On Mon, Apr 27, 2015 at 3:42 PM, James Hammond #!/bin/sh case $1 in onbatt) /sbin/upsmon -c fsd;; *) echo shutdown implemented;; esac root@unifi:/sbin# ./upssched-cmd.sh shutdown implemented root@unifi:/# upsmon -c fsd Network UPS Tools upsmon 2.7.3 I think you should pass $1 parameter to ./upssched-cmd.sh # ./upssched-cmd.sh onbatt The part of case should look like: #!/bin/sh case $1 in onbatt) /sbin/upsmon -c fsd ;; *) echo shutdown implemented ;; esac Also from upssched.conf: AT ONBATT * EXECUTE powerout So you need powerout instead of onbatt in your script. -- Best / С наилучшими пожеланиями *Pavel Potcheptsov* LLC EKTOS-Ukraine System administrator 1, Academika Proskury Mobile UA: +38 050 3642391 Home UA: +380 572 931115 61070 Kharkiv www.ektos.com.ua http://www.ektos.net/ E-mail: p...@ektos.net Skype: potcheptsov.pavel ___ Nut-upsuser mailing list Nut-upsuser@lists.alioth.debian.org http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser
Re: [Nut-upsuser] upssched setup
Hi Roger, I get: Apr 27 20:50:05 unifi upsmon[1022]: UPS ups on batteryApr 27 20:50:05 unifi upssched[2688]: Timer daemon startedApr 27 20:50:06 unifi upssched[2688]: New timer: onbatt (20 seconds)Apr 27 20:50:26 unifi upssched[2688]: Event: onbattApr 27 20:50:26 unifi upssched[2688]: exec_cmd(/sbin/upssched-cmd.sh onbatt) returned 126Apr 27 20:50:41 unifi upssched[2688]: Timer queue empty, exiting /etc/nut/upssched.conf CMDSCRIPT /sbin/upssched-cmd.shPIPEFN /etc/nut/upssched/upssched.pipeLOCKFN /etc/nut/upssched/upssched.lockAT ONBATT * START-TIMER onbatt 20AT ONLINE * CANCEL-TIMER onbatt /sbin/upssched-cmd.sh #!/bin/sh# Debugging: Log all calls to this scriptlogger -t upssched-cmd.sh Calling upssched-cmd.sh $1 case $1 in onbatt) /sbin/upsmon -c fsd;; *) echo shutdown implemented;; esac Any help gratefully received as this has got me beat. Most files have been chmod to 777 with no difference. Cheers, James Date: Mon, 27 Apr 2015 16:04:34 +0200 From: ro...@rogerprice.org To: nut-upsuser@lists.alioth.debian.org Subject: Re: [Nut-upsuser] upssched setup On Mon, 27 Apr 2015, James Hammond wrote: Roger, I did and it didnt work. Aha!, what does your upssched.conf look like? If you add the lines: # Debugging: Log all calls to this script logger -t upssched-cmd.sh Calling upssched-cmd.sh $1 to your /sbin/upssched-cmd.sh , what is reported if anything when it doesn't work? Cheers, Roger ___ Nut-upsuser mailing list Nut-upsuser@lists.alioth.debian.org http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser ___ Nut-upsuser mailing list Nut-upsuser@lists.alioth.debian.org http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser
Re: [Nut-upsuser] upssched setup
On Mon, 27 Apr 2015, James Hammond wrote: Hi Roger, I get: Apr 27 20:50:05 unifi upsmon[1022]: UPS ups on battery Apr 27 20:50:05 unifi upssched[2688]: Timer daemon started Apr 27 20:50:06 unifi upssched[2688]: New timer: onbatt (20 seconds) Apr 27 20:50:26 unifi upssched[2688]: Event: onbatt Apr 27 20:50:26 unifi upssched[2688]: exec_cmd(/sbin/upssched-cmd.sh onbatt) returned 126 Hi James, On opensuse, man exec says exec [command [argument ...]] ... If command is found, but it is not an executable utility, the exit status shall be 126. Check the man exec on Ubuntu, but it looks like an owner/permissions problem. For me /sbin/upssched-cmd.sh should have permissions -rwxr--r-- and owner upsd:daemon . Any help gratefully received as this has got me beat. Most files have been chmod to 777 with no difference. Please don't leave this 777 in place - it's too dangerous :-) Cheers, Roger ___ Nut-upsuser mailing list Nut-upsuser@lists.alioth.debian.org http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser
Re: [Nut-upsuser] upssched setup
