Cheers to all ! I had this problem for years but my Canadian friends finally listened to me/others and built a smart 200A panel for my clients.
 Not going to help your situation Dana but an FYI.
When paired with Schneider Electric XW Pro inverters [3], the Backup Control Switch (BCS) automatically disconnects from the grid during an outage,
 allowing the system to provide backup power to the home.

Certified to UL standards for USA, the Backup Control Switch is used for larger XW Pro systems requiring up to 200 A rated MID or service entrance installation.

Part number: 865-BCS-2200

Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail  offgridso...@sti.net
text 209 813 0060

On 2022-12-17 8:28 am, Dana Orzel via RE-wrenches wrote:

Hey All a Cheery Season to you all!

I inherited a backup system that had "failed". It was unwired, & poorly labeled.

1200 AHR AGM Battery - 1 Radian 8KW inverter - 200 amp Generac transfer switch - No solar - Feeding a 200 amp house panel.

First I explained the there were too many loads for an 8KW inverter. It could & may overload the 8KW inverter. They said "it had worked fine for 5 years & they were OK with it as is please get it back up"…

Replaced the existing Eaton transfer switch as the Generac controller was shot, with a Generac 200 amp Xfer switch complete with controller & transfer switch.

Rewired & had to recharge the 48 volt battery from 20volt back up to full with a pair of IOTA chargers in series.

The original trigger was 3 wires from the Radian to the 12 volt & AUX output to the input on the Generac controller. These were disconnected on the Generac end. So no clue or labeling there.

I called Outback & they called it Redneck engineering & send me a few articles to read.

Has anyone configured a backup in this manner?

All suggestions appreciated, thanks & wishing you all a safe & sane season!

Dana Orzel                              Great Solar Works, Inc.

C - 208.721.7003                       d...@solarwork.com

Idaho Contractor - # 028765         Idaho PV # 028374

www.greatsolarworks.com [1]            www.solarwor.com [2]

"Responsible Technologies for Responsible People since 1988"

P Please consider the environment before printing this email.

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


Links:
------
[1] http://www.greatsolarworks.com/
[2] http://www.solarwor.com
[3] https://solar.se.com/us/en/product/xw-pro-120-240v/
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to