Re: [RE-wrenches] Three-phase off-grid

2011-10-22 Thread penobscotsolar
Ray,
The nice thing about the Exeltech (and what made me decide to use
them) is that they are not large. They are simply an array of 1 kw
inverters, allowing for multiple redundancy. Essentially, a 30 kw
three phase inverter is 31 small inverters, which, with the removal of
two nuts, can be swapped out in case of failure with the system
running and replaced. I, too, liked the idea of a separate charging
system and we will be splitting the system into 20 kw of PV charging
to each of three battery banks, one for each phase.

Daryl




 HI Allan;

 I haven't tried the large Exeltech inverters, but I could see some
 advantages to having a separate charging system, and keeping the
 inverters supplying stable power. Everytime a generator coughs or
 switches from one source to another, it seems to cause trouble. The
 generator could be sized smaller, since it wouldn't need any surge
 capability. It would always run the same charger, and the inverters
 would always run the same loads. I'd at least take another look at it
 for my next large project, but cost might be a limiting factor.
 Here's a Cummins diesel DC generator, just to think about:
 http://www.cumminspowerproducts.com/DCgensets/Other/1500.pdf

 Ray

 On 10/21/2011 4:56 PM, Gary Willett wrote:
 Alan: Thanks for setting me straight about 3-phasing the Outback
 Radian - I was not aware they are limited to parallel single phase
 applications.

 Regards,

 Gary Willett


 On 10/21/2011 15:29, Allan Sindelar wrote:
 Gary,
 I was surprised by this information, as I had presumed that both
 units were for single-phase only. So I checked.

 Mary Raub in tech support at Outback told me that the Radian works
 only in 120/240 single-phase, although they are stackable in parallel.

 Someone in Schneider tech support told me that the XW can be used in
 three-phase, up to six units (36 kW). Setup instructions are in
 Appendix D of the XW installation guide, found online at
 http://www.global-download.schneider-electric.com/85257849002EB8CB/all/5CC689CC3CB7FD10852578BF005EA759/$File/xw-hybrid-inverter-charger_installation-guide%28975-0239-01-01_rev-e%29.pdf.

 Thanks, Allan

 *Allan Sindelar*
 _Allan@positiveenergysolar.com_ mailto:al...@positiveenergysolar.com
 NABCEP Certified Photovoltaic Installer
 NABCEP Certified Technical Sales Professional
 New Mexico EE98J Journeyman Electrician
 *Positive Energy, Inc.*
 3201 Calle Marie
 Santa Fe, New Mexico 87507
 *505 424-1112*
 _www.positiveenergysolar.com_ http://www.positiveenergysolar.com/

 On 10/21/2011 2:01 PM, Gary Willett wrote:
 Allan:
 Also, you might consider using six to nine Schneider/Xantrex XW6048
 inverters, or six to nine Outback Radian GS8048 inverters, in a
 3-phase configuration, with a common battery bank.
 Also, Schneider/Xantrex has an 80A 600V charge controller that may
 be advantageous depending on the distance from the PV arrays to the
 inverters.

 Regards,
 Gary Willett, PE
 Icarus-Engineering LLC

 Icarus Solar Services LLC


 On 10/21/2011 10:17, Allan Sindelar wrote:
 Wrenches,
 We have been asked for a design for an off-grid system to reduce
 generator runtime for a mountain resort. Initial projections
 (consumption measurement results not yet available) suggest 15-20
 kW of PV and around 30 kW of inverter capacity. However, the
 generators and existing wiring are three-phase 120/208.

 My assumption is that our only options are a set of six Sunny
 Islands, or 9-12 Outback GVFX3648s. Are there any other options or
 approaches that I'm missing?