Gents, Thanks, yes definitely a permissions problem. Roger pointed me in the correct direction with the command to add logging for the script. I have the shutdown working now but need to tighten up the permissions. Not too sure where to start with assigning the correct permissions. Cheers, James Date: Mon, 27 Apr 2015 21:25:45 +0100 From: n...@dana.org.uk To: nut-upsuser@lists.alioth.debian.org Subject: Re: [Nut-upsuser] upssched setup Hi, The exec is returning 126 - Command invoked cannot execute. A permission or command not executable problem.. Are you sure that the script is executable by the user running NUT? Do you have SELinux enabled? Regards, Neil. On 27/04/15 20:55, James Hammond wrote: Hi Roger, I get: Apr 27 20:50:05 unifi upsmon[1022]: UPS ups on battery Apr 27 20:50:05 unifi upssched[2688]: Timer daemon started Apr 27 20:50:06 unifi upssched[2688]: New timer: onbatt (20 seconds) Apr 27 20:50:26 unifi upssched[2688]: Event: onbatt Apr 27 20:50:26 unifi upssched[2688]: exec_cmd(/sbin/upssched-cmd.sh onbatt) returned 126 Apr 27 20:50:41 unifi upssched[2688]: Timer queue empty, exiting /etc/nut/upssched.conf CMDSCRIPT /sbin/upssched-cmd.sh PIPEFN /etc/nut/upssched/upssched.pipe LOCKFN /etc/nut/upssched/upssched.lock AT ONBATT * START-TIMER onbatt 20 AT ONLINE * CANCEL-TIMER onbatt /sbin/upssched-cmd.sh #!/bin/sh # Debugging: Log all calls to this script logger -t upssched-cmd.sh Calling upssched-cmd.sh $1 case $1 in onbatt) /sbin/upsmon -c fsd;; *) echo shutdown implemented;; esac Any help gratefully received as this has got me beat. Most files have been chmod to 777 with no difference. Cheers, James Date: Mon, 27 Apr 2015 16:04:34 +0200 From: ro...@rogerprice.org To: nut-upsuser@lists.alioth.debian.org Subject: Re: [Nut-upsuser] upssched setup On Mon, 27 Apr 2015, James Hammond wrote: Roger, I did and it didnt work. Aha!, what does your upssched.conf look like? If you add the lines: # Debugging: Log all calls to this script logger -t upssched-cmd.sh Calling upssched-cmd.sh $1 to your /sbin/upssched-cmd.sh , what is reported if anything when it doesn't work? Cheers, Roger ___ Nut-upsuser mailing list Nut-upsuser@lists.alioth.debian.org http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser ___ Nut-upsuser mailing list Nut-upsuser@lists.alioth.debian.org http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser ___ Nut-upsuser mailing list Nut-upsuser@lists.alioth.debian.org http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser ___ Nut-upsuser mailing list Nut-upsuser@lists.alioth.debian.org http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser
Re: [Nut-upsuser] upssched setup
Roger, Yes thanks I have been using your site as a guide (excellent writeup), trying to work out the difference between OpenSUSE and Ubuntu. I will re-visit this tomorrow and try to tighten up security. Cheers, James Date: Mon, 27 Apr 2015 23:06:37 +0200 From: ro...@rogerprice.org To: nut-upsuser@lists.alioth.debian.org Subject: Re: [Nut-upsuser] upssched setup On Mon, 27 Apr 2015, James Hammond wrote: ... Not too sure where to start with assigning the correct permissions. If it is of any help, you will see a full list of the permissions and owners I use in Table 1 at http://rogerprice.org/NUT.html#SOFT Cheers, Roger ___ Nut-upsuser mailing list Nut-upsuser@lists.alioth.debian.org http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser ___ Nut-upsuser mailing list Nut-upsuser@lists.alioth.debian.org http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser
Re: [Nut-upsuser] upssched setup
Hi, The exec is returning 126 - Command invoked cannot execute. A permission or command not executable problem.. Are you sure that the script is executable by the user running NUT? Do you have SELinux enabled? Regards, Neil. On 27/04/15 20:55, James Hammond wrote: Hi Roger, I get: Apr 27 20:50:05 unifi upsmon[1022]: UPS ups on battery Apr 27 20:50:05 unifi upssched[2688]: Timer daemon started Apr 27 20:50:06 unifi upssched[2688]: New timer: onbatt (20 seconds) Apr 27 20:50:26 unifi upssched[2688]: Event: onbatt Apr 27 20:50:26 unifi upssched[2688]: exec_cmd(/sbin/upssched-cmd.sh onbatt) returned 126 Apr 27 20:50:41 unifi upssched[2688]: Timer queue empty, exiting /etc/nut/upssched.conf CMDSCRIPT /sbin/upssched-cmd.sh PIPEFN /etc/nut/upssched/upssched.pipe LOCKFN /etc/nut/upssched/upssched.lock AT ONBATT * START-TIMER onbatt 20 AT ONLINE * CANCEL-TIMER onbatt /sbin/upssched-cmd.sh #!