[RE-wrenches] Metering
Does anyone have a recommendation for a high quality meter that can be installed near the Main 200 Amp Electric Service Panel at the Point Of Interconnection in the Main Service Panel for a Grid Tied System The client wants to be able to track the electricity the household is actually using And how much the solar electric system is producing In the net metering arrangement with Central Hudson in NY, all the client gets to see on their bill is the net result of the solar credits subtracted from the actual usage. In this case, the solar generated credits is consistently zero because the usage exceeds the production Thanks Larry Brown Sun Mountain ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org
[RE-wrenches] Off Grid Battery Charging
Wrenches I have a client that we did an off grid system for about 4 years ago The system is performing well The client would like to keep charged her batteries in the winter with her stationary bicycle operating a small generator Right now she uses a grid connection that was available and she turns on a breaker if needed to charge the batteries in the winter through the inverter When the batteries are fully charged she turns the breaker back off No need for any back up other times of year That is the only use of the grid Her request was to be off grid This set up eliminated the need for her to have a generator for winter low light conditions So far all is working as designed But there is talk of adding a gas generator so that if the grid is down, there is a back up available The system has 16- AGM Concorde SunXtener Batteries configured in 2 strings of 8 batteries per string They are PVX 3050T 6 volt batteries operating at 48VDC They are charged from the PV Array by 2- Schneider Conext MPPT 80 600 Charge Controllers The system has a Schneider Conext XW+ 5548 Single Inverter Any thoughts or ideas of what equipment can be matched with a stationary bicycle that might give a trickle charge to the battery bank Anyone ever played with setting this up? She wants to try this out and see what is possible Get some winter exercise and perhaps keep the batteries as close to full without using the grid or a back up gas generator All suggestions welcome Thanks Larry Larry Brown Sun Mountain ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org
Re: [RE-wrenches] LiFePo4 Low Temp Charging Damage
My personal opinion is that you should not buy any lithium battery that does not provide adequate protection for all modes of operation. Freezing does not damage the battery; charging a frozen battery may damage it quickly. Trickle charging the battery is not the solution. There are two solutions: provide a heat source to keep the batteries above freezing or incorporate a temperature controller to disable the charger if the battery is unsafe to charge. Larry Crutcher > On May 21, 2021, at 8:44 AM, Mark Frye wrote: > > Folks, > > If I have a charger that does not have low battery charge cut-off, I can get > in trouble if I have a frozen pack and apply a charging voltage. > > But, if I start with a pack that is above freezing and keep a trickle charge > on it, can I keep that pack safe from freezing and damage? > > Or at some point, as ambient temperature drops, the pack will freeze and be > damaged anyway? > > Thanks, > > Mark Frye > > > ___ ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org
[RE-wrenches] Burkina Faso Off Grid
Wrenches I had a call from someone looking for an installer to do some off grid installations in Burkina Faso, Africa They have a school project they are working on If anyone does work in that part of the world would you get in touch and I will hook you up with Pascal Thanks Larry Larry Brown Sun Mountain 845-657-8096 sunmount...@netstep.net ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Ac Coupling
Kirpal Thanks for the recommendations If you have a diagram that would be most helpful and generous What Lithium Battery are you using with this configuration? Much Appreciated Larry Larry Brown Sun Mountain 845-657-8096 sunmount...@netstep.net On Jul 19, 2018, at 11:15 AM, Kirpal wrote: Larry.Outback Radian would work fine but you would need 2 of the 8kW inverters for your ~11kW GT inverter. Outback recommends a maximum 75% loading ratio when AC coupling. We have used a simple solid state relay controlled by the Aux Out of the Radian to turn off one leg of the SolarEdge or any other GT inverter essentially shutting off the GT inverter when a desired battery voltage is reached. As an aside, in earlier days when lead acid batteries where the main battery technology I didn't like this set up because it didn't allow multistage charging of the batteries leading to batteries only reaching approximately 80% SOC (bad for batteries) because there was no ability to taper charge (aside from frequency shift compatible inverters). But nowadays with Lithium batteries, which don't require multistage charging becoming more common this method of AC coupling is pretty attractive because the batteries don't care if they only reach a partial state of chargeEven though you can charge them more than 80% before kicking off the GT inverter. We have used this method successfully in addition to having DC coupling present in the same system as well. Let me know if you need a diagram. Sunny Regards, Kirpal Khalsa Oregon LRT#25 NABCEP Certified PV Installation Professional Oregon Solarworks LLC www.oregonsolarworks.com <http://www.oregonsolarworks.com/> 541-299-0402 On Thu, Jul 19, 2018 at 7:07 AM, Larry Brown mailto:sunmount...@netstep.net>> wrote: Does anyone have a recommendation on a battery based inverter to AC Couple with a Solar Edge 11400A-US Inverter that is already installed? I have been working a lot with the Schneider Conergy XW+ Inverters for off grid but have no experience AC Coupling them with a Solar Edge Inverter Any recommendations? Thanks Larry Larry Brown Sun Mountain 845-657-8096 sunmount...@netstep.net <mailto:sunmount...@netstep.net> ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org <mailto:RE-wrenches@lists.re-wrenches.org> Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html <http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html> List rules & etiquette: www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm> Check out or update participant bios: www.members.re-wrenches.org <http://www.members.re-wrenches.org/> ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
[RE-wrenches] Ac Coupling
Does anyone have a recommendation on a battery based inverter to AC Couple with a Solar Edge 11400A-US Inverter that is already installed? I have been working a lot with the Schneider Conergy XW+ Inverters for off grid but have no experience AC Coupling them with a Solar Edge Inverter Any recommendations? Thanks Larry Larry Brown Sun Mountain 845-657-8096 sunmount...@netstep.net ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Auger for ground mount
We have been using Techno Metal Posts Helical Piers with much success for many years Larry Larry Brown Sun Mountain 845-657-8096 sunmount...@netstep.net Sent from my iPhone > On Feb 9, 2018, at 11:48 AM, Chris Schaefer <ch...@solarandwindfx.com> wrote: > > While I've been using the Zilla platform with an auger attachment for a mini > excavator with good luck. With that said I'm looking at Nuance Energy and > their Osprey mount which requires a hammer drill. Anyone tried this yet? > > Christopher > >> On Fri, Feb 9, 2018 at 11:35 AM, Jerry Shafer <jerrysgarag...@gmail.com> >> wrote: >> Chris >> Azk around for a fence contractor, they generally have what you need >> Jerry >> >>> On Feb 9, 2018 5:05 AM, "Chris Mason" <cometenergysyst...@gmail.com> wrote: >>> I'm taking on construction of a ground mount system of about 30KW. My >>> previous experience has entailed using a utility truck mounted auger for >>> the holes but that's expensive. The soil type here is fairly soft, not >>> rock. There's no contractor available with a skid steer mounted auger. I >>> need at least four inch holes, three foot deep. Siz inch would be better. >>> What are the options? Any novel ideas? >>> We have a service truck with a 2 ton hydraulic crane, anything I can mount >>> to that? I don't mind fabricating brackets and mounts, welding parts to it. >>> >>> -- >>> Chris Mason >>> NABCEP Certified Solar PV Installer™ >>> Solar Design Engineer >>> Generac Generators Industrial technician >>> >>> www.cometsolar.com >>> 264.235.5670 >>> 869.662.5670 >>> Skype: netconcepts >>> >>> ___ >>> List sponsored by Redwood Alliance >>> >>> List Address: RE-wrenches@lists.re-wrenches.org >>> >>> Change listserver email address & settings: >>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >>> >>> List-Archive: >>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html >>> >>> List rules & etiquette: >>> www.re-wrenches.org/etiquette.htm >>> >>> Check out or update participant bios: >>> www.members.re-wrenches.org >>> >>> >> >> ___ >> List sponsored by Redwood Alliance >> >> List Address: RE-wrenches@lists.re-wrenches.org >> >> Change listserver email address & settings: >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >> >> List-Archive: >> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html >> >> List rules & etiquette: >> www.re-wrenches.org/etiquette.htm >> >> Check out or update participant bios: >> www.members.re-wrenches.org >> >> > > > > -- > Chris Schaefer’s > > Tel/Fax 585-229-2083 or Cell 585-748-1870 > 5115 South Hill Road ~ Canandaigua New York 14424 > www.solarandwindfx.com ~ E-mail: ch...@solarandwindfx.com > > > > Thomas Jefferson, the author of our great Constitution, once said, > "democracy" will cease to exist when you take away from those who are willing > to work and give to those who would not." > > ___ > List sponsored by Redwood Alliance > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > www.members.re-wrenches.org > ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
[RE-wrenches] Sunny Island 5048
Wrenches Does anyone have an empty original cardboard box for a Sunny Island 5048 Inverter? Please contact me off list Thanks Larry Larry Brown Sun Mountain sunmount...@netstep.net 845-657-8096 ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
[RE-wrenches] Transverter Total Smart Grid Solution
Have any wrenches had any experience with Heart Transverters http://www.transverter.com/ I have a client who wants to use one to transition from a grid tied system to an off the the grid system Thanks Larry Brown Sun Mountain ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
[RE-wrenches] These Wind Turbines Generate Energy Without any Blades | Digital Trends
Wrenches, Does anyone have any comments or knowledge on this new product about to enter the Renewable Energy world? Larry Larry Brown Sun Mountain http://www.digitaltrends.com/cool-tech/vortex-bladeless-wind-turbine-indiegogo/ ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Tesla Powerwall battery paired with solar
Michael, How do i access the marketing list? Thanks Larry Larry Brown Sun Mountain On May 2, 2015, at 8:07 PM, Michael Welch wrote: Hey gang. This has been interesting, but let's get the list back to wrenching. Let's move any further discussion to the RE-Marketing list, or the RE-Bitching list. Thanks. ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Copper bar current capacity?
I did see these AC 60Hz tables like your link. Is it the same for DC current? Seems like I read that there was a difference. Thank you, Larry Crutcher Starlight Solar Power Systems On 4/29/15 11:27 AM, August Goers wrote: Larry, There are many resources for this online. A quick search for copper bar current rating chart yields results like this: http://www.watteredge.com/pdf/Ampacity_Tables.pdf Best, August -Original Message- From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Larry Sent: Wednesday, April 29, 2015 11:04 AM To: RE-wrenches Subject: [RE-wrenches] Copper bar current capacity? Hi Wrenches, In building lithium battery systems, I have many components that need to be connected in series from the battery. Sometimes the space is very limited making it difficult to bend 2/0 cables. I would like to use copper flat bar and make parts to replace the cables. Does anyone know how much current I can run through copper bar based on its size? For example, 1 or 3/4 wide by .0625 up to .125 thick. The pieces will only be a few inches long and bolted to solenoids, shunt and terminal posts. -- Thank you, Larry Crutcher Starlight Solar Power Systems ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.htm l List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
[RE-wrenches] Copper bar current capacity?
Hi Wrenches, In building lithium battery systems, I have many components that need to be connected in series from the battery. Sometimes the space is very limited making it difficult to bend 2/0 cables. I would like to use copper flat bar and make parts to replace the cables. Does anyone know how much current I can run through copper bar based on its size? For example, 1 or 3/4 wide by .0625 up to .125 thick. The pieces will only be a few inches long and bolted to solenoids, shunt and terminal posts. -- Thank you, Larry Crutcher Starlight Solar Power Systems ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Manufacturers warranty......
Hi Bill, Because of the nature of my business, we have designed and installed thousands of small RE systems. As a result I install a much higher volume of components and consequently deal with a greater number of failed units. Over the last 14 years, Magnum Energy and Kyocera are the only companies that have offered hassle free compensation for labor. Magnum has established time for each repair whereas Kyocera pays for all of our RR time. Fronius? Took me a year and many arguments, pleading, emails and phone calls to get them to cough up payment for an inverter that _they insisted_ I return to them. (BTW, this was the 3rd inverter swap) Then, instead of mailing me a check, they issued a credit to Sunwize that only applied to future Fronius purchases, something which I will never do again. A boat load of crap later I got the credit applied to my account. Larry Crutcher Starlight Solar Power Systems On 4/21/15 10:03 PM, frenergy wrote: My recent experience with SMA was $150 for the warranty change out of one of their string inverters. It was a significant hassle and took months to receive a check. You have to know that they offer the $150, If you don't ask, they won't offer it. Whereas Fronius almost insists they pay you $250 for a warranty change out, easy and prompt. SMA used to ship from Rocklin, CA, now you have to wait for it to come from Colorado. Anybody know Magnum's policy? Bill Feather River Solar Electric ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Gen preheat in cold climates
About the carb heat idea...LP is a liquid at -44°F. The liquid does not combust, it must be vaporized. As the ambient temperature drops closer to the LP liquid temperature, there would be a reduction in how fast liquid is vaporizing and therefor a reduction in volume. What you need in cold weather is enough volume to maintain at least 11 wc while cranking or running the engine. You can test the vapor pressure with a manometer while cranking to verify if this is the problem. If this is the reason the engine does not run, my thoughts are that heating the LP regulator would be much more economical from an energy standpoint, than heating the whole engine block. Perhaps an insulated enclosure with silicone heaters appropriately attached would work. They are available in many DC or AC and at various voltages. Larry Crutcher Starlight Solar Power Systems On 4/2/15 10:34 PM, Allan Sindelar wrote: Gary, Mac's approach is intelligent and will work well, as an automated system with the right hardware. We took a quite different approach on a somewhat similar scenario in 2009. This was a Kohler 8.5REZ, with the electric carb heater and AC charter for the starting battery. No block heater, but that could have been handled the same way. The inverter was a Magnum MS4024PAE, but that doesn't matter here. When we ran the bundle of gennie output conductors, we added a separate load circuit conductor, on its own breaker in the system E-Panel. Here's an excerpt from the original proposal description about our approach: The unit uses an electronic generator controller with modest (estimated at 200-700 mA, depending on state of operation) draw on the starting battery. This controller drops to minimal “sleep” draw automatically after 48 hours of non-operation. This generator does not have a starting battery charging coil, but rather uses a separate AC battery trickle charger to maintain the battery. I will install a 20W PV module and small charge controller on the generator to keep the starting battery charged. I will also install the AC charger to operate whenever the generator is running. While this combined setup has worked successfully for other installers with whom I have spoken, if this proves insufficient I can later add a switch and relay to allow the charger to also operate off of inverter AC if ever needed. The unit also requires a built-in carburetor heater to operate during cold weather. This heater is normally controlled by a thermostat to conservatively come on at or below 40°F, which would mean that it would operate nearly continuously during Taos’ winter months, draining the PV system. My solution is to put the carburetor heater on a manual mechanical one-hour time switch located at the generator; you will activate the heater through this switch 15-30 minutes before starting the generator. This may not work for you. This is a modern doublewide serving as a seasonal family meeting place, rather than a full time residence. With our usual sunny winters, we figure that if nobody is there, loads are minimal, and we don't want automatic (unattended) generator operation. I think we used a DG WP box inside the generator enclosure, with a mechanical timer (maybe one-hour) controlling a GFCI receptacle, with carb heater and battery charger plugged in. I hope that gives you some ideas you can use. *Allan Sindelar* al...@sindelarsolar.com mailto:al...@sindelarsolar.com NABCEP Certified PV Installation Professional NABCEP Certified Technical Sales Professional New Mexico EE98J Journeyman Electrician Founder (Retired), Positive Energy, Inc. *505 780-2738 cell* ** ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Gen preheat in cold climates
