On Wed, 4 Jun 2014, Mick wrote:
Some of the variables (those with HU_FLAG_ABSENT) are apparently not stored
on the UPS itself-- they are sent to the UPS when the shutdown command is
executed. Sending the value starts the timer, in some cases, but I think
the ups.delay.start value should be safe to send at the time when it is
set.

I see.  So if for some reason I wanted to change ups.delay.shutdown on a more
permanent basis and the UPS won't store the changed setting, I would need to
run a script on the server to submit the changed value to the UPS each time
the server boots up.

I had the same problem with an Eaton Ellipse ECO 1500. ups.delay.shutdown got lost at each power cycle. I fixed it by setting

     offdelay = 30
     ondelay = 40

in ups.conf. This seems to me to be a better solution than writing a script. I'm guessing that if these two lines are omitted, no value is sent to the UPS unit. Is this true?

Roger

_______________________________________________