/bin/sh # Debugging: Log all calls to this script logger -t upssched-cmd.sh Calling upssched-cmd.sh $1 case $1 in onbatt) /sbin/upsmon -c fsd;; *) echo shutdown implemented;; esac Any help gratefully received as this has got me beat. Most files have been chmod to 777 with no difference. Cheers, James Date: Mon, 27 Apr 2015 16:04:34 +0200 From: ro...@rogerprice.org To: nut-upsuser@lists.alioth.debian.org Subject: Re: [Nut-upsuser] upssched setup On Mon, 27 Apr 2015, James Hammond wrote: Roger, I did and it didnt work. Aha!, what does your upssched.conf look like? If you add the lines: # Debugging: Log all calls to this script logger -t upssched-cmd.sh Calling upssched-cmd.sh $1 to your /sbin/upssched-cmd.sh , what is reported if anything when it doesn't work? Cheers, Roger ___ Nut-upsuser mailing list Nut-upsuser@lists.alioth.debian.org http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser ___ Nut-upsuser mailing list Nut-upsuser@lists.alioth.debian.org http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser ___ Nut-upsuser mailing list Nut-upsuser@lists.alioth.debian.org http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser
Re: [Nut-upsuser] upssched setup
On Mon, 27 Apr 2015, James Hammond wrote: ... Not too sure where to start with assigning the correct permissions. If it is of any help, you will see a full list of the permissions and owners I use in Table 1 at http://rogerprice.org/NUT.html#SOFT Cheers, Roger ___ Nut-upsuser mailing list Nut-upsuser@lists.alioth.debian.org http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser
Re: [Nut-upsuser] upssched setup
On Mon, 27 Apr 2015, James Hammond wrote: I am unable to get upssched working correctly as my UPS calls low battery too late and there is no way to change it. I am running Nut 2.7.3 on Ubuntu 14.04 I have made this script, called /sbin/upssched-cmd.sh #!/bin/sh case $1 in onbatt) /sbin/upsmon -c fsd;; *) echo shutdown implemented;; esac Hi, Just wondering, do you have a line in upssched.conf which specifies CMDSCRIPT /sbin/upssched-cmd.sh ? Roger___ Nut-upsuser mailing list Nut-upsuser@lists.alioth.debian.org http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser
Re: [Nut-upsuser] upssched setup
Roger, I did and it didnt work. Hence why I was trying to run just the shell script manually. I am not sure if this works though with the timer defined in it? Cheers, James Date: Mon, 27 Apr 2015 15:03:44 +0200 From: ro...@rogerprice.org To: nut-upsuser@lists.alioth.debian.org Subject: Re: [Nut-upsuser] upssched setup On Mon, 27 Apr 2015, James Hammond wrote: I am unable to get upssched working correctly as my UPS calls low battery too late and there is no way to change it. I am running Nut 2.7.3 on Ubuntu 14.04 I have made this script, called /sbin/upssched-cmd.sh #!/bin/sh case $1 in onbatt) /sbin/upsmon -c fsd;; *) echo shutdown implemented;; esac Hi, Just wondering, do you have a line in upssched.conf which specifies CMDSCRIPT /sbin/upssched-cmd.sh ? Roger ___ Nut-upsuser mailing list Nut-upsuser@lists.alioth.debian.org http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser ___ Nut-upsuser mailing list Nut-upsuser@lists.alioth.debian.org http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser
Re: [Nut-upsuser] upssched setup
On Mon, 27 Apr 2015, James Hammond wrote: Roger, I did and it didnt work. Aha!, what does your upssched.conf look like? If you add the lines: # Debugging: Log all calls to this script logger -t upssched-cmd.sh Calling upssched-cmd.sh $1 to your /sbin/upssched-cmd.sh , what is reported if anything when it doesn't work? Cheers, Roger ___ Nut-upsuser mailing list Nut-upsuser@lists.alioth.debian.org http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser