Re: [Repeater-Builder] Adding capacitors to lower electric bill

2010-08-23 Thread sbjohnston
WB6FLY wrote:

Actually, it's the other way around- sites with many linear power 
supplies
almost always have a worse power factor than those with switchers.

As I think about it more, I'm seeing that it depends on how the 
switching supplies are designed.  In general terms, cheapest supplies 
have power factors farthest from one.  Well-designed units (more 
expensive) would be closer to one.  So my earlier generalization wasn't 
really fair.

I wonder what will happen to our power systems as we add all these 
energy saving light bulbs with the absolute-minimum-parts-count 
switching supplies built-in?

WG8S wrote:

All electric utilities are concerned about electricity theft

If you are adjusting your power factor back towards 1, I cannot imagine 
it would be any form of theft.  It would be considered good practice!  
 From the standpoint of having many devices all connecting to the power 
lines, every load should be designed with a power factor close to one.

Steve

sbjohns...@aol.com
http://www.wd8das.net/

Radio is your best entertainment value.






Re: [Repeater-Builder] Adding capacitors to lower electric bill

2010-08-23 Thread Gordon Cooper
Another quirk.


  Sixty plus years ago in England, power factor  was not
the main concern.  Many of the domestic radio receivers
were transformerless and used half-wave rectification to
obtain D.C. for the tubes.  A consequence was a fair dose
of D.C. flowing in the street power mains.

Gordon  ZL1KL
Tauranga N.Z.



RE: [Repeater-Builder] Adding capacitors to lower electric bill

2010-08-22 Thread Eric Lemmon
Like a bad penny, this urban legend just keeps coming back.

Since a kWh meter, whether mechanical or electronic, measures only real
power, the addition of a capacitor- which adds capacitive reactance- cannot
affect real power.  A residential customer will never see a reduction in the
amount of real power measured by the meter after adding a capacitor.  That
said, some electronic meters can display and record reactive power and
energy- but that is not real power.

The same is not true for an industrial customer that has a large number of
motors.  A lightly-loaded induction motor will impose a low power factor on
the electrical supply system, which then must supply the reactive currents
when needed- even though those reactive currents are returned to the source
later in the cycle.  As a result, the utility must have larger substations
and heavier conductors to handle such loads.  To force industrial customers
to raise their power factors, utilities impose a penalty for low power
factors.  Most power utilities want their industrial customers to have PF
above 95%.  So, in this unique case, adding capacitance downstream of the
electric meter WILL reduce the power bill, but only because it reduces or
eliminates the low PF penalty and not because it affects the kWh consumed.

One of the reasons why this so-called energy saver sounds attractive is
because the average Joe Citizen may think that he can measure power in an AC
circuit by multiplying the voltage across the line by the current flowing
through the line.  That product is volt-amperes, not watts, and it will go
down when a capacitor is added- if the power factor is not unity.  The only
way to correctly measure real power in watts is to use an instrument that
incorporates a four-quadrant multiplier, which determines the instantaneous
product of volts and amperes throughout each sine wave cycle.  Although
commercial wattmeters can cost hundreds of dollars, there is at least one
device on the market, called the Kill-A-Watt which is marketed by several
vendors for less than $25.  I bought one of these devices, and was surprised
to discover that its power readings were within 5% of those displayed on my
digital wattmeter.

73, Eric Lemmon WB6FLY
  

-Original Message-
From: Repeater-Builder@yahoogroups.com
[mailto:repeater-buil...@yahoogroups.com] On Behalf Of Chuck Kelsey
Sent: Friday, August 20, 2010 6:00 PM
To: Repeater-Builder@yahoogroups.com
Subject: [Repeater-Builder] Adding capacitors to lower electric bill

  

A while back, maybe a year or two ago, there was a discussion on here where 
a list member had success adding a capacitor to his electric service which 
reduced his bill. It was debated for a while.

Anyway, I am wondering if the utility company ever came and replaced the 
spinning disk meters with electronic versions, and if so, what the outcome 
was.

Could the original poster respond either here or privately? I just today had

a similar discussion with another ham who tried essentially the same thing 
with no success - only his was a commercial model, so it cost him 
considerably more.

