Contact Info:
I am Rick Rys at R2Controls.  I worked at Foxboro for 20 years and have been
an independent contractor for the past 5 years.  I live nearby Foxboro, MA.
I continue to work for Foxboro in both development and applications areas
and I also work for some end users.  Occationally, I do have the chance to
offer my opinion on product directions and I have pushed for
reliable/powerful APXX/WPXX (i.e. Unix/Solaris seems best) platform (and
many other useful features) especially for their Chemical, Oil, and Gas
customers.

Rick Rys P.E.
Principal - R2 Controls
Process  Control Technology
1 Cherry Street
Mansfield, MA 02048
508-339-6633  Phone/Fax
508-846-7195  Cellular
www.R2controls.com



---
This list is neither sponsored nor endorsed by the Foxboro Company. All 
postings from this list are the work of list subscribers and no warranty 
is made or implied as to the accuracy of any information disseminated 
through this medium. By subscribing to this list you agree to hold the 
list sponsor(s) blameless for any and all mishaps which might occur due to 
your application of information received from this mailing list.

To be removed from this list, send mail to 
[EMAIL PROTECTED] 
with unsubscribe foxboro in the Subject. Or, send any mail to
[EMAIL PROTECTED]




RE: Constraint Control - OutSel Block

2001-09-12 Thread Rick Rys

Satish,

The OUTSEL block is set up to handle reset windup  block initialization
handling. It can be used where you have a normal PID loop that should be
bumplessly interupted when a second controlled variable reaches a constraint
target.  Let's say you were normally operating with a fixed and steady gas
flow to a vessel.  In case the vessel pressure was getting close to the
relief valve setting you decide that the normal feedrate must be cut.  You
set the SELOPT parameter to 2 for Low selection and add a second PID
Pressure control loop with a setpoint somewhat below the relief valve
setting. Properly configured: at the moment the pressure rises to the
setpoint of the pressure controller the flow control valve will just start
to close (from it's current position) and the loop will become a pressure
controller with a minimum flow constraint.  When the vapor removal rate from
the vessel is increased the pressure controller will open the flow control
valve until the flow setpoint is achieved and the flow controller will now
bumplessly resume control of the valve.  The SIGSEL block is possible but
the OUTSEL block was built for this specific application.  Many
implementations are possible. Hope this answered your question.

Rick Rys
R2Controls



---
This list is neither sponsored nor endorsed by the Foxboro Company. All 
postings from this list are the work of list subscribers and no warranty 
is made or implied as to the accuracy of any information disseminated 
through this medium. By subscribing to this list you agree to hold the 
list sponsor(s) blameless for any and all mishaps which might occur due to 
your application of information received from this mailing list.

To be removed from this list, send mail to 
[EMAIL PROTECTED] 
with unsubscribe foxboro in the Subject. Or, send any mail to
[EMAIL PROTECTED]




RE: GC Analyzer Control

2001-07-10 Thread Rick Rys

Technically, you should get superior performance by using a Sampled Data
PID Controller rather than a fixed scan PID. i.e. enabling the PID
execution only upon receipt of a new analyzer (maybe a GC) update. This is
the SPLCOP option in the PIDA. One item you did not mention that has a big
impact on the control effectiveness is the analyzer delay time.  I.e. when
the analyzer is giving a new update, how old is this data?  In a GC this
would be the time to transport the sample from the process to the analyzer
plus the time for the analyzer to complete it's result and set the sample
ready timer to on (elution time of the applicable component peaks for a GC).
Also the use of inferred property control (like analyzer to temperature
cascade for distillation for example) can be effective to catch upsets that
are fast relative to the analysis frequency mitigating the need for
improving the analyzer PID loop.  In this case the temperature PID loop
essentially handles the upset. The PIDTAU option (deadtime compensation)
might be considered in conjunction with the SPLCOP option to better handle
the sample delay. Prior to the PIDA feature we would typically just run a
fixed scan PID but filter the measurement with 2 lags in series (set for
about .2 and .5 times the sample interval in minutes). This, in conjuntion
with signal validity logic, was typically satisfactory, but not technically
optimal.  Some multivariable controllers (I think that PCL Connoisseur does
this, and I know that BOSS blending can do this) can make a similar
synchronization and PCL control technology inherently compensates for the
sample delays.  Few of these tricks would substitute for a well designed
fast sample loop, and a fast responding analyzer technology.  My vote is to
implement this in the PIDA rather than sequence blocks or programs as it
will be simpler and easy to maintain.  The validity logic for holding the
PID and alamring might include frozen signal and provisions to
automatically detect analyzer maintenance like calibration in case the
operator did not take the precaution of putting the loop into manual first.

Rick Rys



---
This list is neither sponsored nor endorsed by the Foxboro Company. All 
postings from this list are the work of list subscribers and no warranty 
is made or implied as to the accuracy of any information disseminated 
through this medium. By subscribing to this list you agree to hold the 
list sponsor(s) blameless for any and all mishaps which might occur due to 
your application of information received from this mailing list.

To be removed from this list, send mail to 
[EMAIL PROTECTED] 
with unsubscribe foxboro in the Subject. Or, send any mail to
[EMAIL PROTECTED]




RE: Open-loop detection on analog output cards

2001-05-10 Thread Rick Rys

Let's assume you have an FBM 04 with ECB type 2, and a simple AIN, PID(A),
AOUT analog control loop.  Next you remove the wiring at the FBM terminal
for the 4-20ma output for this channel.

