On 10/31/2011 12:23 PM, Josh Luthman wrote:
> That looks like a better solution then the DR-UPS40 and SDR-120-24
> that you recommended earlier.  Is it?  Does it charge the batteries
> and will it feed the equipment from the batteries when AC power is
> out?
>

The AD-155 will charge the batteries to whatever you set output voltage 
to.  By default, it's set to 24.0V (on the B model) so your batteries 
will never fully charge.  You have to set it to whatever you choose for 
your float voltage (like 27.6V) to get a full charge.  On AC power loss, 
the output remains tied to the batteries and will power your equipment 
(unregulated) until the batteries are nearly fully discharged.  A 
variable LVD would be nice, but it does completely shut down once the 
batteries have hit the low mark, instead of cycling on/off as you 
battery turns to mush.

-- 