Chuck
WB2EDV 







Re: [Repeater-Builder] Adding capacitors to lower electric bill

2010-08-22 Thread Chuck Kelsey
Like a bad penny, this urban legend just keeps coming back. -- Eric 
Lemmon.

Yes, I agree. However, the post that I made (and started all of this again) 
didn't make claim as to whether the capacitor trick worked or didn't work. 
I feel that it has no impact, unless you are being billed for reactive 
demand, and most of us are not.

I was simply trying to seek out an individual whom I believe posted about 
this here, some time ago. He insisted that his electric bill at, I believe, 
three repeater sites as well as his house, dropped considerably when he 
added a fixed value capacitor across the line. Again, I had serious doubts 
at the time, but he was adamant about it. Anyway, my recent post was to 
follow up on this guy. What triggered it was the fact that I just ran into a 
ham who had purchased one of the commercially available energy savers and 
was questioning it's performance (he didn't think it worked). I asked him if 
the utility meter was electronic or whether it was one of the old spinning 
disk units, to which he said electronic. I had posed the question about 
altering the PF to an electrical engineer that I know. He gave me all the 
engineering basis like I'd expected, but then added an interesting comment. 
He was uncertain if a spinning disk meter would remain accurate if the PF 
was forced way out of specification - he left that hint of doubt. He then 
said that he was certain that the newer, electronic meters would record 
accurately regardless of the PF.

Now, the guy that was adamant about beating the system had indicated that 
in every one of his experiments the meter was the older spinning disk 
unit. I suspect that the utility company eventually came out and replaced 
the meters. The guy said that it made a big enough difference that the 
utility had contacted him about the drop in usage.

So, maybe the guy was jerking me (us) around, or maybe the utility installed 
new meters and the savings went poof, or maybe the guy is sitting in 
jail, not able to respond. And maybe it was on a different Yahoo group and 
I'm experiencing brain fade.

I certainly didn't intend to create all the hubbub. But I felt the need to 
jump back in and explain further.

Chuck
WB2EDV 



Re: [Repeater-Builder] Adding capacitors to lower electric bill

2010-08-22 Thread Larry Horlick
And if the capacitor trick did work, would this not be theft?

lh

On Sun, Aug 22, 2010 at 12:05 PM, Chuck Kelsey wb2...@roadrunner.comwrote:



 Like a bad penny, this urban legend just keeps coming back. -- Eric
 Lemmon.

 Yes, I agree. However, the post that I made (and started all of this again)

 didn't make claim as to whether the capacitor trick worked or didn't
 work.
 I feel that it has no impact, unless you are being billed for reactive
 demand, and most of us are not.

 I was simply trying to seek out an individual whom I believe posted about
 this here, some time ago. He insisted that his electric bill at, I believe,

 three repeater sites as well as his house, dropped considerably when he
 added a fixed value capacitor across the line. Again, I had serious doubts
 at the time, but he was adamant about it. Anyway, my recent post was to
 follow up on this guy. What triggered it was the fact that I just ran into
 a
 ham who had purchased one of the commercially available energy savers and

 was questioning it's performance (he didn't think it worked). I asked him
 if
 the utility meter was electronic or whether it was one of the old spinning
 disk units, to which he said electronic. I had posed the question about
 altering the PF to an electrical engineer that I know. He gave me all the
 engineering basis like I'd expected, but then added an interesting comment.

 He was uncertain if a spinning disk meter would remain accurate if the PF
 was forced way out of specification - he left that hint of doubt. He then
 said that he was certain that the newer, electronic meters would record
 accurately regardless of the PF.

 Now, the guy that was adamant about beating the system had indicated that

 in every one of his experiments the meter was the older spinning disk
 unit. I suspect that the utility company eventually came out and replaced
 the meters. The guy said that it made a big enough difference that the
 utility had contacted him about the drop in usage.

 So, maybe the guy was jerking me (us) around, or maybe the utility
 installed
 new meters and the savings went poof, or maybe the guy is sitting in
 jail, not able to respond. And maybe it was on a different Yahoo group and
 I'm experiencing brain fade.

 I certainly didn't intend to create all the hubbub. But I felt the need to
 jump back in and explain further.