 Thank you, Allan
 --
 *Allan Sindelar*
 _Allan@positiveenergysolar.com_
 mailto:al...@positiveenergysolar.com
 NABCEP Certified Photovoltaic Installer
 NABCEP Certified Technical Sales Professional
 New Mexico EE98J Journeyman Electrician
 *Positive Energy, Inc.*
 3201 Calle Marie
 Santa Fe, New Mexico 87507
 *505 424-1112*
 _www.positiveenergysolar.com_ http://www.positiveenergysolar.com/




 ___
 List sponsored by Home Power magazine

 List Address:RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org



 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org

 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 

Re: [RE-wrenches] intermittent battery problem

2011-10-22 Thread David Katz
Ron,
I don't think it was the water.  It was probably the 10 hours they ran the 
generator that brought them up a bit.  If the water is low, the electrolyte is 
more concentrated and will make the s.g seem higher.  Adding water to the 
proper level will make the reading more accurate.
I still think they are pretty sulfated.  When they said they reached 29 volts 
in 5 minutes every morning with a charge of less than 30 amps (an assumption, 
since they are running a 2500 watt generator), that sounds like a battery with 
very little capacity.  The fact that they stayed at 25.7 all day was probably 
because of the 800 watt PV array and light loads.  It would be interesting to 
do a real equalization and a capacity test to see what is left of the batteries.
David

David Katz
CTO  Founder
AEE Solar Inc
P: 707 825-1200
F: 707 825-1202
dk...@aeesolar.com
www.aeesolar.com


From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Ron Young
Sent: Friday, October 21, 2011 11:39 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] intermittent battery problem

Hi Maverick  everyone,

I visited the site a couple of days ago and load tested the batteries, checked 
individual voltages in the string of six Surrette 4KS25's (4.3v each), checked 
all connections etc. The client told me that when they would go to bed battery 
volts read 25.7. Through the night this would seem to stay steady. About 4 a.m. 
as far as they could tell the voltage would drop to about 24.5. This happened 
without a load present and with no charging present (calm, no wind, no sun). 
They would start up the generator for five minutes in the morning and see the 
voltage come up to just above 29v then turn off the generator (a small Honda 
2500) and the voltage would settly at 25.7 and remain there most of the day 
even when using their light loads, some lights, phone system, laptop and the 
Sunfrost.

When checking the batteries I noticed they needed watering and mentioned this 
to the customer. The electrolyte was just over the plastic screen above the 
plates by about 1/4 inch. He said he had just watered them and always kept them 
filled. I replied that they were low and when he looked he said no, that's 
where I keep them! When I checked the specific gravity reading it was very rich 
reading around 1.275 - 1.280. I topped them up properly to about 1/4 inch below 
the bottom of the cell channel which took about 5 cups per each battery. Of 
course as soon as I topped them up the s.g. dropped to around 1.175. I told him 
to put the generator on for about ten hours and call me in the morning.

I heard from the client today and in the last two days the voltage has only 
dropped from 25.6 to 25.4 overnight and s.g. reading is at 1.260 or better so 
problem seems to be solved.

So it appears the battery was under watered for several years. I'm still not 
sure why this would result in a sudden voltage drop, especially in the middle 
of the night with no loads present and no charging. Any additional thoughts 
appreciated.

Best Regards,
Ron Young
earthRight Products - Solareagle.comhttp://Solareagle.com


On 2011-10-21, at 5:18 AM, 
maver...@mavericksolar.commailto:maver...@mavericksolar.com wrote:


Ron,

Just curious what the outcome was?

Thank you,

Maverick


Maverick Brown
BSEET, NABCEP Certified Solar PV Installer (r)
President  CEO
Maverick Solar Enterprises, Inc.
Office: 512-919-4493
Cell:512-460-9825

Sent from my HondaJet!


On 2011-10-11, at 12:11 PM, Maverick Brown [Maverick Solar] wrote:


Ron,

Sounds like you might have a voltage drop in the system at point of measurement.

A large voltage drop can happen for a few valid reasons.
1. High current demand.  Trimetric or better yet PentaMetric can show this 
demand.
2. Poor Cable connection. Visual / Thermal inspection or local Vdc measurement 
along the cable chain.
3. Low to moderate current demand with low SOC. Check the MX60 Logging function 
to see when the last day Float happened, i.e. how many minutes of Float in 
the last 60 days, etc. If there are none or few, then you still might be at a 
low SOC. (Trimetric or better yet PentaMetric can show the SOC as well).

