On Tue, 16 Aug 2022 at 19:45, Todd Zuercher <[email protected]> wrote:

> I'm trying to use Siggen to generate a square wave form and output it to the 
> analog output of a Mesa 7i77.  This is for tuning the current loop on a servo 
> drive.  I set up a simple config to do this, but with the oscilloscope hooked 
> up to the analog output of the 7i77, what we are seeing is not quite the 
> square wave I was expecting.  With the Siggen set for a 100hz signal we are 
> seeing  +1v for about 1ms then 0v for about 4ms then -1v for 1ms then 0v for 
> 4ms,  It isn't quite the square wave I was shooting for.  Where did I go 
> wrong?

What does Halscope think that the output is?

Is the Oscilloscope set up as AC-coupled or DC?

Bsically it sounds like the scope is displaying the derivative of the
square wave, which could be coupling or possibly the probes?

-- 
atp
"A motorcycle is a bicycle with a pandemonium attachment and is
designed for the especial use of mechanical geniuses, daredevils and
lunatics."
— George Fitch, Atlanta Constitution Newspaper, 1912


_______________________________________________
Emc-users mailing list
[email protected]
https://lists.sourceforge.net/lists/listinfo/emc-users

Reply via email to