 Chuck
 WB2EDV

  



RE: [Repeater-Builder] Adding capacitors to lower electric bill

2010-08-22 Thread Eric Lemmon
Larry,

No, it would not.  As has already been noted, adding capacitance to the line
does not affect kWh, which is the energy that does work and which you pay
for.  Indeed, if every customer on a grid were to achieve and maintain a
unity PF, the utility would benefit by being able to defer the purchase and
installation of capital equipment such as substations and uprated power
distribution networks.

The most obvious indicator that someone is stealing power is a sudden and
large drop in the meter readings when the occupancy of the premises has not
changed.  The utility's Fraud Investigation Unit will likely install a test
meter upstream on a pole or in a vault where the suspect customer cannot get
to it, and compare the two meters.  Power theft seldom goes undetected, and
the punishment is severe.

73, Eric Lemmon WB6FLY
 

-Original Message-
From: Repeater-Builder@yahoogroups.com
[mailto:repeater-buil...@yahoogroups.com] On Behalf Of Larry Horlick
Sent: Sunday, August 22, 2010 9:35 AM
To: Repeater-Builder@yahoogroups.com
Subject: Re: [Repeater-Builder] Adding capacitors to lower electric bill

  

And if the capacitor trick did work, would this not be theft?

lh

snip



Re: [Repeater-Builder] Adding capacitors to lower electric bill

2010-08-22 Thread Bill Smith
The answer is simple. The electric company refuses to provide service to that 
location. Or, installs a tamperproof cover over the meter, relocates the meter 
up on the pole, or installs a new electronic meter. They can also go by 
historical use data for that property and sue the customer for it.





From: Chuck Kelsey wb2...@roadrunner.com
To: Repeater-Builder@yahoogroups.com
Sent: Sun, August 22, 2010 12:11:38 PM
Subject: Re: [Repeater-Builder] Adding capacitors to lower electric bill

  Power theft seldom goes undetected,

I'll agree.

 and the punishment is severe.


Not always. I can cite where a customer drilled hole in electric meter glass 
to allow an object to be inserted to prevent disk from spinning. Case 
presented to district attorney. No prosecution. Same customer did same thing 
with water meter later on. Same result with district attorney - no 
prosecution.

Go figure.

Chuck
WB2EDV 







Yahoo! Groups Links



    http://docs.yahoo.com/info/terms/

Re: [Repeater-Builder] Adding capacitors to lower electric bill

2010-08-22 Thread Chuck Kelsey
Correct. That was the intended route should it happen again with said customer 
- terminate service. Period. After the electric incident, the water was already 
being estimated in favor of the utility because that account was showing as a 
stopped meter. Later discovered to be a tampered meter.

Chuck
WB2EDV


  - Original Message - 
  From: Bill Smith 
  To: Repeater-Builder@yahoogroups.com 
  Sent: Sunday, August 22, 2010 1:24 PM
  Subject: Re: [Repeater-Builder] Adding capacitors to lower electric bill





  The answer is simple. The electric company refuses to provide service to that 
location. Or, installs a tamperproof cover over the meter, relocates the meter 
up on the pole, or installs a new electronic meter. They can also go by 
historical use data for that property and sue the customer for it.




--


RE: [Repeater-Builder] Adding capacitors to lower electric bill

2010-08-22 Thread Eric Lemmon
Bill,

A customer who causes physical (read, easily detected by the meter reader)
damage to a meter is quite possibly deranged.  A tamperproof cover will not
deter some really creative power thieves who cut into the service conduit
upstream of the meter and tap into the wires- often to feed a very heavy
load such as an electrically-heated spa.  I have seen pictures of such
handiwork where the service mast was cut into at the attic level, so it
was not visible to the meter reader.  The thief was caught when the meter at
the transformer suddenly did not match the sum of the residential meters.

The denial of service is a last-ditch resort of any utility provider, since
the County Health Inspector can declare the house to be uninhabitable and
cause the residents to be evicted until service is restored and inspected.