Chris, After I hit the send button, I thought about how a small generator or gas grill will use tank pressure through a vapor regulator. If this generator is plumbed that way, there lies a problem that your solution of heating the tank will work with. Personally I would not plumb a generator with vapor lines from the tank, especially is it is a long distance away. Since Gary said this was a large system, I am assuming it is liquid delivery to the generator. Gary, is the LP to the generator vapor or liquid from the tank? Larry On 4/3/15 10:56 AM, Chris Mason wrote: Heating the regulator won't help if the propane is not vapourizing. You would need to heat the tank. However, you do not need to heat it very much, just enough to let it vapourize. Think about putting it somewhere with a little heat, or burying it. On Fri, Apr 3, 2015 at 1:51 PM, Larry la...@starlightsolar.com mailto:la...@starlightsolar.com wrote: About the carb heat idea...LP is a liquid at -44°F. The liquid does not combust, it must be vaporized. As the ambient temperature drops closer to the LP liquid temperature, there would be a reduction in how fast liquid is vaporizing and therefor a reduction in volume. What you need in cold weather is enough volume to maintain at least 11 wc while cranking or running the engine. You can test the vapor pressure with a manometer while cranking to verify if this is the problem. If this is the reason the engine does not run, my thoughts are that heating the LP regulator would be much more economical from an energy standpoint, than heating the whole engine block. Perhaps an insulated enclosure with silicone heaters appropriately attached would work. They are available in many DC or AC and at various voltages. Larry Crutcher Starlight Solar Power Systems ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Gen preheat in cold climates
Hi Chris, LP will boil (vaporize) at -44° so until your ambient temperature is below that it is vaporizing. Heating the tank will increase the liquid and vapor pressure in the tank but it is still liquid, not vapor, that is plumbed to a cold regulator, or vaporizer if they have one, where the vaporization takes place for the engine. I can't see that increase tank temperature would solve the issue. In 1981 I bought a truck with dual fuel capability. The J-valve regulator had liquid heater lines from the coolant system to heat the LP liquid at the point of vaporization. The tank was in the bed and never heated. In very cold weather I had to start the engine on gas then switch to LP after hot water hit the regulator. All worked well with a warm regulator. Larry On 4/3/15 10:56 AM, Chris Mason wrote: Heating the regulator won't help if the propane is not vapourizing. You would need to heat the tank. However, you do not need to heat it very much, just enough to let it vapourize. Think about putting it somewhere with a little heat, or burying it. On Fri, Apr 3, 2015 at 1:51 PM, Larry la...@starlightsolar.com mailto:la...@starlightsolar.com wrote: About the carb heat idea...LP is a liquid at -44°F. The liquid does not combust, it must be vaporized. As the ambient temperature drops closer to the LP liquid temperature, there would be a reduction in how fast liquid is vaporizing and therefor a reduction in volume. What you need in cold weather is enough volume to maintain at least 11 wc while cranking or running the engine. You can test the vapor pressure with a manometer while cranking to verify if this is the problem. If this is the reason the engine does not run, my thoughts are that heating the LP regulator would be much more economical from an energy standpoint, than heating the whole engine block. Perhaps an insulated enclosure with silicone heaters appropriately attached would work. They are available in many DC or AC and at various voltages. Larry Crutcher Starlight Solar Power Systems ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] ITC
On 3/27/15 1:04 PM, Gary Willett wrote: but if a business owned PV system is involved, and does not involve a personal 1040 tax return /_or a residential PV system, the 30% residential energy credit does not apply_/ - the Form 3468 investment tax credit is used. Regards, Gary Willett Icarus Solar Irving TX Hi Gary, The PV system does not have to be a residential system to qualify. The tax credit applies to any dwelling unit owned by the individual including a recreational vehicle. We have had hundreds of customers take the credit over the last few years for systems installed on RV's. Thank you, Larry Crutcher Starlight Solar Power Systems www.starlightsolar.com (928) 342-9103 ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Charging Multiple Battery Banks
Keep in mind that the Midnite controller has a combined PV and bat. negative and the Blue Sky requires isolated PV and bat. negative. Larry Crutcher Starlight Solar Power Systems On 3/24/15 6:11 PM, Jeremy Rodriguez wrote: The thought was to charge the batteries for a new building utilizing an SW4024 with new classic controller and new L A batteries, and once those batteries are charged send the PV to the house system which is the 48v setup with dual outback inverters and dual SB3048 CCs. Lead acid batteries as well. 3 years old I've never had this come up in 16 years! Jeremy Rodriguez All Solar, Inc. 1463 M Penrose Colorado 81240 Sent by Jeremy's iPhone. Sorry for typos and shorthand! On Mar 24, 2015, at 5:31 PM, Ray Walters r...@solarray.com mailto:r...@solarray.com wrote: What's the reasoning behind two different battery banks at different voltages? What is the other equipment involved: batteries type, age, inverters, etc.? R.Ray Walters CTO, Solarray, Inc Nabcep Certified PV Installer, Licensed Master Electrician Solar Design Engineer 303 505-8760 On 3/24/2015 5:07 PM, Jeremy Rodriguez wrote: It would be 2kw of PV Jeremy All Solar Penrose, CO Date: Tue, 24 Mar 2015 12:17:20 -1000 From: jerrysgarag...@gmail.com To: re-wrenches@lists.re-wrenches.org Subject: Re: [RE-wrenches] Charging Multiple Battery Banks How big of a system are you looking at as some of the smaller charge controllers are auto sensing Jerry On Tue, Mar 24, 2015 at 12:11 PM, Jeremy Rodriguez allsolarjer...@msn.com mailto:allsolarjer...@msn.com wrote: Wrenches, I have a client that wants to charge a 24v battery bank and a 48v bank with the same array. Different charge controllers, with some type of relay is what I was thinking, and using the controller's aux. 12v output for the relay control. The primary battery to be charged would be the 24v bank, then once it is fully charged, divert the pv to the secondary controller at the 48v bank. Any comments or recommendations on this would be helpful. Jeremy Rodriguez All Solar Inc. Penrose, CO ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org mailto:RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html http://www.mail-archive.com/re-wrenches%40lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org http://www.members.re-wrenches.org ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org ___ List sponsored by Redwood Alliance List Address:RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org mailto:RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org http://www.members.re-wrenches.org ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org ___ List sponsored by Redwood Alliance List Address: RE
Re: [RE-wrenches] Charging Multiple Battery Banks
The Blue Sky should still work as long as he switches PV positive and negative. However, I like the idea of charging just the 24 volt system and feeding AC to the Outbacks to charge the 48 volt bank. A little more loss but mush easier to implement. You could easily control when AC is fed to the 48 volt system based on voltage of the 24 volt battery. Larry On 3/25/15 10:24 AM, Ray Walters wrote: Hi Jeremy; I usually would combine both buildings all into one system, KISS principle, and also less cost. Later when those batteries die, replace with a properly sized bank. I also wouldn't be building a new system around an SW4024, those are getting really dated. Great inverter, but they don't last forever. They have excellent resell value on Ebay for folks that need replacements in dual and quad systems. Having said that, Jerry's idea of 2 controllers on one array sounds like it would work, but not with Blue Sky because of the grounding as Larry mentioned. R.Ray Walters CTO, Solarray, Inc Nabcep Certified PV Installer, Licensed Master Electrician Solar Design Engineer 303 505-8760 On 3/25/2015 10:36 AM, Larry wrote: Keep in mind that the Midnite controller has a combined PV and bat. negative and the Blue Sky requires isolated PV and bat. negative. Larry Crutcher Starlight Solar Power Systems On 3/24/15 6:11 PM, Jeremy Rodriguez wrote: The thought was to charge the batteries for a new building utilizing an SW4024 with new classic controller and new L A batteries, and once those batteries are charged send the PV to the house system which is the 48v setup with dual outback inverters and dual SB3048 CCs. Lead acid batteries as well. 3 years old I've never had this come up in 16 years! Jeremy Rodriguez All Solar, Inc. 1463 M Penrose Colorado 81240 Sent by Jeremy's iPhone. Sorry for typos and shorthand! On Mar 24, 2015, at 5:31 PM, Ray Walters r...@solarray.com mailto:r...@solarray.com wrote: What's the reasoning behind two different battery banks at different voltages? What is the other equipment involved: batteries type, age, inverters, etc.? R.Ray Walters CTO, Solarray, Inc Nabcep Certified PV Installer, Licensed Master Electrician Solar Design Engineer 303 505-8760 On 3/24/2015 5:07 PM, Jeremy Rodriguez wrote: It would be 2kw of PV Jeremy All Solar Penrose, CO Date: Tue, 24 Mar 2015 12:17:20 -1000 From: jerrysgarag...@gmail.com To: re-wrenches@lists.re-wrenches.org Subject: Re: [RE-wrenches] Charging Multiple Battery Banks How big of a system are you looking at as some of the smaller charge controllers are auto sensing Jerry On Tue, Mar 24, 2015 at 12:11 PM, Jeremy Rodriguez allsolarjer...@msn.com mailto:allsolarjer...@msn.com wrote: Wrenches, I have a client that wants to charge a 24v battery bank and a 48v bank with the same array. Different charge controllers, with some type of relay is what I was thinking, and using the controller's aux. 12v output for the relay control. The primary battery to be charged would be the 24v bank, then once it is fully charged, divert the pv to the secondary controller at the 48v bank. Any comments or recommendations on this would be helpful. Jeremy Rodriguez All Solar Inc. Penrose, CO ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Load testing Lithium battery bank
Hi Jarmo, I agree and recognize your urgency in making us aware of the proper use and charging of Li-ion batteries as well as the dangers of mistreating them. As an early adopter myself, I am very cautious in my approach even to the point of refusing to sell to some customers. Lithium battery technology is in a state of rapid evolution. Not wanting to harp on the GBS brand that I sell, but one of your points goes to prove the safety of their integrated approach. You said, ...all it takes is one poor connection or broken temp sensor on one cell. The GBS EMS system has cell level sensors for temperature (and other data) and each sensor board requires constant communication with the CPU. If the EMS fails to communicate any information with any cell, the CPU immediately shuts down both safety solenoids, disconnecting the battery. With the non integrated systems, failures that don't report information to the management system could lead to disaster. Please keep offering us the knowledge you are gaining as I am a firm believer that Lithium technology is a large part of the inevitable replacement the aged lead battery. Larry Crutcher Starlight Solar Power Systems On 3/17/15 6:11 PM, jarmo.venalai...@schneider-electric.com wrote: Hi: I may sound like I'm a detractor against using Lion, but that's not it. What I want to bring to light is that, being as the technology is new, not all the issues are known and there are things to learn for all early adopters in the foreseeable future. From what I can gather the framework for the issues lies in that Lion technology is based on intercalation, that is, a reversible insertion and removal of Li molecules into compounds with microscopically layered structures. This predicates that there must be no chemical reaction in the battery, but rather only the shelving of the highly reactive Li ions. If there are any chemical reactions taking place, then in the least the battery performance is compromised and in the most there is a thermal event or worse There are some very robust Lion battery packs, a favorite of mine being from a local company from Vancouver, (well Richmond, which is a suburb of Vancouver). It's a small company, but they have designed, developed, built and successfully approved their 6 kWh Lion pack for use in large car ferries in Scandinavia. The ferries have stacks of these packs in the 100's, in the MWh size. It can be done. What I'm advocating is that its best to work with companies that have the time, interest and resources to work through the wrinkles, and if not, then carefully put in reliable and precise BMS circuitry which includes things like fail safe circuits for single point failures of critical sensing circuits, the foremost of which is cell temperature. When you're pushing large currents, all it takes is one poor connection or broken temp sensor on one cell.. Here's a link to the Lion battery pack manufacturer, Corvus, http://corvus-energy.com/ I know they do a good job, but they're not cheap, for now... JARMO * Jarmo Venalainen* | *Schneider Electric **| Xantrex Brand* | *CANADA* | *Sales Application Engineer* * Phone:* +604-422-2528 | *Tech Support:* 800-670-0707 | *Mobile:* +604-505-0291 * Email:* _jarmo.venalainen@schneider-electric.com_ mailto:jarmo.venalai...@schneider-electric.com | *Site:*_www.Xantrex.com_ http://www.xantrex.com/ | *Address:* 3700 Gilmore Way, Burnaby, BC V5G4M1 http://www.xantrexrebate.com/ http://www.xantrex.com/ https://www.facebook.com/Xantrex https://twitter.com/Xantrex https://twitter.com/Xantrex ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Load testing Lithium battery bank
Not at all. The EMS boards are well built and are protected under a cover with the terminals. I have not had any failures of the EMS boards or any failure to communicate with them. Larry On 3/18/15 4:52 PM, Bruce Erickson wrote: If a communication failure with a single cell (not even an actual fault) can cause total battery shutdown, does that lead to a lot of nuisance tripping? *Bruce Erickson* Mendocino Solar Service PO Box 1252 Mendocino, CA 95460 707-937-1701 707-937-1741 fax br...@mendocinosolar.com mailto:br...@mendocinosolar.com /Celebrating 20 Years in Solar!/1994-2014 ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Load testing Lithium battery bank
Hi Chris, Thanks for the recommendation. I received a quote from Comrent$1800 to rent a load for 1 week. Ouch! I'll go with the $10 water elements and a little fabrication time. I have AH counters and controllers to stop the discharge. Thank you, Larry Crutcher Starlight Solar Power Systems On 3/17/15 2:38 PM, Chris Mason wrote: Load banks are for rent, I am in the generator business and it is a common requirement to provide a load bank upon installation. http://www.comrent.com/Solutions/load-bank-rentals.html ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Load testing Lithium battery bank
I was thinking of mounting the water heat elements into an aluminum plate, laying the plate flat over a 55 gallon drum and filling the water level up to the plate. Stratified water may make the top pretty hot but I guess it will work. Larry On 3/17/15 1:07 PM, Ray Walters wrote: Those look like your solution. Also water can take more heat with less trouble than air heaters. I've had air heaters start melting things, etc. You can just install those in the side of a 55 gal barrel with a bulkhead fitting, or yes, weld the appropriate plumbing fitting to the side of the barrel. Might even be able to install them into a section of pipe with Ts and run water through it to cool the elements. R.Ray Walters CTO, Solarray, Inc Nabcep Certified PV Installer, Licensed Master Electrician Solar Design Engineer 303 505-8760 On 3/17/2015 1:40 PM, Larry wrote: Hey Ray, I remember seeing huge banks of light bulbs as loads back in the early 70's. I need to test the entire bank as one unit as the first cell of 32 to reach 2.8 volts determines the capacity for the bank. I just saw Home Depot has a 2kW 120 volt water heater for $10. Guess I need to do some welding. Thank you, Larry Crutcher Starlight Solar Power Systems On 3/17/15 11:59 AM, Ray Walters wrote: Hi Larry, I think you hit on the best load already: water heater elements rated for 120 v. We have also used dump loads for wind turbines like the air heating elements from Bergey, but they are only about 1 kW each. Another possible source are the resistor banks for old golf carts (before they had controllers, they used resistor banks to operate at slow speeds) A very long time ago, an inverter company had a demonstration that used a large bank of incandescent light bulbs. They used to make a 300 watt bulb for mining, so 33 of those would work. (maybe a few more bulbs, since your voltage is bit lower than 120 v) Cheap electric space heaters would work too. You also might look around at an electronics surplus store. Whatever you do, it sounds like a lot of time and work to set up. Any chance of doing a smaller load test for subsets of the total bank? You might be able to use a standard 12 v battery load tester then. Good Luck. R.Ray Walters CTO, Solarray, Inc Nabcep Certified PV Installer, Licensed Master Electrician Solar Design Engineer 303 505-8760 On 3/17/2015 12:41 PM, Larry wrote: I am repairing and restoring a pair of poorly designed lithium-ion battery bank that suffered over discharge, damaging many cells. After cell replacement I need to perform a discharge test with a 10kW load to verify the remaining capacity. The battery voltage is 105 volts @ 100% SoC and 89.6 volts @ 0% I would like advice on how I can create an economical 10kW load. Water heating element? Wire wound resistors? Are there any GT inverters that will operate at these voltages? Thanks. ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
[RE-wrenches] Load testing Lithium battery bank
