If you're using an APC UPS the indicator that it is no longer on battery is
called "powerRestored" which is TRAP Int:9 . You should get the APC file
POWERNET.MIB and compile it using MIBEXTRA. Then add the desired traps as
events to your device and be sure to include them in the alert. The best
sight I have found for mibs, traps, and searching for OID's is at
http://MibDepot.com. Below is a list of TRAPs I like to use for APC. Good
Luck!
Scott Taylor
Westat, Inc.
upsOverload (TRAP Int:6 Int:2)
upsDischarged (TRAP Int:6 Int:4)
upsOnBattery (TRAP Int:6 Int:5)
lowBattery (TRAP Int:6 Int:7)
powerRestored (TRAP Int:6 Int:9)
upsBatteryNeedsReplacement (TRAP Int:6 Int:17)
upsOverloadCleared (TRAP Int:6 Int:33)
dischargeCleared (TRAP Int:6 Int:38)
batteryOverTemperature (TRAP Int:6 Int:53)
batteryOverTemperatureCleared (TRAP Int:6 Int:54)
-----Original Message-----
From: eric.dami [mailto:[EMAIL PROTECTED]
Sent: Friday, July 18, 2003 1:32 PM
To: '[EMAIL PROTECTED]'
Subject: [WhatsUp Forum] SNMP Trap monitoring
I am fairly new to SNMP. I set my UPS to send traps to my WUG server. I
created a monitor to alert me if a "UPS on battery" trap arrives. It works
great. But how do I get WUG to send me a message that it is off battery? Do
I have to set up another monitor for the "UPS on Power" trap? Or can I do
it right through the first monitor?
Thanks,
Eric Dami
MCSE/MCSA
LAN Administrator
Telephone Credit Union of NH
[EMAIL PROTECTED]
(603)645-8103
Please visit http://www.ipswitch.com/support/mailing-lists.html
to be removed from this list.
An Archive of this list is available at:
http://www.mail-archive.com/whatsup_forum%40list.ipswitch.com/
Please visit http://www.ipswitch.com/support/mailing-lists.html
to be removed from this list.
An Archive of this list is available at:
http://www.mail-archive.com/whatsup_forum%40list.ipswitch.com/