73, Eric Lemmon WB6FLY
 

-Original Message-
From: Repeater-Builder@yahoogroups.com
[mailto:repeater-buil...@yahoogroups.com] On Behalf Of Bill Smith
Sent: Sunday, August 22, 2010 10:25 AM
To: Repeater-Builder@yahoogroups.com
Subject: Re: [Repeater-Builder] Adding capacitors to lower electric bill

  

The answer is simple. The electric company refuses to provide service to
that location. Or, installs a tamperproof cover over the meter, relocates
the meter up on the pole, or installs a new electronic meter. They can also
go by historical use data for that property and sue the customer for it.




From: Chuck Kelsey wb2...@roadrunner.com
To: Repeater-Builder@yahoogroups.com
Sent: Sun, August 22, 2010 12:11:38 PM
Subject: Re: [Repeater-Builder] Adding capacitors to lower electric bill

  Power theft seldom goes undetected,

I'll agree.

 and the punishment is severe.


Not always. I can cite where a customer drilled hole in electric meter glass

to allow an object to be inserted to prevent disk from spinning. Case 
presented to district attorney. No prosecution. Same customer did same thing

with water meter later on. Same result with district attorney - no 
prosecution.

Go figure.

Chuck
WB2EDV



Re: [Repeater-Builder] Adding capacitors to lower electric bill

2010-08-22 Thread Jim McLaughlin
Happens often from the small case to a large one...'Prosecutor Discretion'  
they choose which cases are prosecuted and which ones are not. Often for 
unexplained reasons or at least unexplained to me.

Jim-   WA9FPT

  - Original Message - 
  From: Chuck Kelsey 
  To: Repeater-Builder@yahoogroups.com 
  Sent: Sunday, August 22, 2010 12:11 PM
  Subject: Re: [Repeater-Builder] Adding capacitors to lower electric bill



   Power theft seldom goes undetected,

  I'll agree.

   and the punishment is severe.

  Not always. I can cite where a customer drilled hole in electric meter glass 
  to allow an object to be inserted to prevent disk from spinning. Case 
  presented to district attorney. No prosecution. Same customer did same thing 
  with water meter later on. Same result with district attorney - no 
  prosecution.

  Go figure.

  Chuck
  WB2EDV 



  

Re: [Repeater-Builder] Adding capacitors to lower electric bill

2010-08-21 Thread Bill Smith
The utility I used to work for did a lot of testing on the get free 
electricity devices over the years. None worked unless the customer had PF 
issues, even then, it didn't do much. That simple spinning disk electric meter 
is surprisingly accurate and hard to fool. 

Bill   




From: Chuck Kelsey wb2...@roadrunner.com
To: Repeater-Builder@yahoogroups.com
Sent: Fri, August 20, 2010 8:14:14 PM
Subject: Re: [Repeater-Builder] Adding capacitors to lower electric bill

That's my take, but someone on here insisted otherwise based on testing he 
had done. I spoke with an electrical engineer who said the same thing, but 
then he wondered out loud if it could be possible if the power factor was 
shifted to an extreme with a spinning disk meter. He opined that an 
electronic meter wouldn't be fooled. Of course shifting the PF to an 
extreme would be a basis for utility company action.

Chuck
WB2EDV


- Original Message - 
From: Gary Schafer gascha...@comcast.net
To: Repeater-Builder@yahoogroups.com
Sent: Friday, August 20, 2010 9:06 PM
Subject: RE: [Repeater-Builder] Adding capacitors to lower electric bill


 You won't see any difference. The electric meter reads true power not VA.

 73
 Gary  K4FMX

 -Original Message-
 From: Repeater-Builder@yahoogroups.com [mailto:Repeater-
 buil...@yahoogroups.com] On Behalf Of Chuck Kelsey
 Sent: Friday, August 20, 2010 8:00 PM
 To: Repeater-Builder@yahoogroups.com
 Subject: [Repeater-Builder] Adding capacitors to lower electric bill

 A while back, maybe a year or two ago, there was a discussion on here
 where
 a list member had success adding a capacitor to his electric service 
 which
 reduced his bill. It was debated for a while.

 Anyway, I am wondering if the utility company ever came and replaced the
 spinning disk meters with electronic versions, and if so, what the 
 outcome
 was.

 Could the original poster respond either here or privately? I just today
 had
 a similar discussion with another ham who tried essentially the same 
 thing
 with no success - only his was a commercial model, so it cost him
 considerably more.