I am repairing and restoring a pair of poorly designed lithium-ion battery bank that suffered over discharge, damaging many cells. After cell replacement I need to perform a discharge test with a 10kW load to verify the remaining capacity. The battery voltage is 105 volts @ 100% SoC and 89.6 volts @ 0% I would like advice on how I can create an economical 10kW load. Water heating element? Wire wound resistors? Are there any GT inverters that will operate at these voltages? Thanks. -- Larry Crutcher Starlight Solar Power Systems ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Load testing Lithium battery bank
Hi Jarmo, One of the reasons I chose to sell and install GBS batteries is the chemistry is safer, they have vent caps (like AGM) and they offer an integrated solution where the battery, EMS/BMS and CPU are all designed specifically for each other instead of adding various parts from different manufacturers. The chemistry is LFMP (lithium iron manganese) not LFP. There are seven monitored fault events, including temperature, current and voltage, that will disconnect the battery from any load or any charge source. Since we are installing in RV's, there are multiple charge sources and all must be controlled. The systems I design do this very well. Also, our charge and discharge rates are far lower than the industry normally expects; rarely reaching .5C. I have seen private videos of destructive testing of GBS cells. Steel rods fired through entire packs; slow crush tests from top and sides, impact tests, even cells blown away on a gun range (that was more for fun I think as not too likely you will experience that). No fire, no thermal events. Bottom line for me is these are likely the safest Lithium battery I can offer. Many customers have already had shut down events because they were not being responsible. A simple reset and they're back in business. What was the lithium chemistry that you had trouble with? Thank you, Larry Crutcher On 3/17/15 12:49 PM, jarmo.venalai...@schneider-electric.com wrote: Hi: Please be careful when working with solar system size Lithium packs on the cell level. We have been doing on-going testing with Lion battery packs from various suppliers and even with their built in temp sensors and other BMS circuits, have already had two thermal events. Lion is very unforgiving with regards low state of charge, high state of charge, temperature (110F is the max temp at which they should be charged and 140F is the max they can handle). Given the low thermal mass of Lion cells, a high rate of discharge or charge quickly gets the cell temperature into the 110F+ range. As soon as you cross the line things start happening and if the BMS doesn't put a stop to it by turning the battery pack off, it's a very quick slide down the hill from there. JARMO _ * Jarmo Venalainen* | *Schneider Electric **| Xantrex Brand* | *CANADA* | *Sales Application Engineer* * Phone:* +604-422-2528 | *Tech Support:* 800-670-0707 | *Mobile:* +604-505-0291 * Email:* _jarmo.venalainen@schneider-electric.com_ mailto:jarmo.venalai...@schneider-electric.com | *Site:*_www.Xantrex.com_ http://www.xantrex.com/ | *Address:* 3700 Gilmore Way, Burnaby, BC V5G4M1 http://www.xantrexrebate.com/ http://www.xantrex.com/ https://www.facebook.com/Xantrex https://twitter.com/Xantrex https://twitter.com/Xantrex *** Please consider the environment before printing this e-mail From: Larry la...@starlightsolar.com To: RE-wrenches re-wrenches@lists.re-wrenches.org, Date: 03/17/2015 11:41 AM Subject:[RE-wrenches] Load testing Lithium battery bank Sent by:RE-wrenches re-wrenches-boun...@lists.re-wrenches.org ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Load testing Lithium battery bank
Hey Ray, I remember seeing huge banks of light bulbs as loads back in the early 70's. I need to test the entire bank as one unit as the first cell of 32 to reach 2.8 volts determines the capacity for the bank. I just saw Home Depot has a 2kW 120 volt water heater for $10. Guess I need to do some welding. Thank you, Larry Crutcher Starlight Solar Power Systems On 3/17/15 11:59 AM, Ray Walters wrote: Hi Larry, I think you hit on the best load already: water heater elements rated for 120 v. We have also used dump loads for wind turbines like the air heating elements from Bergey, but they are only about 1 kW each. Another possible source are the resistor banks for old golf carts (before they had controllers, they used resistor banks to operate at slow speeds) A very long time ago, an inverter company had a demonstration that used a large bank of incandescent light bulbs. They used to make a 300 watt bulb for mining, so 33 of those would work. (maybe a few more bulbs, since your voltage is bit lower than 120 v) Cheap electric space heaters would work too. You also might look around at an electronics surplus store. Whatever you do, it sounds like a lot of time and work to set up. Any chance of doing a smaller load test for subsets of the total bank? You might be able to use a standard 12 v battery load tester then. Good Luck. R.Ray Walters CTO, Solarray, Inc Nabcep Certified PV Installer, Licensed Master Electrician Solar Design Engineer 303 505-8760 On 3/17/2015 12:41 PM, Larry wrote: I am repairing and restoring a pair of poorly designed lithium-ion battery bank that suffered over discharge, damaging many cells. After cell replacement I need to perform a discharge test with a 10kW load to verify the remaining capacity. The battery voltage is 105 volts @ 100% SoC and 89.6 volts @ 0% I would like advice on how I can create an economical 10kW load. Water heating element? Wire wound resistors? Are there any GT inverters that will operate at these voltages? Thanks. ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
[RE-wrenches] Trace SWRC remote
Does anyone know where I can find a working SWRC remote for Trace PS and SW inverters? -- Thank you, Larry Crutcher Starlight Solar Power Systems ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Uni-Solar 68w Laminate panel removal
Hi Lou, There should be two screws at the top of the module. Remove these and on a very hot day you should be able to start at the top edge and peel it down. Don't hurry. Once started, a heat gun to the bottom will speed it up. If some stick-um gets left on the roof, you'll need a solvent to loosen it (can't remember, WD40?). So, after all that effort you will have a used Uni-Solar 68 Watt PV mod that is worth about $50 to someone that knows about the performance of those amazing modules. Larry Crutcher Starlight Solar Power Systems On 3/3/15 4:33 PM, Lou Russo wrote: Wrenches, Has anyone ever removed these from a metal standing seam roof? If so, was the module or roof damaged? If not, then is there a market for these used panels? Thanks for any insight. Aloha, Lou Russo ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] SunWise or Small 12 or 24 Volts Modules
Hi Tom, For some reason your link goes nowhere and when I Google sunlandusa get nothing related to PV solar. Thank you, Larry Crutcher On 2/24/15 4:00 PM, Tom Lane wrote: SunLand USA at www.sunlandusa.com has a large range of 5 to 180 watt PV modules that are all 12 or 24 volt . The modules are well made and their service is great . They only sell 12 and 24 watt mono and poly modules . I have been happy with their 10 , 20 , 25 , 45 , and 75 , 80 , 85 , 120,140, 160 I have purchased and their other 12 and 24 volt equipment . GatorTom ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
[RE-wrenches] Sunwize or industrial PV modules
Hello Wrenches, Does anyone know where to by small 20 to 75 Watt modules like Sunwize used to sell? They were what I considered industrial grade with a junction box. I checked with Soligent but they don't have any. Thanks, Larry ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Off Grid Inverter Replacement Questions
Dan and Allan, I was not going to comment on this thread since my info is a few years old. But since you brought up recent failures I will tell my experience. A few year ago we were having failures with new FM60 and FM80 controllers. Brand new DOA controllers were replaced with used, warranty repaired controllers. One customer had 3 controllers replaced in 30 days. After too many calls to Outback and not one penny in compensation, we totally quit selling all Outback products. Since then we have sold hundreds of Magnum Energy inverters. The only failure we have had was very recently with their new MSH series. For charge controllers we switched to Midnight Classic. We install 10-15 Classic 150's per month. We have had 1 DOA but Midnite responded well and sent a new replacement. Attention manufacturers...Customer service is everything to me. Larry Crutcher Starlight Solar Power Systems On 2/9/15 12:14 PM, Dan Tittmann wrote: AS someone who works almost exclusively with off grid battery based inverters for years. I would recommend staying away from the outback line of inverters. We are seeing outback failures in units that are only 2 to 3 years old, once you get through to the Tech Support generally a 30 to 40 min hold time and forget about the call you back feature unless you want a call back in three days. The board replacements that we get are a total crap shoot. I have had replacement boards fail within minutes and many of them within in months and there is no warranty on the boards. I would go with Magun Hybrid as it is a 120 V AC unit and has load assist like the old SW's. We are always sorry to replace the old SW units but after 20+ years of service I guess they have put in their work. Magnum has provided us with reliable service since we started installing them 6 Years ago. I hope they keep their product as reliable with the new owners. my two cents Daniel Daniel Tittmann CTO Greenwired www.greenwired.com http://www.greenwired.com dan...@greenwired.com mailto:dan...@greenwired.com 707-923-2001 (office) 707-206-5088 (Cell) On Fri, Jan 30, 2015 at 8:02 PM, Allan Sindelar al...@sindelarsolar.com mailto:al...@sindelarsolar.com wrote: Esteemed Wrenches, What I want to know, please, are answers to two+ questions: 1) what's the real scoop? what is now made where? and 2) what actual experiences, specifically product failures, have any of you had that directly relate to changes directly attributable to overseas production? In other words, how much of this is real and how much is rumor? -- *Allan Sindelar* al...@sindelarsolar.com mailto:al...@sindelarsolar.com NABCEP Certified PV Installation Professional NABCEP Certified Technical Sales Professional New Mexico EE98J Journeyman Electrician Founder (Retired), Positive Energy, Inc. *505 780-2738 tel:505%20780-2738 cell* ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] wire sizing question
Wow, Jarmo! That is some incredible workmanship and a great way to interconnect multiple inverters and chargers. You can tell they have done this a few times. Thanks for sharing those photos. Larry Crutcher Starlight Solar Power Systems On 1/3/15 9:16 AM, jarmo.venalai...@schneider-electric.com wrote: Hi: This link takes you to a site in Romania so you (likely) wont be able to read the text, but it does have a lot of good pictures. This installer has been using XW since about 2007 and has a tons of experience. I like what he does with the DC wiring/busbars. The breakers are in the box below the inverters and charge controllers. http://customer.lpelectric.ro/doc/sibiu2/sibiu2_28kw_fotovoltaic.html JARMO _ * Jarmo Venalainen* | *Schneider Electric **| Solar Business* | *CANADA* | *Training Development Specialist - Senior* * Phone:* +604-422-2528 | *Fax:* +604-420-1591 | *Mobile:* +604-505-0291 * Email:* _jarmo.venalainen@schneider-electric.com_ mailto:jarmo.venalai...@schneider-electric.com | *Site:*_www.SEsolar.com_ http://www.sesolar.com/ | *Address:* 3700 Gilmore Way, Burnaby, BC V5G4M1 _ _http://%20www.sesolar.com/ *** Please consider the environment before printing this e-mail From: drake.chamber...@redwoodalliance.org To: RE-wrenches re-wrenches@lists.re-wrenches.org, Date: 01/02/2015 05:18 PM Subject:Re: [RE-wrenches] wire sizing question Sent by:RE-wrenches re-wrenches-boun...@lists.re-wrenches.org 4/0 copper is good for a 24V, 4000 W inverter. What is being used for multiple inverters? I've paralleled 4/0 into outback boxes using 2, 2 PVC conduits. It gets pretty messy trying to put 4 sets of 4/0s into enclosures and battery boxes (although I have worked on such systems). Does anyone have clean solutions for these systems? Thanks, Drake Some other things: If you keep the conduit less than 24 long, which is recommended anyway for main battery connections, the conduit fill requirements don't apply. (see exception: 310.15(B)3a2) Using table 310.15(B)16 yeilds 230 amps for 4/0 at 75 C. Then 240.6 lists 250 amp as the next standard size of OCPD which is allowed to be used by 240.4(B) So you can just justify 4/0. Further, many manufacturers (like Midnite) use the open air ampacity table: 310.15(B)17, since the cable is not in conduit and 4/0 cable at 75 C is rated to 360 amps. The Free Air interpretation is not completely substantiated in the code from my read of it though. Maybe someone more knowledgable could cite the chapter and verse that defines when the free air rating can and cannot be used. Also remember those breakers are 100% duty cycle rated, and that the inverter usually can't run any where close to 250 amps continuously. Bottomline is we've been using 4/0 with 250 amp breakers for almost 20 years, and I've never seen or heard of a problem. R.Ray Walters CTO, Solarray, Inc Nabcep Certified PV Installer, Licensed Master Electrician Solar Design Engineer 303 505-8760 On 1/1/2015 7:23 PM, jay peltz wrote: Happy new year all. I have a question on wire sizing for the following. 250 amp breaker, in a UL enclosure ( say midnite or outback etc) conduit from battery box to enclosure I'm wondering how folks size this for ampacity not voltage drop. thanks jay peltz power ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] wire sizing question
Jay, Divide inverter capacity by LVD then divide by full load efficiency. Example: 4000 Watt inverter shuts down at 42 volts, efficiency 85% = 4000/42 = 95A/.85 = 111 Amps. Then it depends on the insulation and conductor type and the corrections for ambient temp. How can you not consider voltage drop? This is important for the surge capability of inverters. If the battery-inverter run is long you could have significant voltage drop for a wire correctly rated for ampacity. Larry Crutcher Starlight Solar Power Systems On 1/1/15 7:23 PM, jay peltz wrote: Happy new year all. I have a question on wire sizing for the following. 250 amp breaker, in a UL enclosure ( say midnite or outback etc) conduit from battery box to enclosure I'm wondering how folks size this for ampacity not voltage drop. thanks jay peltz power ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
[RE-wrenches] PV calculator for off grid in South Africa
Does anyone know of an online calculator tool for battery based system in S. Africa? -- Thank you, Larry Crutcher Starlight Solar Power Systems ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Panels with 20.1% efficiency rating?
Lou, Panasonic has 21.1% module efficiency. Too bad the US distribution is gone as they are not only efficient but the best performance available as well since the demise of Uni-Solar. Larry On 12/20/14 9:16 AM, Lou Russo wrote: Wrenches, I am looking for panels with a 20.1% efficiency rating or better, that are NOT Sun Power. My distributors can not acquire anything even near that. Any leads or resources to check would be greatly appreciated. Thanks! Aloha, Lou Russo (440) 345 6762 ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Magnum System - Discharged Battery Bank
Right Bill. We recommend fully charging and then an equalization charge on all new flooded batteries. It takes many cycles on a new battery to achieve full saturation of all the active material. Because of this effect, I believe it is vital to reach 100% SoC regularly during the first few months of a battery life. Larry On 12/19/14 9:34 PM, William Dorsett wrote: That’s the reason it is so essential to get as fresh a batch as possible and make sure all are fully charged before installation. Bill Dorsett Manhattan, KS *From:*RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Larry *Sent:* Friday, December 19, 2014 7:07 PM *To:* RE-wrenches *Subject:* Re: [RE-wrenches] Magnum System - Discharged Battery Bank I have installed/serviced thousands of battery based systems, I have not seen any reversed cells either, but I know how it happens. Here's a thought on what could cause multiple lower capacity cells in a bank. From the moment a battery is not being charged, including newly assembled batteries, it is self discharging and lead sulfate is forming on the plates. If left uncharged or undercharged for months, which could be date of assembly to date of installation, the capacity could be affected due to ionic bonding (a level 2 sulfate bond blocking SO4 from finishing the electrochemical process by discharging its electron to Pb). Simply put, less surface area is available so there is less capacity. Unless the installation date is within 60 days or less of the manufacturing date, this could happen. If these damaged batteries were then mixed with healthy ones, this could account for multiple low capacity cells and the scenario I described in my previous email would apply. Larry Crutcher Starlight Solar Power Systems ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Panels with 20.1% efficiency rating?
Right August, it was the Panasonic HIT 240 that is 21.1% . The newer ones are less. On 12/20/14 9:53 AM, August Goers wrote: Hi Lou, The LG Mono X NeON 305 W 60 cell is 18.6% according to their website. I think that is about the best non-SunPower option you can readily get these days. http://www.lg.com/us/commercial/solar-panels/lg-LG305N1C-B3 Even Panasonic modules are only 19.4%: http://eu-solar.panasonic.net/en/products/n-240-n-245/ Best, August *From:*RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Lou Russo *Sent:* Saturday, December 20, 2014 8:16 AM *To:* RE-wrenches *Subject:* [RE-wrenches] Panels with 20.1% efficiency rating? Wrenches, I am looking for panels with a 20.1% efficiency rating or better, that are NOT Sun Power. My distributors can not acquire anything even near that. Any leads or resources to check would be greatly appreciated. Thanks! Aloha, Lou Russo (440) 345 6762 ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Panels with 20.1% efficiency rating?