Of course, not sure what happened to the Sunfrost, but a DC Clamp meter, might 
determine if it is normal now.

good luck,

Maverick



From: 
re-wrenches-boun...@lists.re-wrenches.orgmailto:re-wrenches-boun...@lists.re-wrenches.org
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Ron Young
Sent: Tuesday, October 11, 2011 2:00 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] intermittent battery problem
Wrenches,
I received some additional info from the customer this morning. They have asked 
me to hold off my visit until they get a few more clues but some of what they 
are telling me doesn't necessarily jive with a sulphated battery. Would 
appreciate comments - here's a quote from their email:

Hi Ron
Still having 

Re: [RE-wrenches] intermittent battery problem

2011-10-22 Thread Dave Palumbo
I have been following this topic over the past couple of weeks. What Dave
Katz said matches up with what I have seen over the years. Although it can
be difficult to diagnose battery issues from long distance there has been a
fair amount of information that points to sulfation. I think Mr. Katz is
right on the money. 

 

David Palumbo

Independent Power LLC 

462 Solar Way Drive

Hyde Park, VT 05655

www.independentpowerllc.com 

NABCEP Certified PV Installer

Vermont Solar Partner

23 Years Experience, (802) 888-7194 

 

 

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of David Katz
Sent: Saturday, October 22, 2011 11:01 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] intermittent battery problem

 

Ron,

I don't think it was the water.  It was probably the 10 hours they ran the
generator that brought them up a bit.  If the water is low, the electrolyte
is more concentrated and will make the s.g seem higher.  Adding water to the
proper level will make the reading more accurate.  

I still think they are pretty sulfated.  When they said they reached 29
volts in 5 minutes every morning with a charge of less than 30 amps (an
assumption, since they are running a 2500 watt generator), that sounds like
a battery with very little capacity.  The fact that they stayed at 25.7 all
day was probably because of the 800 watt PV array and light loads.  It would
be interesting to do a real equalization and a capacity test to see what is
left of the batteries.  

David

 

David Katz

CTO  Founder

AEE Solar Inc

P: 707 825-1200

F: 707 825-1202

dk...@aeesolar.com

www.aeesolar.com

 

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Ron Young
Sent: Friday, October 21, 2011 11:39 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] intermittent battery problem

 

Hi Maverick  everyone,

 

I visited the site a couple of days ago and load tested the batteries,
checked individual voltages in the string of six Surrette 4KS25's (4.3v
each), checked all connections etc. The client told me that when they would
go to bed battery volts read 25.7. Through the night this would seem to stay
steady. About 4 a.m. as far as they could tell the voltage would drop to
about 24.5. This happened without a load present and with no charging
present (calm, no wind, no sun). They would start up the generator for five
minutes in the morning and see the voltage come up to just above 29v then
turn off the generator (a small Honda 2500) and the voltage would settly at
25.7 and remain there most of the day even when using their light loads,
some lights, phone system, laptop and the Sunfrost.

 

When checking the batteries I noticed they needed watering and mentioned
this to the customer. The electrolyte was just over the plastic screen above
the plates by about 1/4 inch. He said he had just watered them and always
kept them filled. I replied that they were low and when he looked he said
no, that's where I keep them! When I checked the specific gravity reading it
was very rich reading around 1.275 - 1.280. I topped them up properly to
about 1/4 inch below the bottom of the cell channel which took about 5 cups
per each battery. Of course as soon as I topped them up the s.g. dropped to
around 1.175. I told him to put the generator on for about ten hours and
call me in the morning. 

 

I heard from the client today and in the last two days the voltage has only
dropped from 25.6 to 25.4 overnight and s.g. reading is at 1.260 or better
so problem seems to be solved. 

 

So it appears the battery was under watered for several years. I'm still not
sure why this would result in a sudden voltage drop, especially in the
middle of the night with no loads present and no charging. Any additional
thoughts appreciated.

 

Best Regards,

Ron Young

earthRight Products - Solareagle.com

 

 

On 2011-10-21, at 5:18 AM, maver...@mavericksolar.com wrote:

 

Ron,

 

Just curious what the outcome was?

 

Thank you,

 

Maverick

 

 

Maverick Brown

BSEET, NABCEP Certified Solar PV Installer R

President  CEO

Maverick Solar Enterprises, Inc.

Office: 512-919-4493

Cell:512-460-9825

 

Sent from my HondaJet!