 Chuck
 WB2EDV



 



 Yahoo! Groups Links






 



 Yahoo! Groups Links









No virus found in this incoming message.
Checked by AVG - www.avg.com
Version: 9.0.851 / Virus Database: 271.1.1/3084 - Release Date: 08/20/10 
14:35:00







Yahoo! Groups Links



    http://docs.yahoo.com/info/terms/

Re: [Repeater-Builder] Adding capacitors to lower electric bill

2010-08-21 Thread Bon Hal
This is a reply to the power issue from a friend of mine:

Yes, it's true.
Heavy industry uses this technique to reduce their electrical utility costs.  
Steel production is an example.
Some utility companies require that customers with large inductive loads use 
and pay for capacitor banks to correct the plant's power factor.

The issue arises when large inductive loads are connected to the electrical 
grid.
For example, a large horsepower electric motor presents two loads to the grid.
One load is the energy consumed or dissipated in work.
The other load is inductive.  The inductive load stores electrical energy, does 
not dissipate it, and it is returned to the grid.

It can't be helped.  It is built into the design of electric motors.  This is 
understandable.  We understand that practical electric motor armatures are 
turned by a strong magnetic field.  That magnetic field is produced by large 
inductors.

As an electrical circuit, you can visualize the motor as a resistor in series 
with an inductor driven by a sine wave 60 Hz alternating voltage source (AC).

On the positive half cycle voltage swing (0-180 degrees), electrical energy is 
dissipated in the load, the resistor.  In the resistor the energy is dissipated 
in heat.  In a motor, the energy is dissipated in work done.

The inductor stores electrical energy on the positive half cycle then returns 
the energy to the grid on the negative half cycle (180-360 degrees).  The 
resistor again  draws and dissipates energy on the negative half cycle.

In the electrical circuit analogy, if the inductor was zero Henrys and the 
Resistor was non zero Ohms, the Power Factor  (PF) is  defined as 1.0, or 
unity.  This is a purely dissipative load.

If the inductor was non zero Henrys and the Resistor was zero Ohms, the PF is 
defined as 0.0.  This is a purely inductive load.

In a practical circuit with some inductance, L,  and some resistance, R, PF 
therefore varies between 0.0 and 1.0.
For given values of L and R,  PF can be measured or computed.

The utility company sells the energy dissipated in a load.  If PF = 1.0, the 
utility company sells all the energy it supplies.
As PF decreases due to inductance, the load increasingly stores and returns 
larger amounts of energy to the utility company.

The utility has to generate the additional power needed to charge the connected 
inductive loads, even if the energy is returned to the grid.  The utility needs 
significantly more capacity and therefore greater investment and operating 
capital.

Worse yet, the increased current flow causes more dissipative energy loss in 
the line resistance.  This inefficiency is a measurable loss of money to the 
utility. 

Adding capacitance across and close to the load helps a lot.
Briefly and simply, it works like this.

The utility initially charges the capacitor.  Then, when the inductive load 
draws current, the capacitor supplies it.  When the inductor dumps its stored 
energy, the capacitor takes it and recharges.  AC cycle after cycle the 
capacitor and inductor exchange stored energy.   The utility company does not 
have to generate the additional energy.  The load continues to dissipate energy 
on each half cycle, no change there. 

This is called Power Factor Correction.  With PF correction, the utility 
supplies mostly dissipative energy and sees a PF approximately = 1.0.
With the capacitance located close to the load, excessive line energy loss is 
eliminated too.
You might have seen these capacitor banks on a utility pole outside a factory.

Entrepreneurs have applied this industrial technology to the home.
You can buy a franchise and sell PF correction as a retail consumer product.
The franchise provides all the equipment and marketing materials.
I have seen a franchise website with convincing evidence of a decrease in a 
utility bill.

The utility company has to supply the electrical energy a home draws, whether 
the homeowner uses it all or not.
The idea is that PF correction can reduce the load to nearly pure dissipation, 
reducing a homeowners utility bill.

So, the technology works.  Is is cost effective?  It is for a large industrial 
load.
Home installation requires labor of a licensed electrician, a capacitor bank, 
and wiring.
This sounds expensive.  Maybe it will pay off over a long period.
It depends on how inductive a load your home presents.