Hey Marco, I pulled the data sheet to scan it and what did I see? CELL efficiency is 21.1%, not module efficiency. I guess I told all my customers wrongsheesh! I will email you the data sheet. Larry On 12/20/14 10:41 AM, Marco Mangelsdorf wrote: Can you please provide a spec sheet on this mod, Larry? Thanks, marco *From:*RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Larry *Sent:* Saturday, December 20, 2014 7:39 AM *To:* RE-wrenches *Subject:* Re: [RE-wrenches] Panels with 20.1% efficiency rating? Right August, it was the Panasonic HIT 240 that is 21.1% . The newer ones are less. On 12/20/14 9:53 AM, August Goers wrote: Hi Lou, The LG Mono X NeON 305 W 60 cell is 18.6% according to their website. I think that is about the best non-SunPower option you can readily get these days. http://www.lg.com/us/commercial/solar-panels/lg-LG305N1C-B3 Even Panasonic modules are only 19.4%: http://eu-solar.panasonic.net/en/products/n-240-n-245/ Best, August *From:*RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Lou Russo *Sent:* Saturday, December 20, 2014 8:16 AM *To:* RE-wrenches *Subject:* [RE-wrenches] Panels with 20.1% efficiency rating? Wrenches, I am looking for panels with a 20.1% efficiency rating or better, that are NOT Sun Power. My distributors can not acquire anything even near that. Any leads or resources to check would be greatly appreciated. Thanks! Aloha, Lou Russo (440) 345 6762 ___ List sponsored by Redwood Alliance List Address:RE-wrenches@lists.re-wrenches.org mailto:RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org http://www.members.re-wrenches.org ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Magnum System - Discharged Battery Bank
Corey, The reason a cell or a battery in series will reverse polarity is due to that cell having a lower capacity than other cells. For example, you have a string of 100AH cells. One cell only has a capacity 70AH. If you discharge the string more than 70Ah, in order for that cell to continue passing current from the string, the voltage will reverse and begin climbing in a negative direction. If it were me, I would pull that cell (cells) from your pack and test individually. Fully charge and do a controlled discharge rate. If it comes up less capacity than the others it should not be returned to the bank. For one reason, the entire string is limited to the lowest capacity battery. That battery will always be first to reach full charge and first to totally discharge, reversing polarity again. Another reason is while charging, it will be severely overcharged while you try to reach 100% SoC on the other batteries. If the battery is AGM or GEL, it can go into thermal runaway and may cause a fire. At the very least, charge the bank to 100% SoC and measure the temperature of the cell(s) that had reversed. Measure before transition to Float charge. If they are hotter than the others, you know you still have a problem. Larry Crutcher Starlight Solar Power Systems On 12/19/14 7:48 AM, Corey Shalanski wrote: Update on my investigation: I visited the customer's house yesterday to set up a pulse charger. Much to my surprise the three batteries that originally registered negative voltage are now reading positive. Does this make sense - are batteries able to shift between negative and positive voltages at such a low charge level? I do not see any evidence of distorted cases. ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Magnum System - Discharged Battery Bank
Here's a drawing to illustrate. When the 70AH is drained, the string voltage will drop because that cell will go to 0 volts. Continued discharge will reverse the cell voltage. When charging, the 70AH will get full first and be overcharged. On 12/19/14 9:44 AM, Larry wrote: Corey, The reason a cell or a battery in series will reverse polarity is due to that cell having a lower capacity than other cells. For example, you have a string of 100AH cells. One cell only has a capacity 70AH. If you discharge the string more than 70Ah, in order for that cell to continue passing current from the string, the voltage will reverse and begin climbing in a negative direction. If it were me, I would pull that cell (cells) from your pack and test individually. Fully charge and do a controlled discharge rate. If it comes up less capacity than the others it should not be returned to the bank. For one reason, the entire string is limited to the lowest capacity battery. That battery will always be first to reach full charge and first to totally discharge, reversing polarity again. Another reason is while charging, it will be severely overcharged while you try to reach 100% SoC on the other batteries. If the battery is AGM or GEL, it can go into thermal runaway and may cause a fire. At the very least, charge the bank to 100% SoC and measure the temperature of the cell(s) that had reversed. Measure before transition to Float charge. If they are hotter than the others, you know you still have a problem. Larry Crutcher Starlight Solar Power Systems On 12/19/14 7:48 AM, Corey Shalanski wrote: Update on my investigation: I visited the customer's house yesterday to set up a pulse charger. Much to my surprise the three batteries that originally registered negative voltage are now reading positive. Does this make sense - are batteries able to shift between negative and positive voltages at such a low charge level? I do not see any evidence of distorted cases. ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Magnum System - Discharged Battery Bank
I have installed/serviced thousands of battery based systems, I have not seen any reversed cells either, but I know how it happens. Here's a thought on what could cause multiple lower capacity cells in a bank. From the moment a battery is not being charged, including newly assembled batteries, it is self discharging and lead sulfate is forming on the plates. If left uncharged or undercharged for months, which could be date of assembly to date of installation, the capacity could be affected due to ionic bonding (a level 2 sulfate bond blocking SO4 from finishing the electrochemical process by discharging its electron to Pb). Simply put, less surface area is available so there is less capacity. Unless the installation date is within 60 days or less of the manufacturing date, this could happen. If these damaged batteries were then mixed with healthy ones, this could account for multiple low capacity cells and the scenario I described in my previous email would apply. Larry Crutcher Starlight Solar Power Systems On 12/19/14 12:23 PM, Jay Peltz wrote: I find it really curious. I've been dealing with batteries for almost 20 yrs. I've seen so many dead, flat batteries, systems etc I can't count them all. But I've yet to find a reversed one. I understand the process. I'm trying to understand how he could get multiple reversed batteries at one go? Jay Peltz power Sent from my iPhone On Dec 19, 2014, at 9:47 AM, jarmo.venalai...@schneider-electric.com mailto:jarmo.venalai...@schneider-electric.com wrote: Hi: This cell reversal ability of lead acid batteries gives good perspective on just how much you can mistreat them and beat them up and still have an expectation of recovery. Lithium cells on the other hand without a full range of protections would have long since filled the home with all kinds of interesting high temperature thermal events, gaseous compounds and chemicals, and there is no way you could get that magic smoke back into them. JARMO _ * Jarmo Venalainen* | *Schneider Electric **| Solar Business* | *CANADA* | *Training Development Specialist - Senior* * Phone:* +604-422-2528 | *Fax:* +604-420-1591 | *Mobile:* +604-505-0291 * Email:* _jarmo.venalainen@schneider-electric.com_ mailto:jarmo.venalai...@schneider-electric.com | *Site:*_www.SEsolar.com_ http://www.sesolar.com/ | *Address:* 3700 Gilmore Way, Burnaby, BC V5G4M1 _ _mime-attachment.jpg http://%20www.sesolar.com/ *** Please consider the environment before printing this e-mail From: Corey Shalanski cshalan...@joule-energy.com mailto:cshalan...@joule-energy.com To: re-wrenches@lists.re-wrenches.org mailto:re-wrenches@lists.re-wrenches.org, Date: 12/19/2014 06:48 AM Subject:Re: [RE-wrenches] Magnum System - Discharged Battery Bank Sent by: RE-wrenches re-wrenches-boun...@lists.re-wrenches.org mailto:re-wrenches-boun...@lists.re-wrenches.org Update on my investigation: I visited the customer's house yesterday to set up a pulse charger. Much to my surprise the three batteries that originally registered negative voltage are now reading positive. Does this make sense - are batteries able to shift between negative and positive voltages at such a low charge level? I do not see any evidence of distorted cases. On Thu, Dec 18, 2014 at 7:58 AM, _jay@asis.com_ mailto:j...@asis.com wrote: I second tump. Most likely a bad /cell battery took out the system. As these are VRLA batteries, I'm curious do,the cases look damaged such as expanded or sunk in? Jay Peltz power __ ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Programmable Battery Charger
boB and Jarmo, thanks for great explanations...So, let's dump that idea and go back to square one: a programmable 1.5kW charger for 12 volt batteries. I have been checking with all the charger manufacturers I can find and no one makes this product. Argus said no, Pro Charging said no, a few others, no. Brian, an inverter/charger and remote will work great but that still represents $1000 cost and about $1350 to my customer for a 100 amp charger. But, so far, this is my only option. A few years ago Magnum Energy told me they were working on a stand alone programmable charger but nothing yet. It probably does not cost much less to build than the inverter/charger does. Thanks to all for the answers. Thank you, Larry On 12/16/14 2:19 PM, b...@midnitesolar.com wrote: Jarmo, you are absolutely correct. This is another great reason NOT to use an MPPT charge controller as an AC sourced battery charger. Also, if my instructions are not followed to a TEE, the CC WILL blow up ! The input capacitors are going to wear out MUCH sooner than a real charger because of the 60Hz or 120 Hz ripple shown in Jarmo's graph. Capacitor ripple abuse was one answer to one of Larry's questions about long term reliability. Also, if the input diodes short, you are applying AC directly to the input capacitors and will go POOF as well as the power section. And you would NOT know that you needed an input power resistor first or possibly where to even find one of the correct resistor values and power ratings if the input source is stiff. This is the scariest problem in my mind Too high of input max power voltage, overcurrent and then, battery voltage regulation will overshoot without that resistor. I would just spend the extra money and do this right in the first place and don't try to cut corners on price. Brian Teitelbaum had the best idea I think... Just buy an inverter with a power factor corrected charger like the newer Schneider SW inverter/charger (I think that was the one ?) or one of the MSW Magnums. Or, a decent charger if one exists. Haven't seen the Argus/Alpha one. MPPT charge controllers are really just NOT designed for this. (although they might work for a while). In fact, Ryan from MidNite Solar blew up several Classics at first. But knowing that some folks are going to try this, I thought it best to give at least some directions. Thanks, boB On 12/16/2014 12:34 PM, jarmo.venalai...@schneider-electric.com wrote: Hi: I'm enjoying learning many new ways of looking at things and of practical solutions on this forum. In that spirit, the only thing I would add to this discussion is that the power factor as seen by the AC source will be very poor. In that regard, the larger the caps, the more stable the DC voltage, but the poorer the PF. This will show up as much lower charging efficiency due to the way in which AC current is drawn by the bridge rectifier/capacitor circuit. Here's an actual graph of how a bridge rectifier connected to a capacitor draws AC current, The graph is from my past life a couple of decades ago back when I was studying. It's not a conventional phase-shift PF problem, but rather a form factor PF problem. It shows the current drawn by a 13 PC monitor of that era, before PF correction was mandated for all new products. In this example the 'crest factor', (peak current as measured versus what it could have been if the current was drawn throughout the AC pulses, was about 4x). Depending on the size of capacitor, it can be as high as 7x. The practical effect on the wires and devices including the diodes and charge controller, is that a lot of heat is generated in their power components. The source of the energy for that heat is the AC source and in cases where the AC source is a generator that translates to much higher fuel consumption, (in some cases over 30% more). Out of my tests back then, I also discovered one practical recommendation. If you are using bridge rectifiers connected to capacitors, do not have any length of wire and in particular no loop area in the wires between the bridge rectifier and capacitors. Having wire/loop area introduces inductance into the circuit which behaves somewhat like an ignition coil due to the high speed reverse recovery period of the diodes; and this happens four times every AC cycle. Given the right conditions the voltage spikes caused by that inductance/ignition coil like effect will make short work of the diodes and other components which are on the circuit. The voltage spikes wont be a problem if the bridge rectifier is as close as possible to the capacitors, but due to reverse recovery effect, you'll still be stressing the parts and heating wires. In my opinion, its ok to do this, but I wouldn't push power levels to anywhere near the limits of components and devices. JARMO
Re: [RE-wrenches] Programmable Battery Charger
I must have missed the prior discussion about using PV CC. The concept sounds good but how many of you have done this and are there any pitfalls to be aware of? If I use a 20 amp bridge I should be able to produce 80 amps @ 14.4V. For continuous operation, will I need a large heat sink on it? How does the unfiltered full wave peak voltage affect the CC over time? Are they (specifically Midnite) really designed to handle input waveform like this? I like this idea, especially if I can stack the controllers. Thank you, Larry On 12/15/14 6:51 PM, jay peltz wrote: Hi Kirk, If you use a 200vdc midnight CC you'll have no issues. When you rectify 120vac its up around 166vdc ( uses the peak vac which is around 170vac.) For a 150vdc max controller ( midnite 150) or a 144vdc ( outback FM) then a buck transformer or standard transformer is the trick to reduce the AC and hence the DC for these lower voltage units. jay peltz power On Dec 15, 2014, at 5:38 PM, Kirk Herander wrote: This has been discussed on this list in years past. It is possible to use an outback charge controller as a battery charger. You need to put the 120 AC into a bridge rectifier, then feed the 120 DC into the controller’s PV input. So you’ll have an 80 amp battery charger. *Kirk Herander* *VT Solar, LLC* */Proven PV provider since 1991/* *www.vermontsolarnow.com* dba Vermont Solar Engineering NABCEP^TMInaugural Certificant VT RE Incentive Program Partner 802.863.1202 *From:*RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org]*On Behalf Of*Dan Tittmann *Sent:*Monday, December 15, 2014 8:18 PM *To:*i...@windsine.org mailto:i...@windsine.org; RE-wrenches *Subject:*Re: [RE-wrenches] Programmable Battery Charger You can manually adjust Iotas with tweaking the potentiomiters while monitoring it with a god volt meter. But no time adjustment. Daniel Daniel Tittmann CTO Greenwired www.greenwired.com http://www.greenwired.com dan...@greenwired.com mailto:dan...@greenwired.com 707-923-2001 (office) 707-206-5088 (Cell) On Mon, Dec 15, 2014 at 4:21 PM, Windsine Inc. winds...@gmail.com mailto:winds...@gmail.com wrote: Check out Argus Technologies. RoyR On Dec 15, 2014 4:01 PM, Larry la...@starlightsolar.com mailto:la...@starlightsolar.com wrote: Wrenches, Does anyone know of a 120/12 volt battery charger that can be programmed for absorb and float voltage and time in absorb mode? I have been needing this product for many years but I can only find it in inverters with built in chargers from Magnum, Outback, and Xantrex. -- Thank you, Larry Crutcher Starlight Solar Power Systems ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
[RE-wrenches] Programmable Battery Charger
Wrenches, Does anyone know of a 120/12 volt battery charger that can be programmed for absorb and float voltage and time in absorb mode? I have been needing this product for many years but I can only find it in inverters with built in chargers from Magnum, Outback, and Xantrex. -- Thank you, Larry Crutcher Starlight Solar Power Systems ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Parallel Wire combining
You ask a simple question to this group and stunning brilliance floods my inbox. RE-Wrenches, You are truly amazing. Thanks to all that discussed this for the knowledge I have gained. Larry On 12/2/14 3:47 PM, Daniel Young wrote: It all boils down to how ampacity is determined in the NEC. Ampacity is really related to temperature as far as the NEC is concerned. The ampacity of a 1/0 wire at 90c is the constant current it can carry in free air (30 C air) and not achieve an internal temperature of more than 90 C. the 75 c ampacity is the same, the amperage it can carry while not going over 75 C. Now, if you double the diameter of a circle, the circumference also doubles, but the cross sectional Area actually goes up much more (4x more in fact) because cross sectional area is based on the square of the diameter and circumference is simply based on the diameter ^1 power. Wire dissipates heat from its surface only, so the dimension critical for the amount of heat a wire can dissipate is circumference, not cross sectional area. So even though the wire is larger and has a much lower resistance, the heat dissipating area does not increase by as much, so in the end the larger wire has a lower current carrying capacity per unit cross sectional area, than a smaller wire. Here is an example that lets me keep the math simple: (the #’s are all round #’s and not based on real ampacities/resistances, just to keep the math simple.) Wire 1: A diameter of 10 units and can carry 100A through it and stay at 90C. It has a resistance of 1 ohm/1000ft. Wire 2: A diameter of 20 units. It has 4times the cross sectional area, and double the circumference (which means 2x the outer surface area) to dissipate heat. It has a resistance of .25 ohm/1000ft (1/4 that of wire 1 since it has 4x the amount of copper to carry current). For wire 1 to stay at 90 C, it has to dissipate (P=I^2*R), P=(100amps^2)*1 omh=10,000 watts per unit of outer surface area. So if Wire 2 has double the surface area to dissipate heat, it can dissipate about 2x the energy, or 20,000watts. So if we work it backwards (P=I^2*R is the same as I=sqrt[P/R]) I=sqrt[20,000/.25]=sqrt[8]=282amps So wire 2 can handle (282amps/100amps)=2.8 times the amperage, even though it has 4times the cross sectional area, all because it only has 2 times the surface are to get rid of heat. There are other factors with heat transfer that make the larger wire have even lower ampacity, but this demonstrates the main contributing factor. [In the NEC table 310.15(B) we see that a 250kcmill copper wire handles 255A @75C, and a 100kcmill (4x the area) can only take 545A, or 2.2 times the current, so not too far from my example]. I hope the above helps more than it hurts. With Regards, Daniel Young, NABCEP Certified PV Installation Professional^TM : Cert #031508-90 NABCEP Certified Solar Heating Installer^TM : Cert #SH031409-13 ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
[RE-wrenches] Parallel Wire combining
Wrenches, If I combine 3 conductors of equal length in parallel, is the resulting size equal to 3 times the Circular Mil area? For example, #4 is 42,080cm so are three #4's close to 2/0 (134,200cm) in size? Is it as simple as this? Assuming the conductors can not be removed individually, does this mean the current capacity is equal to the resulting wire size? Thanks, Larry ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Parallel Wire combining
OK, let's use 1/0 for the example. 108,350 x 3 = 325,050. Do I now have a cable between 300 and 350 AWG? Thank you, Larry On 12/2/14 10:51 AM, Bill Turberville wrote: The minimum conductor size that can be paralleled, according to the NEC is 1/0. William C. Turberville P.E. President Electrical Contracting Enterprises LLC 3080 Stage Post Dr ste 107 Bartlett, TN 38133 901-348-9230 ext 101 phone 901-289-6346 cell 901-348-2192 FAX *From:*RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Jerry Shafer *Sent:* Tuesday, December 02, 2014 11:45 AM *To:* RE-wrenches *Subject:* Re: [RE-wrenches] Parallel Wire combining We have installed multible mcm 500 to meet this and there were three on each leg but that was because of the required size and bending room Jerry On Dec 2, 2014 7:43 AM, Larry la...@starlightsolar.com mailto:la...@starlightsolar.com wrote: Wrenches, If I combine 3 conductors of equal length in parallel, is the resulting size equal to 3 times the Circular Mil area? For example, #4 is 42,080cm so are three #4's close to 2/0 (134,200cm) in size? Is it as simple as this? Assuming the conductors can not be removed individually, does this mean the current capacity is equal to the resulting wire size? Thanks, Larry ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Parallel Wire combining
That's the part that is throwing me off. If I have 3 times the circular mil and compare that to a single conductor of similar circular mil, how do I have 3 times the ampacity? These are very different numbers. Example: 1/0 @ 90c is 170 amps x 3 = 510 amps. 510A is what a conductor just over 750 AWG will carry. The circular mils of 3 1/0 cables is only 325,050 or a 325 AWG cable which would be rated at about 330 amps. So, is it 510 amps (3x the ampacity) or 330 amps (3x circular mil)? And, more importantly, why? Larry On 12/2/14 11:14 AM, Bill Turberville wrote: I am sorry. Bad fingers. Three times the ampacity under the same conditions. *From:*RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Larry *Sent:* Tuesday, December 02, 2014 12:09 PM *To:* RE-wrenches *Subject:* Re: [RE-wrenches] Parallel Wire combining OK, let's use 1/0 for the example. 108,350 x 3 = 325,050. Do I now have a cable between 300 and 350 AWG? Thank you, Larry ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Parallel Wire combining
Hey boB, This is the reference table I was using. They show 325 AWG and 325kCM refer to the same diameter cable but I should have used kcm for clarity. If all insulation/temp rating is the same we are back to my original question. Anyone else able to explain this? To be safe I am leaning toward using the combined CM number to size for current rather than 3 times the ampacity as that just makes no sense to me. On 12/2/14 3:54 PM, b...@midnitesolar.com wrote: The area of the conductor will be 3 times and you would think that the NEC Ampacity would also be 3 times that of one conductor. But one LARGE conductor with the same area might not be as high as you think because of insulation. I would think that ampacity of 3 cables in parallel would be 3 times. But probably not when you take a single cable of the 3X area out of the NEC table. (I haven't looked at this to verify) Also, Larry, 325 AWG 750 AWG (gauge) wire is a bit too small for this, don't you think ? I know... You mean circular mils... boB ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Aqueous Hybrid Ion batteries
David, Something does not add up to me. The cell has a voltage discharge curve way outside of RE equipment, 1.75 Vpc down to 0.5Vpc. I can't see how this technology could be scaled to RE applications without wasting much of the capacity. From what I see, only about 40% could be used before LVD. On 11/10/14 10:10 AM, Dave wrote: Wrenches, I have a customer with a grid-tied w battery back-up (formerly off-grid) with failing LA batteries. He found these batteries on the web and asked me to check them out. Anyone out there know anything about this AHI technology and or this company, Aquion Energy? *http://www.aquionenergy.com/microgrid-energy-storage* ** Thanks, David Palumbo Independent Power LLC 462 Solar Way Drive Hyde Park, VT 05655 802-888-7194 ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] LiFePo4
Mac, Li-ion batteries are connected the same as any other deep cycle, positive and negative terminals. The Battery management is done actively on each cell. The brand that we sell has a CPU that receives serial data from the string of “sense” boards that are monitoring temperature and voltage per cell. The sense boards also function to balance the cells after they reach 2.55 volts per cell. There is a 0.5 amp shunt on the cells that are higher and this allows the current to continue charging cells that are lower. The management system is strictly DC. You can charge from a number of sources. Larry On Sep 16, 2014, at 6:44 AM, Mac Lewis maclew...@gmail.com wrote: Hello wrenches, How do you get PV power into the battery management system? Are there PV application specific battery management systems, or are these AC loads? Thanks ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] LiFePo4
Hi William, I have designed and installed a few lithium iron battery banks. We now stock the GBS line and plan to add additional brands soon. My experience is very positive toward the performance and future of LFP and LFMP as a replacement to lead acid for off grid, stand-by and mobile use. As the price point continues to drop and manufacturers begin to support this technology, I can see it replacing all lead acid designs. But, I’m no Ray Kurzweil. What would you like to know? Larry On Sep 15, 2014, at 5:28 PM, William Miller will...@millersolar.com wrote: Wrenches: Does anyone have any experience with Lithium Ferrous Phosphate cells? What are your experiences? I am looking at an installation tomorrow and would like some input. Thanks in advance. William Miller image003.jpg Lic 773985 millersolar.com 805-438-5600 ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Grid-tie inverter for wind generator
Chris, I would not touch that with a..….20 foot pole. It will never work right and he will assign you the blame when he sees his electric bill go down by $1 per month. Larry On Sep 5, 2014, at 9:42 AM, Chris Daum ch...@oasismontana.com wrote: One killowatt, and three wire. He's been using it with some heating elements as a dump load, to make hot water. And he just sent me a picture -- heck, it's on something like a 20 ft. pole, so no wonder it's not making much power! Also he doesn't want to spend a lot of money, so I suspect the Aurora (which would be a pretty good deal) will still be too costly for him. His machine's output is put through rectifiers to make the battery voltage. --Chris @ the Oasis Montana ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Sunpower off grid?
