On Tue, 27 Oct 2015, George Anchev wrote:

Yes, that was the power off test. However the upssched-cmd script gave absolutely no signs of activity. Even it's logger lines don't show up in journalctl. No any permission error messages - nothing. Only the 2 messages from upsmon - on battery and then on line power.

Here is the nut-report:
http://www.filehosting.org/file/details/518300/NUT.report

Hi George, Thanks for the report. I think the problem may be in your upsmon.conf. Could you try adding "+EXEC" to the NOTIFYFLAG declarations. These will then activate the NOTIFYCMD declaration which should cause upssched to get called. Roger

        ########### /etc/ups/upsmon.conf ###########
RUN_AS_USER upsd
MONITOR myups@localhost 1 upsmaster ********* master
MINSUPPLIES 1
SHUTDOWNCMD "logger -t upsmon.conf \"SHUTDOWNCMD calling /sbin/shutdown to shut down 
system\" ; /sbin/shutdown -h +0"
NOTIFYCMD /usr/sbin/upssched
POLLFREQ 5
POLLFREQALERT 5
HOSTSYNC 15
DEADTIME 15
POWERDOWNFLAG /etc/ups/killpower
NOTIFYMSG ONLINE        "UPS %s on line power"
NOTIFYMSG ONBATT        "UPS %s on battery"
NOTIFYMSG LOWBATT       "UPS %s battery is low"
NOTIFYMSG FSD           "UPS %s: forced shutdown in progress"
NOTIFYMSG COMMOK        "Communications with UPS %s established"
NOTIFYMSG COMMBAD       "Communications with UPS %s lost"
NOTIFYMSG SHUTDOWN      "Auto logout and shutdown proceeding"
NOTIFYMSG REPLBATT      "UPS %s battery needs to be replaced"
NOTIFYMSG NOCOMM        "UPS %s is unavailable"
NOTIFYMSG NOPARENT      "upsmon parent process died - shutdown impossible"
NOTIFYFLAG ONLINE       SYSLOG+WALL   <== add +EXEC to this line
NOTIFYFLAG ONBATT       SYSLOG+WALL   ...
NOTIFYFLAG LOWBATT      SYSLOG+WALL   ...
NOTIFYFLAG FSD  SYSLOG+WALL           ...
NOTIFYFLAG COMMOK       SYSLOG+WALL   ...
NOTIFYFLAG COMMBAD      SYSLOG+WALL   ...
NOTIFYFLAG SHUTDOWN     SYSLOG+WALL   ...
NOTIFYFLAG REPLBATT     SYSLOG+WALL   ...
NOTIFYFLAG NOCOMM       SYSLOG+WALL   ...
NOTIFYFLAG NOPARENT     SYSLOG+WALL   up to this line