To me, there is a larger picture.  We are in an era of energy conservation.  PF 
correction for the home sounds to me like a stimulus for increased electrical 
energy consumption.  PF correction controls your cost of increased consumption. 
 A homeowner might install a bigger air conditioner, put an additional 
refrigerator in the basement or garage.  Motors and transformers are inductive 
loads, presumably having some impact on PF.

California has asked people to unplug the extra refrigerators in garages to 
conserve energy.
Now the Energy Police are after us about Vampire Power - all those small 

RE: [Repeater-Builder] Adding capacitors to lower electric bill

2010-08-21 Thread Gary Schafer
The guy did ok on the first part explaining how power factor works but fell
down when it comes to the save money part.

The utilities do not charge you extra or give you a break if you do or don't
have any power factor correction. Unless you are an industrial customer.

 

I have seen demonstrations at shows where the guy trying to sell consumers
power factor correction devices had a motor and an ammeter showing current
draw. He then switches in a capacitor and shows you how the current drops
and shows you how volts times amps reduces the wattage used.  Only problem
is the electric meter doesn't care what the power factor is! So the utility
will bill you the same amount if you use power factor correction or not in
your home.

 

The other thing involved if you are going to do power factor correction is
that it needs to be done on EACH motor or inductive device. If you just hang
a capacitor across the main power line of the proper size when all motors
are running it will correct that. But when a motor or other inductive device
is shut down and the capacitor is still across the line, now it will have a
capacitive load rather than an inductive load. Same problem; capacitive
current that is out  of phase. 

You can hook a large AC capacitor across your power line and measure the
current thru it. It may look like you are drawing a lot of power thru it but
the meter will not see it. Yes it cost the utility more to generate that
extra current whether it be capacitive or inductive but you don't pay for
it. If the utility was really worried about it they would give incentives
for high power factor equipment or they would bill you like they do in
industry. We are small potatoes to them.

 

Trying to sell power factor correction to home owners and small business' is
a scam. You save nothing on your bill!

73

Gary  K4FMX

 

 

 

  _  

From: Repeater-Builder@yahoogroups.com
[mailto:repeater-buil...@yahoogroups.com] On Behalf Of Bon  Hal
Sent: Saturday, August 21, 2010 2:39 PM
To: Repeater-Builder@yahoogroups.com
Subject: Re: [Repeater-Builder] Adding capacitors to lower electric bill

 






This is a reply to the power issue from a friend of mine:

 

Yes, it's true.

Heavy industry uses this technique to reduce their electrical utility costs.
Steel production is an example.

Some utility companies require that customers with large inductive loads use
and pay for capacitor banks to correct the plant's power factor.

 

The issue arises when large inductive loads are connected to the electrical
grid.

For example, a large horsepower electric motor presents two loads to the
grid.

One load is the energy consumed or dissipated in work.

The other load is inductive.  The inductive load stores electrical energy,
does not dissipate it, and it is returned to the grid.

 

It can't be helped.  It is built into the design of electric motors.  This
is understandable.  We understand that practical electric motor armatures
are turned by a strong magnetic field.  That magnetic field is produced by
large inductors.

 

As an electrical circuit, you can visualize the motor as a resistor in
series with an inductor driven by a sine wave 60 Hz alternating voltage
source (AC).

 

On the positive half cycle voltage swing (0-180 degrees), electrical energy
is dissipated in the load, the resistor.  In the resistor the energy is
dissipated in heat.  In a motor, the energy is dissipated in work done.

 

The inductor stores electrical energy on the positive half cycle then
returns the energy to the grid on the negative half cycle (180-360 degrees).
The resistor again  draws and dissipates energy on the negative half cycle.

 

In the electrical circuit analogy, if the inductor was zero Henrys and the
Resistor was non zero Ohms, the Power Factor  (PF) is  defined as 1.0, or
unity.  This is a purely dissipative load.

 

If the inductor was non zero Henrys and the Resistor was zero Ohms, the PF
is defined as 0.0.  This is a purely inductive load.

 

In a practical circuit with some inductance, L,  and some resistance, R, PF
therefore varies between 0.0 and 1.0.

For given values of L and R,  PF can be measured or computed.