Hello Ray, I have been installing SunPower cell modules for about a decade. All of our mobile installations are ungrounded arrays, off grid we use negative ground. We have never had any issue using them to charge batteries up to 48 volts, even when combined in series. I have not installed any for grid tie. Last year I purchased about 100 of the 327 and 435 Watt modules, likely from the same seller, for a very low price. There is no SunPower label on the back. I was told that these modules were laminates that SunPower rejected due to cosmetic flaws. The surface has lots of blemishes clearly visible under the glass. Someone other than SunPower made frames and assembled the module. The frame quality is not so great and the 435 structurally feels inadequate. I sell these to off grid customers in Mexico that want cheap but high performance PV solar power. That’s all... Larry Crutcher Starlight Solar Power Systems On Aug 20, 2014, at 10:46 PM, Ray Walters r...@solarray.com wrote: Greetings fellow Wrenches; I have a customer that just purchased some Sunpower E20 -435 modules somehow from Ebay, and wants me to design a backup power system for him. This system would be battery based and not be grid tied. SO the question is: has Sunpower put to rest the positive grounding issue with these modules? I would want to either use a negative ground system or go ungrounded, as the charge controllers and battery based inverter do not play well with a positive grounded system. My idea is that I could run these modules at lower voltage, either all in parallel (85.6 Voc) or 2 in series (191 Voc) with Midnite Classic controllers, and that the whole surface polarization issue will be minimized at these lower voltages. I know this came up before, and Sunpower basically said they would revoke their warranty for any battery based systems, (which is why I'm no longer a Sunpower dealer :) Don't the newer Sunpower modules no longer need positive ground, and if so, which models is this true for? In this case, the warranty is already suspect, so that's not an issue. It just has to work safely. Thanks in advance for your help, -- R.Ray Walters CTO, Solarray, Inc Nabcep Certified PV Installer, Licensed Master Electrician Solar Design Engineer 303 505-8760 ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] WorkTruck Inverter Suggestions
Hi Bill, I’m probably stating the obvious but we always install mobile inverters closest to the battery due to the high loss at 12 volts, then run AC to the point of use. Larry On Aug 7, 2014, at 7:07 AM, Bill Loesch solar1onl...@charter.net wrote: Gentlemen: Does anyone have any suggestions/preferences on mounting the inverter streetside or curbside on the service body pickup? TIA, -- Bill Loesch Solar 1 - Saint Louis Solar 314 631 1094 ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Lithium Ion Battery....was 2v metal cased cells
$360/kWh is a good price. Can you share the brand with us or email me off list? We sell Li-ion (LFMP) at our store but I include a CPU, protection solenoids, battery capacity meter and video display. My dealer cost is quite a bit higher than you were quoted. Larry On Jul 12, 2014, at 11:42 AM, Phil Lawes p...@insoltechsolar.com wrote: Just curious if fellow wrenches are looking at Li-on batteries. We were just quoted a 50KWHR at 48 volt battery pack with enclosure and BMS for $ 360.00 per KWHR or $0.36 per watt hour. ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] FullRiver Battery
Hello Bob, We began selling FullRiver about 4 years ago and probably have over 200 systems installed. We have had no failures or issues with them. One aspect I like is the high acceptance voltage of 2.483 Vpc. Higher voltage means more power into the battery so you are charging faster. The 2 volt L16 (1150AH @ C20 rate) is very popular at our store. I might go as far as saying they are comparable in quality and performance to Lifeline battery. Cost is about 10% less than Lifeline, and 20% less than SunXtender. Made in China so I don’t promote them as I do US made Lifeline which is our best selling battery. Larry Crutcher Starlight Solar Power Systems On Jul 2, 2014, at 3:58 PM, RE Ellison reelli...@gmail.com wrote: What has been everybody’s experience with Full River Batteries? Bob ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Magnum and Pumps
Hi Drake, If the Enphase are online, up to 60 amps (30A @ 240V) can be transferred through the Magnum inverter to loads. The inverter is not providing power to loads at that time. If the Enphase go offline, the Magnum takes over using power from the battery. If the load is greater than your Enphase system can provide, the Magnum will transfer to battery power based on the VAC dropout setting. You probably want to use the UPS mode (read ME-ARC manual about this). The new Magnum MSH models can combine AC input power and battery power to increase the total AC output capacity for starting heavy loads. Larry On Jul 3, 2014, at 7:59 AM, Drake drake.chamber...@redwoodalliance.org wrote: This information helps greatly. I really appreciate all of your expert advice. One other wild card in the installation is that the inverter is going to be AC coupled with an Enphase system. The Enphase system will contribute greatly to the overall power available in the protected loads panel. But, with Magnum's slow voltage response I'm not sure if the Enphase system will drop off line when the pump surges, or if the Enphase power will be available to help with the startup surge. Any insights on this? Thank you, Drake ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Magnum and Pumps
Yes Drake, I stand corrected, I was picturing the micro inverters feeding the input rather than coupling the output of the Magnum. To your original question, I think you would have to be consuming more power than the PV array alone can provide before the Magnum voltage would drop with the pump load. So it may be a rare event unless the PV array is small. Of course after sundown its all on the Magnum. That’s why I suggested two Magnums in my first response. Does anyone know how tolerant the Enphase inverters are of such a momentary sag? Larry On Jul 3, 2014, at 1:42 PM, Drake drake.chamber...@redwoodalliance.org wrote: Hi Larry, In this case, the Enphase will AC couple with the Magnum in the protected loads panel. The AC out of the Magnum provides the micro grid to which the Enphase connects. If charging exceeds loads, when the grid is down, power will go to the batteries (up to the high battery voltage set point). If loads are greater than the output of the Enphase system, the Magnum will produce power to feed the loads. Thanks, Drake At 10:55 AM 7/3/2014, you wrote: Hi Drake, If the Enphase are online, up to 60 amps (30A @ 240V) can be transferred through the Magnum inverter to loads. The inverter is not providing power to loads at that time. If the Enphase go offline, the Magnum takes over using power from the battery. If the load is greater than your Enphase system can provide, the Magnum will transfer to battery power based on the VAC dropout setting. You probably want to use the UPS mode (read ME-ARC manual about this). The new Magnum MSH models can combine AC input power and battery power to increase the total AC output capacity for starting heavy loads. Larry On Jul 3, 2014, at 7:59 AM, Drake drake.chamber...@redwoodalliance.org wrote: This information helps greatly. I really appreciate all of your expert advice. One other wild card in the installation is that the inverter is going to be AC coupled with an Enphase system. The Enphase system will contribute greatly to the overall power available in the protected loads panel. But, with Magnum's slow voltage response I'm not sure if the Enphase system will drop off line when the pump surges, or if the Enphase power will be available to help with the startup surge. Any insights on this? Thank you, Drake ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Magnum and Pumps
If you have a clamp on meter that can capture inrush current (I use a Fluke 337 for this) you can get a good idea of the starting current needed. One problem is that while backing up the house, you will likely have other loads operating when the pump starts which will decrease the available surge current. I would recommend using a stacked pair of 4448’s as a minimum if you have other house loads. Larry Crutcher Starlight Solar Power Systems On Jul 2, 2014, at 8:17 AM, Drake drake.chamber...@redwoodalliance.org wrote: Hello Wrenches, We are hoping to use a Magnum PAE 4448 to back up a household that includes a 3/4 HP deep well pump. There is about 120 feet of vertical rise and about 1000 feet of horizontal distance. I have been told that there is a correlation between the locked rotor current of a pump and the predictable ability of a specified inverter to power that pump. The plumber who installed the pump left no paperwork and retained no records of what pump he put in the hole last year. He could only say it was a 3/4 HP pump. We are therefore unable to obtain the manufacturer's nameplate specifications. The Magnum PAE 4448 has a 1 mS surge of 70 A (at 240 V) and a 100 MS surge of 40 A. According to the NEC Table 430.251(A), a 3/4 HP motor has a locked rotor current of 41.4 amps at 230 V. This inverter can surge at 35.4 A for 5 seconds. The specified battery bank will be 8 Full River L-16 AGMs. Can anyone say if: Is there enough information to know if this setup will handle the pump, and if so, will it? How can an inverter's ability to power a motor or pump be calculated by knowing its locked rotor current? Which surge periods should be compared to the locked rotor current? Does the surge current need to equal locked rotor. How long must the inverter meet its required maximum surge? From experience with Magnums and pumps, does this seem like a good combination? Thank you, Drake Drake Chamberlin Athens Electric LLC OH License 44810 CO License 3773 NABCEP Certified Solar PV 740-448-7328 http://athens-electric.com/ ___ ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Magnum and Pumps
Hi Roy, The FullRiver DC400-6 AGM battery can issue 2000 amps for 5 seconds so he should be fine. Larry On Jul 2, 2014, at 12:35 PM, Roy Butler r...@four-winds-energy.com wrote: I haven't seen anyone mention the battery bank. If I understand correctly, there's a single string of sealed L16 batteries on this inverter. I have my doubts as to whether or not that bank can provide the high current the inverter needs to start this load. Roy Butler NABCEP Certified Solar PV Installer® NYSERDA eligible PV wind installer IREC Certified Master Trainer™ for Small Wind Installer Four Winds Renewable Energy, LLC 8902 Route 46, Arkport, NY 14807 607-324-9747 www.four-winds-energy.com Join us at the 10th Annual Small Wind Conference A Gathering of Installers, Manufacturers, Dealers, Distributors June 17 and 18, 2014 in Stevens Point, Wisconsin www.smallwindconference.com Although no trees were killed in the sending of this message, a large number of electrons were terribly inconvenienced. On 7/2/2014 2:10 PM, Jason Szumlanski wrote: To further qualify my statements, the inverter will start the pump without issue, but I should echo the warnings by others that if there are other loads present, especially other motor loads that could start concurrently, you may experience issues. As long as your customer understands the limitations and possibilities, you may be just fine. Jason Szumlanski Fafco Solar On Wed, Jul 2, 2014 at 11:00 AM, Jason Szumlanski ja...@fafcosolar.com wrote: For what it's worth, I've run a single speed 1.5HP pool pump with a MS4448PAE in a mobile application on a 38.4kWh battery bank (sixteen Rolls S-530's). I have also run a 2.5HP Hayward EcoStar Variable Speed pool pump at full RPM, but that startup current is likely less than you well pump. I'm going to guess your 3/4HP well pump will be a breeze to start with this inverter. Jason Szumlanski Fafco Solar On Wed, Jul 2, 2014 at 10:47 AM, Allan Sindelar al...@sindelarsolar.com wrote: Drake, As a normal CYA, I'll always gently let a customer know that this (or any) particular combination of inverter and load sometimes proves incompatible, just in case the unexpected happens. (We once had a MS4448 that would not reliably start and run a condensing boiler; a switch to a different boiler resolved the issue.) Having said that note of caution, I wouldn't give it any concern. 3/4 HP and 1 HP well pumps have never been an issue; I would expect 1.5 HP to be easy to run. At 2 HP I'd be asking these questions here. You might check that it's a 3-wire, capacitor-start motor, but nowadays nearly all are. Two-wire pumps (with no control box) can add 50% to the surge. The Magnum has a fairly poor voltage regulation response. Sometimes the AC voltage can drop to ~80 VAC momentarily. So you might also caution your customer that the lights may flicker when the pump starts. In our home we know whenever our Kenmore fridge turns on. Allan Allan Sindelar al...@sindelarsolar.com NABCEP Certified PV Installation Professional NABCEP Certified Technical Sales Professional New Mexico EE98J Journeyman Electrician Founder (Retired), Positive Energy, Inc. 505 780-2738 cell On 7/2/2014 8:17 AM, Drake wrote: Hello Wrenches, We are hoping to use a Magnum PAE 4448 to back up a household that includes a 3/4 HP deep well pump. There is about 120 feet of vertical rise and about 1000 feet of horizontal distance. I have been told that there is a correlation between the locked rotor current of a pump and the predictable ability of a specified inverter to power that pump. The plumber who installed the pump left no paperwork and retained no records of what pump he put in the hole last year. He could only say it was a 3/4 HP pump. We are therefore unable to obtain the manufacturer's nameplate specifications. The Magnum PAE 4448 has a 1 mS surge of 70 A (at 240 V) and a 100 MS surge of 40 A. According to the NEC Table 430.251(A), a 3/4 HP motor has a locked rotor current of 41.4 amps at 230 V. This inverter can surge at 35.4 A for 5 seconds. The specified battery bank will be 8 Full River L-16 AGMs. Can anyone say if: Is there enough information to know if this setup will handle the pump, and if so, will it? How can an inverter's ability to power a motor or pump be calculated by knowing its locked rotor current? Which surge periods should be compared to the locked rotor current? Does the surge current need to equal locked rotor. How long must the inverter meet its required maximum surge? From experience with Magnums and pumps, does this seem like a good combination? Thank you, Drake Drake Chamberlin Athens Electric LLC OH License 44810 CO License 3773 NABCEP Certified Solar PV 740-448-7328 http://athens-electric.com/ ___ List sponsored
[RE-wrenches] Trace SW4024 LCD display problem
I am looking for someone that can repair the SW4024 LCD control. The display is getting to dim to view. Thank you, Larry ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Lightning Damage - Need Replacements (Correction)
Hi Dan, You mentioned that “his grounds didn't work”. Actually, they worked, just in an undesirable way. One thing to look at is how or whether the house ground system was bonded to the tower ground. If they were not properly bonded, and with poor soil condition, the potential difference between the two grounds could create very high voltages. The voltage path would be the turbine wiring to find the house ground, traveling through any AC connected items to do so. I would like to hear more about this as it’s a personal subject of study for me. Larry Crutcher On Jun 15, 2014, at 4:29 PM, Exeltech exelt...@yahoo.com wrote: Hello Chris, ….The system is off-grid north of Fort Worth, Texas. The house and equipment are sitting on and in the worst caliche I've ever seen. It's as close to concrete as you can get. There's virtually no topsoil. Watering grounds won't help .. even poured into a hole. It just sits there. They had to jackhammer to dig the tower hole. He's got a 110' tower for his Bergey. He told me they drove numerous grounds diagonally into the bottom of the tower hole from the edges, bonded them all together, then connected everything to the tower, as well as the other equipment using #4 AWG solid. All of the guy wires are equally bonded. Lightning hit the tower directly, but the fact is .. his grounds didn't work. Everything electrical in the house was destroyed. Didn't matter if it was turned on or off. The only things that DID survive are his batteries (as far as he can tell) .. and the Bergey itself. He connected a three-phase diode array directly to the Bergey output leads, and it's charging his batteries, just not as well as with the controller in place (of course). The genny runs smoothly in the wind, meaning all three phases are intact. If one or two phases were open, you'd see it and hear it in the motion of the blades - much the same effect on the engine if you had a plug wire fall off. If you're a wind person (how can you NOT be in Montana?) .. you already knew that. He may bonded everything to his well casing. I don't know - but I'll ask. This is indeed a good learning opportunity. I'm going to help him get things operating again .. and will highly recommend some of the new lightning protection units Midnite is making. In the meantime .. charge controllers and inverters first. Thanks! Dan ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Kyocera 120's low voltage
David, Kyocera KC-120-1’s from 1999 to Dec 2002 will fail from a defective solder joint. Although out of warranty, they are still be warranted by Kyocera and replaced with a remanufactured KC-120-1R. Contact them (rae.parafin...@kyocera.com) with the serial numbers and mfg dates to get an RMA started. We keep the remanufactured units in stock at our store because we see so many of these. Kyocera will also pay labor to replace them. Thank you, Larry Crutcher Starlight Solar Power Systems On Jun 11, 2014, at 4:47 PM, Dave d...@independentpowerllc.com wrote: Wrenches, I troubleshot an underperforming off grid array today and found low Voc's in 4 out of 10 KC-120's (nominal 12v modules rated at 21.5 Voc and 7.45 Isc). Modules are vintage 2000. Under modest sunlight (500 to 600W per M sqd) 6 modules measured from 18 to 19 Voc and 4 Isc. Four modules measured from 9.6 to 13.7 Voc and 4 Isc. I was chased off the roof by a coming thunderstorm and did not check for bad diodes. These modules have nice old school J-boxes with 6 diodes per each module. Am I looking at a diode issue, or failing modules? Thanking you in advance for your time, David Palumbo Independent Power LLC 462 Solar Way Drive Hyde Park, VT 05655 802-888-7194 ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Battery cable crimper