The CP is good, the fieldbus is good, and the FBM is good. ECB Failsafe is
not enabled. The field wiring is bad (open), however, and the valve is
getting 0ma and thus going to it's failure state.  You will likely be
getting some alarms soon enough, but I understand why you might want to get
an alarm immediately.  This might be possible with intelligent transmitters,
but it is my understanding that the FBM04 is not smart enough to identify a
single open loop output.  Inputs would be caught by out of range, but I
don't think there is any way to detect a bad output short of a valve
position transmitter with some type of deviation alarming scheme.  In the
AOUT block the BAO when set to 1 has alarming looking at BAD (BO193AX Block
Book).  BAD is set from the OPSTAT of the ECB block (with some logic I could
not find), but the ECB is only setting the BAD based on communication
related errors (see ECB Block description) and not disconnected output
wires.  You can look at BAD, OPSTAT, or ECBSTA to verify that nothing is
showing as bad. Maybe someone else could verify this behavior as I didn't
check it on real hardware.

Rick Rys
R2 Controls



---
This list is neither sponsored nor endorsed by the Foxboro Company. All 
postings from this list are the work of list subscribers and no warranty 
is made or implied as to the accuracy of any information disseminated 
through this medium. By subscribing to this list you agree to hold the 
list sponsor(s) blameless for any and all mishaps which might occur due to 
your application of information received from this mailing list.

To be removed from this list, send mail to 
[EMAIL PROTECTED] 
with unsubscribe foxboro in the Subject. Or, send any mail to
[EMAIL PROTECTED]




RE: Daylight Savings

2001-04-24 Thread Rick Rys

Bo,

As a consultant, I have seen many customer systems and it seems most do
synch with the local time.  One FDA regulated site in the US did set their
I/A system to true GMT time, (i.e. timezone and DST did not match local
time).  In this way timestamped data and files had the correct times when
transferred to other machines in local time. This avoided confusing
timestamp conversions. Generally, they adapted to this quite well and were
able to make this work without incident.

Rick Rys
R2 Controls



---
This list is neither sponsored nor endorsed by the Foxboro Company. All 
postings from this list are the work of list subscribers and no warranty 
is made or implied as to the accuracy of any information disseminated 
through this medium. By subscribing to this list you agree to hold the 
list sponsor(s) blameless for any and all mishaps which might occur due to 
your application of information received from this mailing list.

To be removed from this list, send mail to 
[EMAIL PROTECTED] 
with unsubscribe foxboro in the Subject. Or, send any mail to
[EMAIL PROTECTED]




RE: Accumulator Block

2001-03-18 Thread Rick Rys

Loyd,
One item to be aware of is:  TIM in the CALC block gets the time from the CP
operating system (VRTX).  As the CP (operating system) is a slave timekeeper
that is updated about every 10 minutes it is possible to skip a particular
second if time is adjusted forward or if the time were set back, to pass
through the same seconds from midnight twice within a few seconds.  This
would rarely happen as there are 600 seconds in 10 minutes and it would
depend on the CP clock drift relative to the Master timekeeper clock drift
and unknown details of how the time is actually updated.  Some engineers
have had trouble with this i.e. when CALC blocks looked for a particular
point in time.  It's not clear how much a CP clock can drift in 10
minutes, but unlike your PC motherboard the CP must keep time with the
relatively poor clock of the Intel CPU as it has no battery backed real time
clock.  Ray Chouinard gives a pretty good example CALC.  If the clock update
were a few seconds backwards it would appear possible to get 2 resets within
a few seconds. Presumably this is tolerable.

Also upon a power-off CP reboot the CP time is unlikely to be correct
initially (I think it comes up Jan 1, 1986) until the master timekeeper sets
the time - a few minutes later.  CALC blocks using TIM will likely undergo
an abrupt change during this first time adjustment.  This may present
problems if you have one master accum block reset function used for multiple
CP's.

Rick Rys
R2Controls



---
This list is neither sponsored nor endorsed by the Foxboro Company. All 
postings from this list are the work of list subscribers and no warranty 
is made or implied as to the accuracy of any information disseminated 
through this medium. By subscribing to this list you agree to hold the 
list sponsor(s) blameless for any and all mishaps which might occur due to 
your application of information received from this mailing list.

To be removed from this list, send mail to 
[EMAIL PROTECTED] 
with unsubscribe foxboro in the Subject. Or, send any mail to
[EMAIL PROTECTED]




RE: Rolling average

2000-09-08 Thread Rick Rys

Alex suggests averaging 8 buckets from the DEADTIME block and this is very
practical. Some other suggestions are:

First DTOPT is set to 0 (DEADTIME block) so that the input is averaged over
the duration of bucket transfers (the so called rolling average feature).
If the DEADTIME block period is at least as fast as the variable to be
averaged, then every single available sample will be considered in the
rolling average (this precision may not be required).  If DT is set to 60
minutes then the 10 buckets will transfer every 6 minutes.  If the average
must be updated every 1 minute then 6 DEADTIME blocks could be ganged
together, but now several CALC, SELECTOR, or SEQUENCE blocks (60 sec period)
would be needed to average 60 buckets.  As required precision is not
specified, heck maybe a simple lag block would do.

Rick Rys



---
This list is neither sponsored nor endorsed by the Foxboro Company. All 
postings from this list are the work of list subscribers and no warranty 
is made or implied as to the accuracy of any information disseminated 
through this medium. By subscribing to this list you agree to hold the 
list sponsor(s) blameless for any and all mishaps which might occur due to 
your application of information received from this mailing list.

To be removed from this list, send mail to 
[EMAIL PROTECTED] 
with unsubscribe foxboro in the Subject. Or, send any mail to
[EMAIL PROTECTED]