 

 

On 2011-10-11, at 12:11 PM, Maverick Brown [Maverick Solar] wrote:

 

Ron,

 

Sounds like you might have a voltage drop in the system at point of
measurement. 

 

A large voltage drop can happen for a few valid reasons.

1. High current demand.  Trimetric or better yet PentaMetric can show this
demand.

2. Poor Cable connection. Visual / Thermal inspection or local Vdc
measurement along the cable chain.

3. Low to moderate current demand with low SOC. Check the MX60 Logging
function to see when the last day Float happened, i.e. how many minutes of
Float in the last 60 days, etc. If there are none or few, then you still
might be at a low SOC. (Trimetric or better yet PentaMetric can show the SOC
as well).

 

Of 

[RE-wrenches] Shell solar module question

2011-10-22 Thread David Katz
Wrenches,
I received the letter below from Photon magazine. I am posting it hear because 
it seems like a great way to get an answer:


Hi David,



Over the past year, Photon magazine's German publication has been reporting on 
significant delamination/hotspot problems reported with Shell Solar modules 
(RSM and S series) in Germany, and the customer-unfriendly response of 
Solarworld (which inherited the warranties when it acquired Shell Solar in 
2006).



Now, I am trying to figure out if similar problems are happening in North 
America -- e.g., how many of these defective modules were sold in North America 
and who are some of the main installers and system owners that are potentially 
affected. Can you recommend any sources that can help answer some of these 
questions? These panels were probably sold sometime between 2000 and 2006.



Thank you for your assistance,

Mike



Michael D. Matz





PHOTON USA Corp.

514 Bryant Street

San Francisco, California 94107, USA


David Katz
CTO  Founder
AEE Solar Inc
P: 707 825-1200
F: 707 825-1202
dk...@aeesolar.com
www.aeesolar.com
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Push-in Wire Connectors

2011-10-22 Thread Drake
Other examples of NEMA 3R enclosures are virtually all meter bases, 
outdoor service boxes, pole mounted disconnects, air conditioner and 
other roof mounted disconnects as well as wiring enclosures for 
changing wiring methods from underground conduits to building 
interiors, which generally make the connections with standard wire 
nuts.  Electricians use NEMA 3R enclosures a lot, and don't use 
sealed connectors inside.  As William points out, NEMA 3R may be 
superior to gasket sealed boxes in that 3R allows for any 
condensation to evaporate readily.



Drake Chamberlin
ATHENS ELECTRIC LLC
OH License 44810
CO license 3773
NABCEP Certified PV
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] intermittent battery problem

2011-10-22 Thread Ray Walters
I've seen behavior like that from Series 5000 Rolls that were only a 
year old, but chronically under charged. (20 amp load and the inverter 
would reach low shut off in minutes, 30 amp charge and it hit high 
voltage and quit charging) Any other battery, and I would assume its 
capacity was gone.
It seems to be something about their slightly different alloy in the 
plates, but I don't know for sure.
Enough time held at high enough voltage, and they seem to recover, but 
its definitely concerning to have a 1000 AH battery behave like a 10 AH 
battery. I found that if the voltage is held at the high side, that the 
charging amps would actually increase over time, which is opposite of 
other batteries. It must have a coating of sulfation on the plates that 
initially keeps the battery from working right, then with enough time it 
knocks that layer off to expose the actual plates and begin actual 
charging. (just a guess)
I'll actually set the charge amps down, and the voltage up at first, 
then when I see it start taking more amps, I set it back to normal 
charge parameters.


Ray

On 10/22/2011 9:01 AM, David Katz wrote:
When they said they reached 29 volts in 5 minutes every morning with a 
charge of less than 30 amps (an assumption, since they are running a 
2500 watt generator), that sounds like a battery with very little 
capacity.


David Katz

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] intermittent battery problem; ...Battery Sulfation

2011-10-22 Thread Larry Crutcher, Starlight Solar Power Systems
Hi Ron,

As many on this list have suggested, it sounds like a sulfated battery 
condition. In your last message you revealed something to me that absolutely 
confirms this but perhaps you didn't recognize it. 