Hi Allen,It is huskie, not Husky. Ithink my auto correct unfixed it. I purchased this one used. I think it was about $1800. When I get back to the office tomorrow, I'll check the model #. It is a dieless design with 4 points that crimp from #4 to 4/0 ( I think it goes to 500). We make well over 300 crimps per month and this tool has been fast and flawless.Larry Original Message Subject: Re: [RE-wrenches] Battery cable crimper From: Allan Sindelar al...@sindelarsolar.com Date: Thu, May 01, 2014 4:20 pm To: RE-wrenches re-wrenches@lists.re-wrenches.org Larry, OK, need more info please... "Husky" is a Home Depot house brand for tools. "Huskie" makes hydraulic and battery powered crimpers costing up to $2500. What's the specific brand and model? Did you get this from Home Depot or otherwise, and what did you pay? Thanks, Allan Allan Sindelar al...@sindelarsolar.com NABCEP Certified PV Installation Professional NABCEP Certified Technical Sales Professional New Mexico EE98J Journeyman Electrician Founder (Retired), Positive Energy, Inc. 505 780-2738 cell On 5/1/2014 4:46 PM, Larry Crutcher, Starlight Solar Power Systems wrote: Ray, This might be a "great mind think alike" moment..…I own all 4 of those crimpers also. But, the best money I ever spent was on this Husky battery operated monster. I can reach into an area when replacing a lug that you could never reach with other crimpers. Larry On Apr 30, 2014, at 11:08 PM, Ray Walters r...@solarray.com wrote: Here's all the battery lug crimpers I tried over the years in order of the best to worst connections they produced: bdbagfhj.jpg Yes, believe it or not: the venerable Hammer crimper makes excellent connections. Its also Cheap, but its Slow, cumbersome, and can't be used in a J box. The V and indent connection with the thin wall lugs makes the ideal battery and DC connections. They look just like the crimps from Outback, Trace, Midnite,etc. I've cut them open on a band saw, and the fine strands are practically fused together into an almost solid cross section of copper with no voids, but no tearing of strands at the edges either. This crimper goes out on most jobs, as it fits in the bottom of the tool box. fhibhicd.jpg The Greenlee indentor crimper makes the same V crimp connection as the hammer crimper, but is faster, and can be used up in a j box. More expensive, and adjuster readings can't be counted on. I tighten the adjuster until I can just pull the handle down with putting some body weight into it, but not so much that I'm standing on it or straining the tool. Depending on the cable and lug combination, the setting may be 2 sizes smaller with thin wall lugs. Overall, this is what we use most of the time. I found that this set in a drill vice makes a good bench crimper, when you need to do a batch of battery jumpers. fcafcjdi.jpg I used this one for many years, also a V crimper, but has different dies. Crimp quality was not as good, as the dies tore into the lug some. Also changing the dies took time, and we once lost one of the dies, and it took months to get a replacement. Not adjustable for different lug and cable combos. bfdddceg.jpg The "UL" Hex type crimper that you will find at regular electrical supply houses. Quite expensive, but I am not a fan. The dies bend slightly under pressure and so the hex crimps are not aligned with each other. The dies tear the lugs, leaving sharp edges that can tear heat shrink, and there is no adjustment available to account for different cable and lug combinations. We have X flex from Cobra, MTW from Quick Cable, and some DLO from another supplier. All are UL listed 4/0 and all somewhat different in diam. and how the strands crush. I have had a connection failure with this tool, and cutting through a cross section of the lug was not as solid a crimp as the V type. I removed this tool from our shop, to avoid mistakes. I'm sure with regular Class B stranded THHN, and the heavy wall, color coded lugs, that this is a good tool, but for battery connections, it does not work as well with thin wall lugs. Finally, I do not recommend the heavy wall, long barrel lugs on batteries. The square lug end is just too big and thick, and can't bolt to battery terminals in some cases. We have had to grind away a corner for instance to have the heavy wall lugs land on an battery Flag terminal. The heavy terminals some what negate the advantages of flex cable in the first place. R.Ray Walters CTO, Solarray, Inc Nabcep Certified PV Installer, Licensed Master Electrician Solar Design Engineer 303 505-8760 ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wre
Re: [RE-wrenches] Battery cable crimper
Here's one almost identical to mine:http://www.ebay.com/itm/GREENLEE-GATOR-PLUS-EK06AT-CRIMPER-TOOL-/261468069343?pt=LH_DefaultDomain_0hash=item3ce0b61ddf Original Message Subject: Re: [RE-wrenches] Battery cable crimper From: la...@starlightsolar.com Date: Thu, May 01, 2014 4:51 pm To: "RE-wrenches" re-wrenches@lists.re-wrenches.org Hi Allen,It is huskie, not Husky. Ithink my auto correct unfixed it. I purchased this one used. I think it was about $1800. When I get back to the office tomorrow, I'll check the model #. It is a dieless design with 4 points that crimp from #4 to 4/0 ( I think it goes to 500). We make well over 300 crimps per month and this tool has been fast and flawless.Larry Original Message Subject: Re: [RE-wrenches] Battery cable crimper From: Allan Sindelar al...@sindelarsolar.com Date: Thu, May 01, 2014 4:20 pm To: RE-wrenches re-wrenches@lists.re-wrenches.org Larry, OK, need more info please... "Husky" is a Home Depot house brand for tools. "Huskie" makes hydraulic and battery powered crimpers costing up to $2500. What's the specific brand and model? Did you get this from Home Depot or otherwise, and what did you pay? Thanks, Allan Allan Sindelar al...@sindelarsolar.com NABCEP Certified PV Installation Professional NABCEP Certified Technical Sales Professional New Mexico EE98J Journeyman Electrician Founder (Retired), Positive Energy, Inc. 505 780-2738 cell On 5/1/2014 4:46 PM, Larry Crutcher, Starlight Solar Power Systems wrote: Ray, This might be a "great mind think alike" moment..…I own all 4 of those crimpers also. But, the best money I ever spent was on this Husky battery operated monster. I can reach into an area when replacing a lug that you could never reach with other crimpers. Larry On Apr 30, 2014, at 11:08 PM, Ray Walters r...@solarray.com wrote: Here's all the battery lug crimpers I tried over the years in order of the best to worst connections they produced: bdbagfhj.jpg Yes, believe it or not: the venerable Hammer crimper makes excellent connections. Its also Cheap, but its Slow, cumbersome, and can't be used in a J box. The V and indent connection with the thin wall lugs makes the ideal battery and DC connections. They look just like the crimps from Outback, Trace, Midnite,etc. I've cut them open on a band saw, and the fine strands are practically fused together into an almost solid cross section of copper with no voids, but no tearing of strands at the edges either. This crimper goes out on most jobs, as it fits in the bottom of the tool box. fhibhicd.jpg The Greenlee indentor crimper makes the same V crimp connection as the hammer crimper, but is faster, and can be used up in a j box. More expensive, and adjuster readings can't be counted on. I tighten the adjuster until I can just pull the handle down with putting some body weight into it, but not so much that I'm standing on it or straining the tool. Depending on the cable and lug combination, the setting may be 2 sizes smaller with thin wall lugs. Overall, this is what we use most of the time. I found that this set in a drill vice makes a good bench crimper, when you need to do a batch of battery jumpers. fcafcjdi.jpg I used this one for many years, also a V crimper, but has different dies. Crimp quality was not as good, as the dies tore into the lug some. Also changing the dies took time, and we once lost one of the dies, and it took months to get a replacement. Not adjustable for different lug and cable combos. bfdddceg.jpg The "UL" Hex type crimper that you will find at regular electrical supply houses. Quite expensive, but I am not a fan. The dies bend slightly under pressure and so the hex crimps are not aligned with each other. The dies tear the lugs, leaving sharp edges that can tear heat shrink, and there is no adjustment available to account for different cable and lug combinations. We have X flex from Cobra, MTW from Quick Cable, and some DLO from another supplier. All are UL listed 4/0 and all somewhat different in diam. and how the strands crush. I have had a connection failure with this tool, and cutting through a cross section of the lug was not as solid a crimp as the V type. I removed this tool from our shop, to avoid mistakes. I'm sure with regular Class B stranded THHN, and the heavy wall, color coded lugs, that this is a good tool, but for battery connections, it does not work as well with thin wall lugs. Finally, I do not recommend the heavy wall, long barrel lugs on batteries. The square lug end is just too big and thick, and can't bolt to battery terminals in some cases. We have had to grind away a corner for instance to have the heavy wall lugs land on an battery Flag terminal. The heavy terminals some what negate the advantages of flex cable in the first place. R.Ray Walters CTO, Solarray, Inc Nabcep Certified PV Installer, Licensed Mas
Re: [RE-wrenches] high efficiency modules in U.S.
marco, We used to stock Panasonic. I first heard about this in February when I tried to reorder inventory. I was told by a distributor that Panasonic increased the minimum order. Every one I contacted had no intention of ordering them due to this new minimum. In contacting Panasonic back in Feb. they told me they were working it out with Sunwize. Now they no longer reply to phone or email messages. Larry On Apr 25, 2014, at 9:26 AM, Marco Mangelsdorf ma...@pvthawaii.com wrote: Regarding Panasonic Solar news, this is the first I’ve heard of this. Anyone know why they’re no longer distributing in the U.S.? marco ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] high efficiency modules in U.S.
Hey Kirk, We have sold sanyo then Panasonic modules for over a decade. Not only were they highly efficient, they were the last truly high performance modules in the US. I have exhausted my search for them, only 3 left in stock. Panasonic will not return my phone calls or emails. There are dozens of China companies making small and expensive modules using SunPower cells but I doubt any are listed. I managed to buy some 327 and 435 Watt Sunpower modules dirt cheap from a guy. These were cosmetically blemished laminates that someone framed. Isc tests show they are producing rated power or higher but the frame is light and the cell surface has blotches under the glass. No listing on these either but my off grid customers in Mexico love them for the performance and cheap price per Watt. Does anyone know which of the 60 cell manufacturers have the highest module efficiency? Larry On Apr 25, 2014, at 5:05 AM, Kirk Herander k...@vtsolar.com wrote: Now that it appears Sanyo/Panasonic is no longer available, and Sunpower distribution is tightly controlled, what other high-efficiency alternatives are U.S.-available? Thanks. Kirk Herander VT Solar, LLC Un-Common quality since 1991 www.vermontsolarnow.com dba Vermont Solar Engineering NABCEPTM Inaugural Certificant VT RE Incentive Program Partner 802.863.1202 ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Wrong title on my inquiry ... Charge Controller Question!
Hi Karl, On their main page they claim charging ...with little or no electrolyte gassing. Gassing is a function of charge voltage. If you are charging deep cycle batteries properly, you will be gassing. After reading through the brochure, I'm not very impressed. Do yourself a favor and listen to what Ray said. Stick with proven, mainstream CC manufacturers. The fact that it is not an MPPT controller is a major drawback in any system over a few hundred Watts. Please share with us the operating and customization functions that you are looking for? Thank you, Larry Crutcher Starlight Solar Power Systems On Apr 22, 2014, at 12:27 PM, Karl Jaeger kjae...@lightwavesolar.com wrote: From: Karl Jaeger Sent: Tuesday, April 22, 2014 2:28 PM To: RE-wrenches@lists.re-wrenches.org Subject: RE: Fault Current Greetings Wrenches, We’re considering a new charge controller for an upcoming project that offers a wide range of operation and customization. Has anyone had experience with this product? General specs and link below: Sollatek - Solar Control Centre/ Solar Charge Controller 12/24/or 48V 10-100V Voltage Range 90-960A Max Charge Current http://www.sollatek.com/product/solarcontrolcentre/ Thank you in advance! Karl Jaeger LightWave Solar ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] EMP question
Good answer Wayne…how strong AND how far away. I'm sure the inverse-square law apples here but if you don't know the initial power and distance, it does not matter much anyway. Now, for a hilarious interjection, there is a customer in our showroom at this moment asking about PV solar in case there is am EMP that takes out utility power! So funny. Larry On Apr 22, 2014, at 2:12 PM, Wayne wa...@pureenergysolar.com wrote: We get that question all the time. We reply with the same question that we ask them with regard to hurricanes. Well... how strong will it be? We have not found any good supported answer on line or otherwise. However, the answer I like the most is You will either be completely fine or totally screwed! There is no in between. Oh and here is your aluminum foil helmet.. no charge. Wayne Irwin, President License #CVC56695 State Licensed Solar Contractor Pure Energy Solar International Inc. wa...@pureenergysolar.com http://PureEnergySolar.com 352 377-6527 Office 352 336-3299 Fax The Sun Is Always Shining! The content of this message is Pure Energy Solar Confidential. If you are not the intended recipient and have received this message in error, any use or distribution is prohibited. Please notify me immediately by reply e-mail and delete this message from your computer system. Thank you. ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Solar World shattered module
Hi David, We have thousands of PV modules installed mostly on RV's. An RV roof can be a very abusive environment with turbulence, flying debris, driving under limbs, heavy vibrations and more. I have not had any glass breakage that could not be accounted for, i.e, breaking for unknown reason. But, we have had hoodlums shooting at PV modules. Perhaps look at the back for a hole. Larry On Apr 21, 2014, at 3:32 PM, Dave Palumbo d...@independentpowerllc.com wrote: Wrenches, I have a customer with one SW 230 poly V2.0 frame (top mount) module that has shattered glass. It is on a DPW TPM10 pole mount. She noticed it the other day and does not think that it was hit by anything. I agree that is unlikely based on the site conditions. Other than by a falling tree, thrown rock, or twisted frame – is there another way that glass shatters on a 65 degree tilted pole mount like this? We installed the system 2 years ago. The module was on the lower corner of the array. · Is it likely that this modules frame was being pressured by the module(s) above it? TPM has two rows of 5 modules in landscape, so this bottom module has 4 modules mounted above it. Again it is a top mounted DPW pole array. · Or, is there another way that glass shatters on this type of module? I have not visited the site yet, just received the phone call today. David Palumbo Independent Power LLC 462 Solar Way Drive Hyde Park, VT 05655 (802) 888-7194 ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] AC coupling with Fronius
Mac, I have a customer with 17kW on 3 Fronius inverters. He connected a cheap 40kW china diesel generator during a week long power outrage. I was amazed when he told me they sync'd up with no problems. Larry On Apr 16, 2014, at 1:44 PM, Mac Lewis maclew...@gmail.com wrote: Hello wrenches, Has anyone had good success AC coupling with Fronius Inverters? If so, what equipment did you use? Was this with an IG or an IG Plus? I have had quite a few people lately with Fronius Inverters that would like a backup solution and I'm not comfortable AC coupling these, but could potentially be persuaded. Thanks Mac Lewis ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Zomeworks Cool Cell
Sorry for reposting but perhaps my original post was missed. Has anyone used the Zomeworks Cool Cells? http://www.zomeworks.com/battery-electronic-enclosures/cool-cell/ Thank you, Larry Crutcher Starlight Solar Power Systems On Mar 28, 2014, at 3:14 PM, Larry Crutcher, Starlight Solar Power Systems la...@starlightsolar.com wrote: Wrenches, Have any of you used the Zomeworks Cool Cell battery enclosures? I would like to hear about their effectiveness, especially if you have used them in a very hot, dry climate. What maintenance is required? Zomeworks says on their website that one location kept the battery/equipment 41° below ambient. The customers site is a remote desert location with ambients up to 118°. The only access is by helicopter so I want to compare the total cost verses replacing batteries more frequently. I have built a few remote power systems here in the desert with Hoffman boxes and added some shading on sides and tops (pic). I used Sun Xtenders in these and they are still performing after 7. Thank you, Larry Crutcher ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
[RE-wrenches] Midnite Solar Whizbang Jr.
Has anyone successfully installed a Whizbang Jr. battery monitor for the Midnite Classic yet? I'm having strange trouble with a Classic after firmware updates and WB install and wonder if others have had trouble. Thank you, Larry Crutcher Starlight Solar Power Systems ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Battery Temp, SOC, and Voltage
Ray, I have never considered the effect of battery voltage at low temperature under load, only capacity loss, so you got me thinking. Here's a simple idea: why not put a battery in a freezer with your expected load and monitor voltage, or better yet, chart to see where it lands. I would be doing this test right now but I don't have a freezer at the shop. Larry On Mar 30, 2014, at 12:26 PM, Ray Walters r...@solarray.com wrote: Hi folks; I have pondered LVD set points to protect batteries from freezing, and realized I don't have enough information. While temp compensation is fairly straight forward when charging ( increase charge voltage when cold, reduce when hot, manufacturer's #s are close to charge controller assumptionsno problem) However, it is not at all clear what the battery voltage is at low temperatures, when the battery is at rest or during discharge. I've actually found a chart that shows battery voltage at rest for a fully charged battery Decreases at cold temps. (Look at voltage at bottom of chart) cighdiif.jpg I know battery capacity is reduced, but the voltage actually goes down, while charge voltage goes up? what happens during discharge? is the voltage higher or lower at low temps? I know that it becomes complicated with discharge rate, so that higher discharge rates create artificially lower voltages, hence the wonderful LVD settings of the old Trace SW 4024, which had 3 different voltage set points for 15 minutes, 2hrs, and 24 hrs periods. However, were these set points temperature compensated? and if so, was it a negative or positive compensation? Example: I want to keep electrolyte specific gravity above 1.15 (roughly 40% SOC) as this has a freeze point of about 5 deg F. So voltage for a lead acid battery at room temperature at 40% SOC is about 12 volts (open circuit, at rest) Just looking at this chart, and applying the same voltage ratio to a battery at 40% SOC, I'm seeing a set point of 11.8 v for a battery at rest at 5 deg F. But this doesn't account for discharge rate, and I don't know whether to fudge voltage up or down based on discharge rate at low temps. Basically I want set points that protect the battery, but aren't overly conservative. Anyone have a temperature compensation chart (or coefficient) that applies to different Discharge rates? -- R.Ray Walters CTO, Solarray, Inc Nabcep Certified PV Installer, Licensed Master Electrician Solar Design Engineer 303 505-8760 ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Zomeworks Cool Cell
….after 7 years. Wrenches, Have any of you used the Zomeworks Cool Cell battery enclosures? I would like to hear about their effectiveness, especially if you have used them in a very hot, dry climate. What maintenance is required? Zomeworks says on their website that one location kept the battery/equipment 41° below ambient. The customers site is a remote desert location with ambients up to 118°. The only access is by helicopter so I want to compare the total cost verses replacing batteries more frequently. I have built a few remote power systems here in the desert with Hoffman boxes and added some shading on sides and tops (pic). I used Sun Xtenders in these and they are still performing after 7. Thank you, Larry Crutcher ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Arcing from inside Trace DR2412
Hi Benn, Over the years I have seen several of the DR inverters burn up near the transfer switch, or perhaps the switch. I've never dug into the chars to determine what actually failed. I would replace that relic before the inevitable happens. Larry Crutcher Starlight Solar Power Systems On Mar 27, 2014, at 3:36 PM, Benn Kilburn b...@skyfireenergy.com wrote: Wrenches, An off-gridded (system installed by others) called me yesterday with a concern. His system is older and has had mods added over the years. It is up to 7x Siemens SP75 and 1x She'll SQ80P. I believe the inverter is the original. It is a Trace DR2412, and where the concern stems from. He says he has noticed an arc from inside the inverter about 3 of the last 8 times he has fired up his generator (remote start next to inverter). He described seeing the arc thru the vent fins on the top right of the inverter. Is this internal arc typical when a generator connects to the inverter and he just hasn't noticed it before? ...or is his ol Trace toast? Thanks, benn Sent from a 'smart' phone, with touch screen keys. Please excuse shortcuts and typos. ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
[RE-wrenches] Uni-Solar, Kaneka…now Panasonic?
Wrenches, What high performance PV modules are being sold in the US? I can't find Panasonic modules anymore. I have written to them twice but they can't direct me to any distribution in the US. They insist that Sunwize will have them but Sunwize says they have no plans yet to purchase again. From what I can tell, the next best thing is Sunpower modules with -0.38% /K temp coefficient. Are there any others to consider? Larry Crutcher ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Uni-Solar, Kaneka.now Panasonic?
Dave and August, I'm looking for high performance (capturing the most energy), not high necessarily high efficiency (using less space). Efficiency would be a bonus, though. LG are just average performance. Example: Uni-Solar was one of the lowest efficiency modules ever made but holds the record for highest performance. Thank you, Larry Crutcher On Mar 14, 2014, at 8:52 AM, August Goers aug...@luminalt.com wrote: Hi Larry, LG is selling Neon panels which are pushing 300 W for a 60-cell arrangement. My understanding is that they are sold out in the US but sooner or later more will be imported. Focused Energy is a distributor of them. http://www.lg.com/us/commercial/solar-panels SunPower is our workhorse high efficiency module. The new X series 335 and 345 are hard to beat. Best, August -Original Message- From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Larry Crutcher, Starlight Solar Power Systems Sent: Friday, March 14, 2014 8:34 AM To: RE-wrenches Subject: [RE-wrenches] Uni-Solar, Kaneka.now Panasonic? Wrenches, What high performance PV modules are being sold in the US? I can't find Panasonic modules anymore. I have written to them twice but they can't direct me to any distribution in the US. They insist that Sunwize will have them but Sunwize says they have no plans yet to purchase again. From what I can tell, the next best thing is Sunpower modules with -0.38% /K temp coefficient. Are there any others to consider? Larry Crutcher ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Uni-Solar, Kaneka.now Panasonic?
Thanks for your reply August. I'm quite surprised that you have two Uni-Solar systems not performing well. Third party testing consistently proved them the top performer. (eg. Santa Cruz and Tucson sites) With my experience both on and off grid, I am convinced. Panasonic was great because, in addition to performance, it also had very high efficiency. In my world of cramming 2kW+ PV arrays on the roof of an RV or boat, that is also a necessity. Example: Here's todays job; the last of my Panasonic stock, 1410 Watts on a 40' coach. No possible way to do this with standard 60 cell modules.Bottom line for me is, someone has abest and worst performing PV module just like someone has the most efficient. Glad to hear your SunPower installs areproducing above expectations. That's probably what I will go with.LarryOn Mar 14, 2014, at 9:50 AM, August Goers aug...@luminalt.com wrote:Hi Larry,It sounds like you are talking about the temperature coefficient or energyyield per kW-peak? Uni-Solar was great on paper but I'm not so sure aboutreal world performance. We have a couple of Uni-Solar systems installed awhile back and they are not doing so well in the real world. Companieskeep coming to me over the years claiming that their modules harvest morekWh per kW peak and it is really hard to keep everything straight.Certainly the PTC ratings help in comparison to STC. Then there are paperslike this from SunPower claiming 8 to 10% more energy per Watt:http://www.solarips.com/admin/content/uploads/SunPower_Yield_Report_BEW.pdfSunPower also claims that their modules degrade less annually compared toothers.And here's a doc comparing PV module performance measurements:http://fire.nist.gov/bfrlpubs/build05/PDF/b05047.pdfEach year we try to compare the actual monitored performance of oursystems compared to our as-built production estimates at time of theinstallation completion. In general, I've found that both SunPower andother standard efficiency modules seem to outperform the normal PV-Wattscalculation by 7 to 10%. In 2012 our systems were averaging about 17%above our estimates! I haven't seen a huge difference between SunPower andstandard efficiency modules. Furthermore, I haven't seen the performancegains that microinverter manufacturers are claiming compared to stringinverters. I admit that our informal comparison is not perfectlyscientific because there are simply too many variables that we don'tcapture. My main concern is material and or workmanship degradation inmodules over the long haul. Only time will tell.Best,August___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
[RE-wrenches] Purchasing SunPower modules
It looks like SunPower will only sell direct to authorized dealers. Are there any SunPower distributors that can sell to non-authorized dealers? Thank you, Larry ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Lithium ion
Todd, Lithium batteries offer many distinct benefits over lead acid. Life, weight, size, time to charge and more. For me, it is market specific. Our primary business is designing, installing and servicing large power systems in recreational vehicles. Hundreds of our customers only use the RV seasonally by coming to SW Arizona to escape winter. When they go home, they leave the RV in storage for 6 months, not healthful for batteries. Our other customers are off grid residents n Mexico (US and Canadians mostly). They, too, are seasonal and leave their homes for 6 months or more. I regularly recycle over 30,000 pounds of batteries at our store and I'm only open for 6 months per year! Most customers that come in for batteries have damaged theirs in just a few years. The frequent culprit: deficit charging. A Lithium battery will not be harmed by under charging, they never need to reach 100% SoC, or leaving for long periods partially charged. You can disconnect the battery at 60% SoC and leave it for a year and it will be ready to use again when you turn it back on. I am fully committed to offering LFMP batteries as a lead acid replacement for RV's and off grid homes. Larry On Feb 27, 2014, at 7:24 PM, toddc...@finestplanet.com wrote: not trying to be dumb here, but what's the attraction to lithium ion batteries? todd On Thursday, February 27, 2014 3:44pm, Larry Crutcher, Starlight Solar Power Systems la...@starlightsolar.com said: Jay, I'm an authorized dealer of GBS systems and we stock and sell them here in our retail store. I can build any voltage bank in 12 volt increments. All our systems include EMS computer, cell level balancing, temperature and SoC monitoring with over/under voltage protection. Basically a turn-key setup. We tested CALB for a while and tried to get other lithium brands in but the distribution market in the USA is a horrible mess when it comes to Lithium batteries. I got frustrated after trying to communicate with importers and choose GBS because they had the best and most intelligent response to me. GBS batteries are LiFeMgPO4 or LFMP which is safer, won't catch fire. When comparing life cycles, LFMP is lower cost than any lead acid batteries. If you're interested, I can configure a system for you and get you discount cost for resale. Contact me off the board. Larry 928-342-9103 Sent from Finest Planet WebMail. ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Lithium ion
Ray, I had a 100AH battery for about 3 weeks of testing. I worked it hard. I even over discharged it once. It worked perfectly at different charge and discharge rates. The most interesting thing was that the 100Ah battery regularly provided 115AH at 95% DoD. I would sell the CALBS but, again, the US distribution is only through other dealers. There are several people importing them but they all teated me like the end user or consumer. For off grid use, the Lithium battery industry has a long way to go to make these mainstream. I hope to change that some. Larry On Feb 27, 2014, at 7:43 PM, Ray Walters r...@solarray.com wrote: Larry; You mentioned you tested CALB batteries; what was your experience with them? R.Ray Walters CTO, Solarray, Inc Nabcep Certified PV Installer, Licensed Master Electrician Solar Design Engineer 303 505-8760 On 2/27/2014 4:44 PM, Larry Crutcher, Starlight Solar Power Systems wrote: Jay, I'm an authorized dealer of GBS systems and we stock and sell them here in our retail store. I can build any voltage bank in 12 volt increments. All our systems include EMS computer, cell level balancing, temperature and SoC monitoring with over/under voltage protection. Basically a turn-key setup. We tested CALB for a while and tried to get other lithium brands in but the distribution market in the USA is a horrible mess when it comes to Lithium batteries. I got frustrated after trying to communicate with importers and choose GBS because they had the best and most intelligent response to me. GBS batteries are LiFeMgPO4 or LFMP which is safer, won't catch fire. When comparing life cycles, LFMP is lower cost than any lead acid batteries. If you're interested, I can configure a system for you and get you discount cost for resale. Contact me off the board. Larry 928-342-9103 ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Source for wire
Perhaps this? http://www.waytekwire.com/products/1461/Marine-Wire-Cable/--of-Conductors=2 Larry On Feb 28, 2014, at 5:54 PM, Allan Sindelar al...@positiveenergysolar.com wrote: Wrenches, Simple request, please: who carries 10/2 jacketed submersible cable, specifically to use with the Shurflo 9300 pump? Conventional pump suppliers don't carry it, as any pump with metal parts needs a third conductor for ground, and usually run 240V. The 9300 fits only 10/2 or 12/2 wire without ground and with flat jacketing. It must be flat-jacketed to seal to the cable gland. Thank you, Allan -- Allan Sindelar al...@positiveenergysolar.com NABCEP Certified PV Installation Professional NABCEP Certified Technical Sales Professional New Mexico EE98J Journeyman Electrician Founder, Positive Energy, Inc. A Certified B CorporationTM 3209 Richards Lane Santa Fe, New Mexico 87507 505 424-1112 office 780-2738 cell www.positiveenergysolar.com ___ ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Lithium ion
Jay, I'm an authorized dealer of GBS systems and we stock and sell them here in our retail store. I can build any voltage bank in 12 volt increments. All our systems include EMS computer, cell level balancing, temperature and SoC monitoring with over/under voltage protection. Basically a turn-key setup. We tested CALB for a while and tried to get other lithium brands in but the distribution market in the USA is a horrible mess when it comes to Lithium batteries. I got frustrated after trying to communicate with importers and choose GBS because they had the best and most intelligent response to me. GBS batteries are LiFeMgPO4 or LFMP which is safer, won't catch fire. When comparing life cycles, LFMP is lower cost than any lead acid batteries. If you're interested, I can configure a system for you and get you discount cost for resale. Contact me off the board. Larry 928-342-9103 On Feb 26, 2014, at 10:44 AM, Jay Peltz j...@asis.com wrote: Does anyone know of a distributor of lithium ion for re systems And recommended brands Thanks Jay Jay @asis.com ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
[RE-wrenches] Panasonic PV modules
Desperate here….Does anyone know where I can still purchase Panasonic PV modules? Any quantity. Thank you, Larry Crutcher (928) 342-9103 ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] controllers
Hi Ron, I agree and share the frustration. I've been asking Rick at Blues Sky Energy for a few years to build an IPN network controller that can handle 100 volts input and 60 amps out. With the IPN Pro, the BSE controllers are the very best in battery monitoring and terminating charge based on AH returned. If Morningstar made their controllers less archaic to program, I would consider using them. I have not found anything agreeable that fits this gap in charge controllers. As you discovered, the 3024iL can only handle one 60 cell module, unless you can find some 200 Watt modules. The next step is to the Midnite Classic which is a 96 amp CC. We uses lots of 60 and 72 cell modules on 12 volt systems. We have installed quite a few Classics but many of the systems are only 600 - 800 Watts. The problem I see for manufacturing is the price point. A 40 amp BSE controller is about $350 and the Midnite Classic is about $520 (online prices). A $170 spread does not leave much room to built a 60 amp IPN network controller. But I WOULD buy them by the dozen, if only…. Larry On Feb 20, 2014, at 3:49 PM, RM You solarea...@solareagle.com wrote: Anybody have any recommendations for a 45a MPPT controller other than Morningstar? I’ve had absolutely miserable tech support from Morningstar so I want to drop the line but I need something that will handle 2 60 cell modules in the 250w range for off grid applications. I use a Blue Sky for single panels and a Midnite Classic for three or more but in the middle the only one I can see is the Morningstar. Outback, Midnite and Xantrex are all overkill for just a couple of panels unless they want to expand in the future. Ron ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Midnite solar Charge controllers
Jerry,People do like to touch stuff. One of the benefits of the Midnite controllers is you can remove the MNPG after programming and the user can not alter any settings. Some customers need this type of interference. Here's a picture of a thermal runaway in an AGM battery after a customer, while playing with a charge controller program, turned the voltage up to 3 Vpc.Larry On Feb 17, 2014, at 9:06 PM, Jerry Shafer jerrysgarag...@gmail.com wrote:Has anyone had an issue with Midnite solar Charge controllers loosing programming. I have had Out back FM 80 do this and it was an software issue they fixed it. Now I have the same thing with midnite either that or the customer is messing with it and this is also a good possibility but before I go there I want to confirm with you all out there. The issue from Outback is if the CC is powered down on both sides it will loose memory, I cant confirm this as the customer is away and I cant get on site but we have Nickle Iron batteries that require high charge voltage to charge at all and it seams to not maintain the charge voltage setting. Thanks Jerry___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] AC Back feed from Radian.
