Arjen de Korte <nut+us...@de-korte.org> va escriure: > > Citeren Ernest Sales <ersa...@gmail.com>: > > > I would like to report a working device to add to the hardware > > compatibility list, but cannot find a way on the website. > Would this > > list be OK for that purpose? > > Sure. Please list the output of 'upsc' as well as whether or not you > tested the shutdown function of the UPS. >
This is a low-end UPS sold in Spain under the IPAR brand, Mini Energy series, model ME 800. It apparently works well with the megatec_usb driver. Tested on power failure, after exhausting batteries the system is gracefully shut down. upsc output: battery.charge: 100.0 battery.voltage: 13.80 battery.voltage.nominal: 12.0 device.mfr: device.model: TR00061J device.serial: unknown device.type: ups driver.name: megatec_usb driver.parameter.pollinterval: 2 driver.parameter.port: auto driver.version: 2.4.3 driver.version.internal: 1.6 input.frequency: 50.0 input.frequency.nominal: 50.0 input.voltage: 204.6 input.voltage.fault: 140.0 input.voltage.maximum: 207.9 input.voltage.minimum: 201.2 input.voltage.nominal: 220.0 output.voltage: 202.3 ups.beeper.status: enabled ups.delay.shutdown: 0 ups.delay.start: 2 ups.load: 19.0 ups.mfr: ups.model: TR00061J ups.serial: unknown ups.status: OL ups.temperature: 30.0 ups.type: standby N.B.: the blazer_usb driver recognized the device, but logs showed connection loss about every minute, so I didn't do further trying. Best regards, Ernest _______________________________________________ Nut-upsuser mailing list Nut-upsuser@lists.alioth.debian.org http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser