cziarhe       20010915 15:52 UTC
> The current status relayed to us by Telehouse is as follows:
> 
> The Con Ed generator is monitored around the clock by Con Ed personnel,
> who are responsible for refuelling it.  As of 15:00 UTC there was
> approximately 15 hours worth of fuel remaining.
> 
> The water pump on Telehouse's own generator has been replaced and
> the unit has been run for about 30 minutes to test.  Telehouse
> are taking this opportunity to perform some routine maintenance
> (changing oil and filters, pressure washing the radiator) to ensure
> it is ready should it be needed for another extended run.
> 
> Fuel currently available onsite should last until Thursday at current
> consumption rates.  Another delivery is being planned for Monday.
> 
> Engineer access is possible, but the procedure is slightly different
> due to movement restrictions still in effect.
> 
> cziarhe       20010915 08:55 UTC
> Power was returned via the Con Edison generator at approximately
> 02:45 UTC this morning (Saturday).  All DANTE World Service equipment
> is functioning without any failed power supplies.  Telehouse also
> expect their own generator to be fixed soon, so there will be two
> sources of power again, as the Con Edison generator will remain
> until grid power is restored.
> 
> cziarhe       20010914 18:06 UTC
> Con Edison have delivered the transformer and connected it to be
> building's power supply, they expect to have the generator itself
> online by approximately 21:00 UTC this evening (Friday).
> 
> Unfortunately the water pump for Telehouse's own generator has
> been difficult to source and is currently being shipped from Pennsylvania
> with an expected arrival time at 25 Broadway of midnight tonight
> UTC.  Installation is planned for tomorrow.
> 
> Hopefully the Con Edison generator should allow the DANTE World
> Service to resume at some point this evening.
> 
> cziarhe       20010914 08:11 UTC
> To clarify the previous entry, the generator from Con Edison was
> expected onsite yesterday evening US time for connection this morning
> their time, i.e. early to mid-afternoon European time.
> 
> cziaseo       20010914 06:16 UTC
> The  generator failed because of the water pump. Estimated repair
> time
> is late tomorrow (Friday, 9/13). In the meantime, Con Ed has committed
> 
> to provide generator from the street and we expect delivery tonight.
> 
> Estimated connection is sometime tomorrow morning.
> 
> 
> cziajom       20010914 04:57 UTC
> An engineer is on-site to try and repair generator. However, still
> not able to give any indication of a resolution time. Further information
> will be given, as it becomes known to us.
> 
> cziarhe       20010914 01:50 UTC
> Power failed again at 01:40 UTC.  Apparently there is a generator
> technician onsite, and Telehouse are talking to Con Edison about
> borrowing a generator in the event the current one cannot be fixed.
> 
> cziarhe       20010914 01:39 UTC
> Power has returned at 01:30 UTC.  More information will be supplied
> as we have it.
> 
> cziarhe       20010914 00:20 UTC
> Have spoken to Telehouse Ops, they are waiting for an engineer for
> the diesel generator and will let us know via email as soon as
> they have more information.  This ticket will be updated when the
> information reaches us.
> 
> 
> cziajom       20010913 23:11 UTC
> Received msg from M+ (23:06 BST) to contact WorldCom. Contacted
> WorldCom. Engineer stated that generator had to be powered off
> due to overheating .... and that if generator cannot be fixed,
> then they will have to await the arrival of a new generator. Therefore
> not possible to give any restoration time for power.
> 
> Ticket # 447111 issued by WC.
> 
> Asked WorldCom to contact us, as they get further information.
> 
> cziarhe       20010913 21:45 UTC
> As of 21:40 UTC, Telehouse have been required to shut down the generator
> due to a rapid increase in temperature, this has meant a loss of
> power to all DANTE World Service equipment.  We currently have
> no time for restoration of power.
> 
> cziarhe       20010913 16:24 UTC
> Fuel has arrived on-site and is currently being transferred into
> Telehouse's storage tanks.  Once this is complete there will be
> sufficient diesel for another four days of generator power.
> 
> cziarhe       20010913 14:29 UTC
> The fuel delivery truck is currently preparing to leave Staten Island
> for 25 Broadway, however, progress is expected to be slow.
> 
> Should this fail, Con Edison are prepared to deliver fuel to 25
> Broadway.  They are still unable to give an estimate as to when
> utility power will be restored.
> 
> cziarhe       20010912 21:35 UTC
> Commercial power to 25 Broadway was interrupted when debris from
> WTC 7 (The Salomon building) fell on the substation.  It is not
> expected to be restored before the weekend, so delivery of the
> fuel mentioned in a previous update is being investigated.
> 
> Telehouse believe they will be able to allow personnel onto the
> site at some point tomorrow (Thursday).
> 
> cziarhe       20010912 18:23 UTC
> Telehouse have secured an additional 4500 gallons of diesel fuel
> and are attempting to get permission from the Port Authority of
> New York to transport it to 25 Broadway.
> 
> cziarhe       20010912 13:31 UTC
> Telehouse have informed us that if commercial power is not restored,
> it is unlikely that they will be able to replenish the fuel supply
> when it becomes depleted.
> 
> In addition, the area in which 25 Broadway is located has been
> evacuated.  Essential staff are remaining on-site, but should they
> be forced to vacate the building, Telehouse say the ability to
> continue to provide emergency power would be impacted.
> 
> 
> cziarhe       20010912 12:17 UTC
> Sorry, "18:35 UTC" in the previous entry should read "18:35 UTC
> on Friday September 14th".
> 
> cziarhe       20010912 12:13 UTC
> As of 20:35 UTC on September 11th, 25 Broadway is running on the
> emergency diesel generator.  Initial information was that they
> had 24 hours worth of fuel, but drain is currently much lower and
> we have been informed that they could last up to 70 hours, which
> takes service up to 18:35 UTC, although this is a maximum.
> 
> It is not clear whether refuelling will currently be possible,
> or when commercial grid power will be restored.