Ditto Tom, seen this too often in Mexico. I carry a manometer to make check the pressure at the LP input to the generator with the engine running. Make sure it is at/above 11 WC when it starts to act up. If the regulator is at the tank, long vapor runs can cause too much pressure loss. Larry On Feb 17, 2014, at 1:36 PM, Tom Duffy t...@thesolar.biz wrote: Hi Guys We have had “icing” problems here in Central America as well where the gas company put in ½’ pipe to a 12K Gillette Generator, same description the gen would initially start and run fine but then it went erratic the Radian didn’t like it, the customer wanted to blame the Radian (I was sure it wasn’t) The installer/dealer couldn’t figure it out. I went out and immediately saw the small pipe, plus they had bent a crimp into the incoming fuel line as well. ¾” line fixed the whole thing. LP has a lot of moisture and will always have delivery problems with funky installation of pipe. Seems that a lot of gas guys just hook up kitchen ranges (Here) Kind regards Tom Duffy Senior Solar Design Engineer image002.png E-Mail: t...@thesolar.biz Panama Office: 507-6126-1253 Direct Toll Free: 888-503-6772 International: 575-539-2111 SKYPE Address: thesolarbiz Although no trees were killed in the sending of this message, a large number of electrons were terribly inconvenienced. Confidentiality Notice: This message including any attachments is for the sole use of the intended recipient and may contain confidential and privileged information. Any unauthorized review, use, disclosure or distribution is prohibited. If you are not the intended recipient, please contact the sender and delete any copies of this message. ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] DC Solenoid Coil Current
...600 Watt HOURS per day…. It must be active 24/7. If deactivated, the battery is disconnected. Thanks but this is irrelevant now since I found a 500 amp solenoid that only consumes 41 WH per day. Larry On Feb 13, 2014, at 4:33 PM, Jerry Shafer jerrysgarag...@gmail.com wrote: OK So if you only have the 600 watts per day when you are either on shore power or on a genny can you design the system to not be needed when they are off and kill that load Jerry On Feb 13, 2014 11:51 AM, Larry Crutcher, Starlight Solar Power Systems la...@starlightsolar.com wrote: Hi Jerry, The no-fault condition from the CPU is +12Vdc. A fault causes 0 volts. These are the contactors I plan to use: http://www.alliedelec.com/search/productdetail.aspx?SKU=70062412 Larry On Feb 13, 2014, at 12:38 PM, Jerry Shafer jerrysgarag...@gmail.com wrote: So Ian clear does the fault activate the relay or does the absence of the fault activate the relay because its usually best to have a absent or no fault hold the relay on and if anything fails as a the relay will rest this can be done with motorized on or contactor high load switch, you should also look at the switch AIC rating also Jerry___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] DC Solenoid Coil Current
Hi Jerry, The no-fault condition from the CPU is +12Vdc. A fault causes 0 volts. These are the contactors I plan to use: http://www.alliedelec.com/search/productdetail.aspx?SKU=70062412 Larry On Feb 13, 2014, at 12:38 PM, Jerry Shafer jerrysgarag...@gmail.com wrote: So Ian clear does the fault activate the relay or does the absence of the fault activate the relay because its usually best to have a absent or no fault hold the relay on and if anything fails as a the relay will rest this can be done with motorized on or contactor high load switch, you should also look at the switch AIC rating also Jerry On Feb 11, 2014 4:43 PM, Larry Crutcher, Starlight Solar Power Systems la...@starlightsolar.com wrote: Hello Wrenches, We're preparing to offer Lithium batteries to some of our customers as a replacement to lead acid in recreational vehicles. RV batteries can have multiple charge sources simultaneously so I have worked out protective circuitry to interface with a EMS computer. To insure failsafe operation, I need to install 2 solenoids that will be active 24/7, opening only when fault conditions are met. The solenoids I have looked at (200 amp) have a coil current of about 1 ampere each which equates to 600Wh daily consumption. I'de like to reduce that BUT the computer only provides a +12v or 0 volt state. Does anyone know of a latching solenoid that will work with a 12v hi/lo voltage state, OR an interface or circuit for hi/lo to control latching relay OR a solenoid with a very low quiescent current when on? Many thanks in advance, Larry Crutcher ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Lead-selenium tubular plate batteries
Hi Allan, FYI, their data sheet shows cycle life at 50% DoD is 1850 or 5 years. The 20 year life is probably for standby use. I looked at these many years ago but I have not tried these because of price. Larry On Feb 11, 2014, at 9:27 PM, Allan Sindelar al...@positiveenergysolar.com wrote: Has anyone tried these? This is my first awareness of them. http://www.renewableenergyworld.com/rea/companies/sbs-battery/products/stt-opzs-series-flooded-tubular-batteries Description: 20 year Lead-Selenium Tubular Plate Batteries: 12V 55-165Ah, 6V 220-330Ah, 2V 110-3585Ah Best to ask here first! Thank you, Allan -- Allan Sindelar al...@positiveenergysolar.com NABCEP Certified PV Installation Professional NABCEP Certified Technical Sales Professional New Mexico EE98J Journeyman Electrician Founder, Positive Energy, Inc. A Certified B CorporationTM 3209 Richards Lane Santa Fe, New Mexico 87507 505 424-1112 office 780-2738 cell www.positiveenergysolar.com ___ ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] DC Solenoid Coil Current
Pure genius, Dan. Exactly what I needed. You are truly an asset to the Wrench board. Thanks Frank for the tip on the MOSFET. Good to hear from you. Thank you, Larry Crutcher On Feb 11, 2014, at 6:16 PM, Exeltech exelt...@yahoo.com wrote: Larry, A latching relay isn't suitable for fail-safe applications. Look into the Kilovac Czonka III EV200HAANA. This series has a coil economizer that reduces coil current (and thus power consumption) after pull-in. Rated coil power is less than 2 watts. Models are good to 900Vdc and up to 500A. Coil inrush current on one model I found is spec'd at 3.8 A for a 130 milliseconds, so you'd need an external transistor to drive it from the computer. If power consumption is a critical aspect, use a suitable MOSFET. If you don't mind wasting another watt or two, a bipolar NPN will also work. The coil current throttles back to less than 100 mA at 12Vdc after contact closure. Because a specialized electronic power supply is driving the coil, Kilovac rates the DC input to the coil driver at anything from 9Vdc to 36Vdc. Here's the Allied page: http://www.alliedelec.com/search/productdetail.aspx?SKU=70062411 Not cheap .. but excellent quality. If you're a registered reseller with Allied, the $ is less. Dan On Tue, 2/11/14, Larry Crutcher, Starlight Solar Power Systems la...@starlightsolar.com wrote: Subject: [RE-wrenches] DC Solenoid Coil Current To: RE-wrenches re-wrenches@lists.re-wrenches.org Date: Tuesday, February 11, 2014, 6:43 PM Hello Wrenches, We're preparing to offer Lithium batteries to some of our customers as a replacement to lead acid in recreational vehicles. RV batteries can have multiple charge sources simultaneously so I have worked out protective circuitry to interface with a EMS computer. To insure failsafe operation, I need to install 2 solenoids that will be active 24/7, opening only when fault conditions are met. The solenoids I have looked at (200 amp) have a coil current of about 1 ampere each which equates to 600Wh daily consumption. I'de like to reduce that BUT the computer only provides a +12v or 0 volt state. * Does anyone know of a latching solenoid that will work with a 12v hi/lo voltage state, * OR an interface or circuit for hi/lo to control latching relay * OR a solenoid with a very low quiescent current when on? Many thanks in advance, Larry Crutcher ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] morning star ts-mppt-60-600
Hello William, There is a hassle factor with the Morningstar MPPT controllers. If you need a custom charge setting, and I do most of the time, then you must download and install software, use a RS-232 data cable, and reprogram settings from a Windoz PC. That's SO 1980's!. We don't sell many Morningstar controllers because many of our battery systems are Lifeline, Sun Xtender or FullRiver AGM batteries. None of the DIP switch settings are right for those batteries. Also, none are right, but close, for Trojan or Crown batteries which we also sell. Besides that, I left the world of Microsoft many moons ago and I also can't find my DB9 cables anywhere. Larry On Feb 12, 2014, at 12:50 PM, will...@millersolar.com wrote: Hello again: Anyone have any experience with these charge controllers? How about the meter? Thanks so much for all of the help. William Miller ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] morning star ts-mppt-60-600
OK, so you need a PC, an internet connection, a router, download and install software, network PC to router, plug in CC, connect PC to the controller, then you can change parameters. Got it…..still say hassle. There is no doubt the controllers are feature laden and most of their smaller controllers that we have sold have not failed. most. On a positive note, they are great about warranty. Larry On Feb 12, 2014, at 2:49 PM, James Jefferson Jarvis j...@aprsworld.com wrote: The Morningstar TriStar MPPT 60 and the 600 volt 60 amp both have ethernet built in. Yes, you use their MSVIEW software, but no you don't need an RS-232 cable. The MSView software allows you to easily load previously developed settings and to easily save and print those settings. After putting lots of Morningstar products at remote site, I found found them not to crash, glitch, reset, or do anything besides work. I've found the built-in communications (using industry standard Modbus) to be excellent and easy to manage. I've not found any other charge controller manufacturer that has unified software across their whole product line, a unified communications standard, and the level of built-in monitoring the Morningstar products have. I'll take RS-232, RS-485, or Ethernet any day over proprietary stuff that doesn't work. I don't have any vested interest in Morningstar. I've just spent a lot of time developing monitoring and control software to work with all manners of different equipment. And when I get my choice, I go with the Morningstar stuff because I know it works well. -James Jarvis APRS World, LLC www.aprsworld.com On 02/12/2014 03:31 PM, Larry Crutcher, Starlight Solar Power Systems wrote: Hello William, There is a hassle factor with the Morningstar MPPT controllers. If you need a custom charge setting, and I do most of the time, then you must download and install software, use a RS-232 data cable, and reprogram settings from a Windoz PC. That's SO 1980's!. We don't sell many Morningstar controllers because many of our battery systems are Lifeline, Sun Xtender or FullRiver AGM batteries. None of the DIP switch settings are right for those batteries. Also, none are right, but close, for Trojan or Crown batteries which we also sell. Besides that, I left the world of Microsoft many moons ago and I also can't find my DB9 cables anywhere. Larry On Feb 12, 2014, at 12:50 PM, will...@millersolar.com mailto:will...@millersolar.com wrote: Hello again: Anyone have any experience with these charge controllers? How about the meter? Thanks so much for all of the help. William Miller ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org -- -James Jefferson Jarvis APRS World, LLC +1-507-454-2727 www.aprsworld.com ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
[RE-wrenches] DC Solenoid Coil Current
Hello Wrenches, We're preparing to offer Lithium batteries to some of our customers as a replacement to lead acid in recreational vehicles. RV batteries can have multiple charge sources simultaneously so I have worked out protective circuitry to interface with a EMS computer. To insure failsafe operation, I need to install 2 solenoids that will be active 24/7, opening only when fault conditions are met. The solenoids I have looked at (200 amp) have a coil current of about 1 ampere each which equates to 600Wh daily consumption. I'de like to reduce that BUT the computer only provides a +12v or 0 volt state. Does anyone know of a latching solenoid that will work with a 12v hi/lo voltage state, OR an interface or circuit for hi/lo to control latching relay OR a solenoid with a very low quiescent current when on? Many thanks in advance, Larry Crutcher ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Charging a HUP
Hi Bruce, Please explain feeding it properly. Charging any lead acid battery slowly actually preserves battery life. As long as you are achieving the recommended charge voltage (temperature compensated) for long enough time, and reaching 100% SoC regularly, you are caring for the battery. At 82kWh battery capacity and 6.5kW PV, the customer may have a hard time getting to 100%. You did not mention, but I HOPE you have a battery capacity meter in the system. It's mandatory if they want to care for the battery. Since the customer has a small generator, they need to realize the limitations and reduce their loads during generator time so you can use the full output. Larry On Feb 7, 2014, at 11:46 PM, br...@willpowerelect.com wrote: Hi All, 3 VFX 3648 2 FM 80 6.5 kw solar 12 kw generator PSX 240 on generator output and VFX stacking Mate 3 HUP 1690 ah System design considering 45 amp charge current from each VFX totaling 135 amps. (135 x ~55v = 7.42kw) Potential charge current from 2 arrays and FM 80's, 90 - 100 amps. On a good day, reasonable to expect 200+ amps? Have not been able to exceed 90 amps for more than 30 minutes, with the generator putting out about 9 kw before it's 70 amp 2pole breaker trips. L1 42 amps, L2 37 amps. 5 amps neutral. Load banked to 12.3 kw (51 amps @ 240v) resistive without breaker trip. I have had to dial back the maximum charge current in the Mate 3 to 12 amps each on two of the inverters (L1 and L2) and 8 on inverter 3 to keep the generator from tripping out when customer turns on the microwave or coffee pot. In effect, 42 amps charge @ 240 v = 7.6 kw. At the battery, I'm only seeing 80 amps of charge current. Running loads are typically less than 1 kw but there has been a of construction going on with chop saws and compressors creating annoying spikes that are easily handled by the inverters when the generator is off. I don't want to kill this new battery by not feeding it properly! I would have put in a larger generator, but the owner bought the 12 kw before deciding on the new battery. I thought the 12 would be merely adequate, but not so Any suggestions? Thanks! Bruce Fiero-RMI sigimg0.jpeg I'd put my money on the sun and solar energy. What a source of power! I hope we don't have to wait until oil and coal run out before we tackle that. T. Edison, 1931 ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Battery venting issue
Allan, The primary concern should be the volume of gas discharge if over voltage occurs. This study helped me understand the risks: http://www.sonnenschein.org/Gassing.htm Quote from the study: Gassing according to IEC 896/2-Oct 95 @ 2.3v / cell within 30 days was measured @ 5mL/cell/ah while Overcharging @ 2.48v/cell caused 900m L / cell / ah within 30 days! Also heres a technical bulletin from CD that discusses how long a 2% concentration takes during overcharge. See document 41-6739: http://www.cdtechno.com/resource/support_doc.html Thank you, Larry Crutcher (928) 342-9103 www.starlightsolar.com la...@starlightsolar.com Retail Store Warehouse 2998 Shari Ave. Yuma, Az 85365 USPS Postal Mail Only 11881 S Fortuna Road, #210 Yuma, AZ 85367 On Feb 5, 2014, at 7:38 PM, Allan Sindelar al...@positiveenergysolar.com wrote: Wrenches, I need a bit of help here if you have it. Since 2002 we have installed somewhere between 30 and 35 systems with sealed batteries installed in manufactured enclosures, originally Outback enclosures and in recent years Midnite MNBE enclosures. At least ten of these have been indoors in one form or another - usually a laundry or mechanical room. Our battery of choice is Concorde SunXtender. We have only added mechanical ventilation (Zephyr Power-Vent to outside) if the battery enclosure itself is sealed. Nearly all of these have been permitted and inspected systems, and we have never had a problem with the inspectors. Of course, we always vent flooded systems to the outside, nearly always using a Power Vent fan. Now we have. An AHJ failed a system for lack of ventilation, and our attempts to resolve it have not been effective. The Chief Electrical Inspector has weighed in, and we are right at the point of filing a Request for Code Interpretation with the New Mexico Electrical Division Technical Advisory Panel. I have not wanted to just add ventilation to pass inspection because of the precedent doing so is likely to set for future installations. The GC on the job supports my attempts to push back, as do the homeowners. The Chief Inspector thinks that the 700 square foot unheated room in which our system is installed is a bedroom; it's actually a storeroom for the homeowners' collectible book home business. My request: please send me documented work by others establishing that PV systems with sealed VRLA batteries are used specifically because they are considered safe without venting to the outside. If you know of good online links, I could use them too. For example, the AHJ asked for a document stating that the batteries or the enclosure were specifically approved for this use in an indoor location. I can't - Midnite battery enclosures are simply listed to UL508A, which is industrial control panels and there's nothing specific to this application in the standard. To me this is a common-sense issue, but common sense doesn't cut it when needing to prove a procedure. Can anyone help? For what it's worth, or for those Wrenches with too much spare time, below is the text of the original defense of our installation that I sent to the AHJ. His response was that he's not an electrical engineer and this would have to be taken upstairs. For what it's worth, I'm not an EE either... My frustration is showing, I'm sure. Thank you for any links, reports or other resources you may be able to send my way. Allan Original Message Mr. [AHJ], I have done some research as followup to our discussion last week about battery venting for the [X] job. Here are several perspectives on the issue: The NEC Section 480.9(A) states only that Provisions shall be made for sufficient diffusion and ventilation of the gases from the battery to prevent the accumulation of an explosive mixture. At root, you are questioning whether ventilation of the batteries into the storeroom at the [X] home is sufficient under worst-case conditions. The NEC Handbook entries for Section 480.9(A), which are considered as explanatory support documentation and are not Code requirements, include two paragraphs that are fundamentally contradictory to each other. The two read: The intent of 480.9(A) is not to mandate mechanical ventilation. Hydrogen disperses rapidly and requires little air movement to prevent accumulation. Unrestricted natural air movement in the vicinity of the battery, together with normal air changes for occupied spaces or heat removal, normally is sufficient. If the space is confined, mechanical ventilation may be required in the vicinity of the battery. This paragraph refers to batteries in general, including flooded batteries which release hydrogen gas as a normal part of the charging process. The Handbook section goes on to specifically identify sealed batteries as being unlikely to release explosive gases: Although valve-regulated batteries are often referred to as sealed, they actually emit very small quantities
Re: [RE-wrenches] 72-cell modules
Does anyone know where to still purchase Panasonic modules since Sunwize no longer carries them? Larry On Feb 3, 2014, at 2:28 PM, Kirk Herander k...@vtsolar.com wrote: Panasonics are longer available through Sunwize. That’s what my rep just told me. They had trouble selling them due to the higher cost. Kirk Herander VT Solar, LLC dba Vermont Solar Engineering NABCEPTM Certified Inaugural Certificant NYSERDA-eligible Installer VT RE Incentive Program Partner 802.863.1202 From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Tump Sent: Monday, February 03, 2014 11:43 AM To: al...@positiveenergysolar.com; RE-wrenches Subject: Re: [RE-wrenches] 72-cell modules contact me of list for contact at sunwize if you need to but thats where I got my replacements last month, On Feb 3, 2014, at 10:51 AM, Allan Sindelar wrote: Does anyone have a source for Panasonic modules, in other than pallet quantity? Allan Sindelar al...@positiveenergysolar.com NABCEP Certified PV Installation Professional NABCEP Certified Technical Sales Professional New Mexico EE98J Journeyman Electrician Founder, Positive Energy, Inc. A Certified B CorporationTM 3209 Richards Lane Santa Fe, New Mexico 87507 505 424-1112 office 780-2738 cell www.positiveenergysolar.com On 2/3/2014 4:28 AM, Tump wrote: The Sanyo/panasonic are a bit smaller, just need to reduce rail width drill holes but thats what I am doing. ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org t...@swnl.net www.SWNL.net Solarwinds Northernlights Serving Mid Coast Maine Northern California 207-832-7574 Cl. 610-517-8401 Blair TUMP May MAINE'S CHARTER NABCEPCertified PV Installer MAINE'S CHARTER Trace Xantrex Certified Dealer / Installer ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org