Battery voltage readings are deceiving because they do not indicate capacity. 
25.7 volts sounds like a fully charged 24 volt bank, but is it? Only if the 
battery was at rest for 5-6 hours could you have some confidence that the bank 
was full at this voltage. But this is not the case because the bank is in daily 
use, always charging or discharging. However, there is one useful indication 
that voltage can be used for: detecting a sulfated battery. 

You mentioned that the the battery drops to 24.5 in the early AM without any 
heavy loads on. For the 4KS25 battery this equates to about 800AH at the 72 
hour rate. Then you said that the customer ran a 2500 watt generator for 5 
minutes and drove the voltage up to 29 volts. Here's the Ah-Ha moment: That is 
EXACTLY the behavior of a heavily sulfated battery bank. A fast rise in voltage 
indicates sulfation.  It is impossible for that tiny generator, or any charge 
source they own for that matter, to replace the hundreds of AH it would take to 
drive a healthy battery up to the absorb voltage of 29 volts. The bank is about 
45,000 watt hours (72h rate). There would have to be over 20,000 Wh removed to 
be at that voltage. How many Wh's are replaced in 5 minutes by a 2500 watt 
genny? I'm sure you are getting the picture. 

Why did this happen to these expensive batteries? Glad you asked. Battery 
plates are not uniformly efficient in the electrochemical process leaving some 
portions with lead sulfate even after 8 hours of charging. Unless these 
portions are cleared off regularly by achieving 100% SoC and occasional, 
thorough equalization, the amorphous sulfate will convert to a crystalline form 
and grow. 99% charge, if not corrected in time, will always cause premature 
battery failure. 

Undersized RE charging systems, or perhaps oversized batteries, is the culprit 
that contributes to this all too frequent phenomenon of chronic undercharging. 
I say contribute because there are other factors. Fact: it can take 10-12 hours 
to fully charge a lead acid battery. Fact: The time element of battery charging 
is a highly misunderstood part. With only a few daily sun-hours to work with, 
how do we get a battery charged with PV solar? Properly sizing the PV array to 
the battery AND consumption is critical. One method I think is essential for 
nearly all PV systems is use a generator and charger, appropriately sized to 
the battery. By bulk charging early in the AM you can reduce the finish time to 
perhaps 5-6 hours of constant voltage charging, something easily done with a PV 
system.

Ron, you might be able to recover some capacity in this bank if the sulfate has 
not formed hard crystals by now. You can try a very long charge time, up to 24 
hours, at high voltage, about 31 volts. You will need a larger generator. 
Monitor the temperature and reduce current if they get up to 125F internal. In 
our shop I have recovered sulfated batteries with high voltage charging, as 
much as 3Vpc (do not do this with any loads connected), at reduced current, 
about C*.05, and a 1 kHz pulser that I built. My findings over the years is the 
current will begin to rise very slowly, peak then drop if the recovery is 
working.

Sorry that this post is getting so long. There's just so much. OK, one last 
thing. In my last post to you I recommended a battery AH monitor. This problem 
could have been detected and perhaps prevented if they had one. 

Larry Crutcher
Starlight Solar Power Systems




On Oct 21, 2011, at 11:39 AM, Ron Young wrote:

 Hi Maverick  everyone,
 
 I visited the site a couple of days ago and load tested the batteries, 
 checked individual voltages in the string of six Surrette 4KS25's (4.3v 
 each), checked all connections etc. The client told me that when they would 
 go to bed battery volts read 25.7. Through the night this would seem to stay 
 steady. About 4 a.m. as far as they could tell the voltage would drop to 
 about 24.5. This happened without a load present and with no charging present 
 (calm, no wind, no sun). They would start up the generator for five minutes 
 in the morning and see the voltage come up to just above 29v then turn off 
 the generator (a small Honda 2500) and the voltage would settly at 25.7 and 
 remain there most of the day even when using their light loads, some lights, 
 phone system, laptop and the Sunfrost.
 
 When checking the batteries I noticed they needed watering and mentioned this 
 to the customer. The electrolyte was just over the plastic screen above the 
 plates by about 1/4 inch. He said he had just watered them and always kept 
 them filled. I replied that they were low and when he looked he said no, 
 that's where I keep them! When I checked the specific gravity reading it was 
 very rich reading