Yes, I do now think, the heat exchanger should do it in the horizontal orientation.
I tested this as follows:
I downloaded and installed the heatexchanger calculation software from SWEP. It is unregistered and in demo mode. Registering is free bust must be approved, so I have none. In this mode the application supports only water-water applications, so far I found.

So I inserted the primary water flow multiplied by 5, this gives about the thermal energy of the steam.

Under this conditions I get secondary delta_t of 5° and the difference between primary out and secondary in is about 0.5 degrees.
Lewan reported about 1 degree.

So if this exchanger can do it with water, then it should also be able to do it with the equivalent energy in steam.
Apparently horizontal orientation is not a problem here.

BTW, the difference between primary out and secondary in was about 1 degrees in Lewans report. If the primary delta_t was 100° then this means, the energetic efficiency of the heatexchanger was 99 %. This is pretty good and is probably because this exchanger is designed for higher flow rates.

Best,

Peter


Am 11.12.2011 21:06, schrieb Alan Fletcher:
"Peter Heckert"<peter.heck...@arcor.de>

Here is a screenshot about condensing applications:
http://hphsite.de/vortex/SWEP-handbook.png

I think Rossi did it perfectly wrong and the exchanger cannot work in
horizontal orientation.
I think that the combination of using it horizontally AND with a low team 
volume will work against Rossi -- any pooling of water in the HE which creates 
a blockage would rapidly result in a temporary fall in the secondary output 
temperature.

But which wins .. a blockage, or negative pressure from condensation?

Any negative pressure from condensation (vacuum relief valve) feeding back into the eCat 
would result in a lower pressure and greater evaporation. Also, this argues against the 
"input pump" blockage -- negative pressure would increase the flow.

All of which makes the 120C reading less  understandable.

SWEP has also a software to calculate heatexchangers. ...
I'll try to give it a shot next week.

Maybe I'll also try to get the Elmer FEM system working again.