That is a good try.  I agree with all that you say except for one key item.  
1). No negative current flows due to the diode. 2). The instantaneous power 
being delivered to the resistor is I^2*R as you suggest. 3). The DC rated clamp 
on meter should measure the total RMS current provided it can handle distorted 
AC waveforms.  Now, here is where you have a problem with the measurement.  You 
say to multiply the true RMS current by the voltage and that is where the 
problem arises.   I am confident that you realized that as soon as you said it!

All of the power that is applied to the resistor comes from the wall socket.  
The voltage at this location is a sinewave at the frequency supplied by the 
electrical service.  There is no DC voltage component, so the DC power being 
supplied is 0.  The AC component of the input frequency is the only one that 
can have power supplied and that can only be given to current at its 
fundamental frequency.  So, to determine how much power the resistor absorbs 
you must take the fundamental current component and multiply it by the 
fundamental voltage supplied by the wall socket.  This needs to be corrected 
for phase shift if any exists with the product by the cosine of the difference 
in phase of the two components.

Therefore, the DC flowing through the rectifier does not contribute to the 
measurement.

Dave


-----Original Message-----
From: Duncan Cumming <[email protected]>
To: vortex-l <[email protected]>
Sent: Mon, May 27, 2013 2:56 pm
Subject: [Vo]:Re: [Vo]:Torbjörn Hartman describes power measurments


          
    
I will give it my best shot.
      
      Consider a diode in series with a resistor, and connected to an AC      
outlet. For the first half of the cycle the diode conducts, and a      positive 
current flows. For the second half, the diode does not      conduct and NO 
NEGATIVE CURRENT FLOWS, even though a negative      voltage is present. This is 
the function of a diode. So what you      have is an intermittent flow of 
positive current, which delivers      power to the load resistors. The 
magnitude of this power is given      by I^2*R. 
      
      If you were to measure the current using a clamp on ammeter which      is 
DC rated, then the current would be determined accurately and      the RMS 
value determined by the digital voltmeter (which must be a      true RMS type, 
of course). Multiplying this by the voltage gives      the power dissipated in 
the resistor. 
      
      If you  were to measure the current using a clamp on ammeter which      
is NOT DC rated, then only the fluctuations in current would be      measured, 
which fluctuations would be a lot less than the true      value of current. So 
a misleadingly low value of current would be      measured, leading to a 
substantial under estimate of the power      dissipated in the resistor.
      
      This is electrical engineering 101, but it shows some of the      
problems involved in measuring AC power with a non-sinusoidal      waveform. 
There are those who assume that a commercially available      "power meter" 
measures just that, but in fact this is a difficult      task that should be 
undertaken by a qualified engineer with      knowledge of the waveform that he 
is measuring. The specs of such      an instrument clearly indicate the 
limitations to which it is      subject, and one must be careful not to exceed 
these limitations.      An absence of DC sensing capability is one such 
limitation.
      
      In the diode example above, the diode itself does not provide any      
power whatever. It merely confuses some types of power meters.
      
      
      On 5/26/2013 9:51 PM, David Roberson wrote:
    
    
        
          
                          
It does not make any difference whether or not the                instrument 
measures DC current through the input power                cables.   That issue 
is dead unless someone wants to                insist that Rossi or one of his 
partners hid a DC supply                inside the wall, or in some other place 
which allows the                DC to appear at the power input terminals.  
This would                have been obvious to anyone looking at the voltage.
              
 
              
Andrew or Duncan please explain how the DC current                through the 
input power cable is able to deliver a large                power to the load 
resistors?   It can not be done with                any type of diode hidden 
within the blue box.  Are you                ready to concede the point?
              
 
              
Dave   
              
-----Original Message-----
                From: Alan Goldwater <[email protected]>
                To: vortex-l <[email protected]>
                Sent: Mon, May 27, 2013 12:19 am
                Subject: Re: [Vo]:RE: [Vo]:Re: [Vo]:Torbjörn Hartman            
    describes power measurments
                
                
                  
                    
That is a different                      instrument. The one used in the tests  
(PCE-830) does not measure                      DC.
                      
                      On 5/26/2013 7:53 PM, Jones Beene wrote:
                    
                    
                      
Did                            you actually check the PCE site?
                      
 
                      
It                            looks to me like all the current clamps on        
                    the PCE power analyzer site measure both AC                 
           and DC 
                      
 
                      
http://www.industrial-needs.com/technical-data/current-detector-PCE-DC-3.htm
                    
                    
                  
                
              
                      
        
          
    
  