 

The utility company sells the energy dissipated in a load.  If PF = 1.0, the
utility company sells all the energy it supplies.

As PF decreases due to inductance, the load increasingly stores and returns
larger amounts of energy to the utility company.

 

The utility has to generate the additional power needed to charge the
connected inductive loads, even if the energy is returned to the grid.  The
utility needs significantly more capacity and therefore greater investment
and operating capital.

 

Worse yet, the increased current flow causes more dissipative energy loss in
the line resistance.  This inefficiency is a measurable loss of money to the
utility. 

 

Adding capacitance across and close to the load helps a lot.

Briefly and simply, it works like this.

 

The utility initially charges

Re: [Repeater-Builder] Adding capacitors to lower electric bill

2010-08-21 Thread Chuck Kelsey
Guess I should have done a message archive search. I didn't mean to start all 
this.

Chuck
WB2EDV

  - Original Message - 
  From: Gary Schafer 
  To: Repeater-Builder@yahoogroups.com 
  Sent: Saturday, August 21, 2010 5:17 PM
  Subject: RE: [Repeater-Builder] Adding capacitors to lower electric bill





  The guy did ok on the first part explaining how power factor works but fell 
down when it comes to the save money part.

  The utilities do not charge you extra or give you a break if you do or don't 
have any power factor correction. Unless you are an industrial customer.

   

  I have seen demonstrations at shows where the guy trying to sell consumers 
power factor correction devices had a motor and an ammeter showing current 
draw. He then switches in a capacitor and shows you how the current drops and 
shows you how volts times amps reduces the wattage used.  Only problem is the 
electric meter doesn't care what the power factor is! So the utility will bill 
you the same amount if you use power factor correction or not in your home.

   

  The other thing involved if you are going to do power factor correction is 
that it needs to be done on EACH motor or inductive device. If you just hang a 
capacitor across the main power line of the proper size when all motors are 
running it will correct that. But when a motor or other inductive device is 
shut down and the capacitor is still across the line, now it will have a 
capacitive load rather than an inductive load. Same problem; capacitive current 
that is out  of phase. 

  You can hook a large AC capacitor across your power line and measure the 
current thru it. It may look like you are drawing a lot of power thru it but 
the meter will not see it. Yes it cost the utility more to generate that extra 
current whether it be capacitive or inductive but you don't pay for it. If the 
utility was really worried about it they would give incentives for high power 
factor equipment or they would bill you like they do in industry. We are small 
potatoes to them.

   

  Trying to sell power factor correction to home owners and small business' is 
a scam. You save nothing on your bill!

  73

  Gary  K4FMX


Re: [Repeater-Builder] Adding capacitors to lower electric bill

2010-08-21 Thread Chuck Kelsey
Well, I tried a search and came up empty. Maybe it was another group. Oh well.

Chuck
WB2EDV




  - Original Message - 
  From: Chuck Kelsey 
  To: Repeater-Builder@yahoogroups.com 
  Sent: Saturday, August 21, 2010 9:24 PM
  Subject: Re: [Repeater-Builder] Adding capacitors to lower electric bill





  Guess I should have done a message archive search. I didn't mean to start all 
this.

  Chuck
  WB2EDV

- Original Message - 
From: Gary Schafer 
To: Repeater-Builder@yahoogroups.com 
Sent: Saturday, August 21, 2010 5:17 PM
Subject: RE: [Repeater-Builder] Adding capacitors to lower electric bill


The guy did ok on the first part explaining how power factor works but fell 
down when it comes to the save money part.

The utilities do not charge you extra or give you a break if you do or 
don't have any power factor correction. Unless you are an industrial customer.

 SNIP


RE: [Repeater-Builder] Adding capacitors to lower electric bill

2010-08-20 Thread Gary Schafer
You won't see any difference. The electric meter reads true power not VA.

73
Gary  K4FMX

 -Original Message-
 From: Repeater-Builder@yahoogroups.com [mailto:Repeater-
 buil...@yahoogroups.com] On Behalf Of Chuck Kelsey
 Sent: Friday, August 20, 2010 8:00 PM
 To: Repeater-Builder@yahoogroups.com
 Subject: [Repeater-Builder] Adding capacitors to lower electric bill
 
 A while back, maybe a year or two ago, there was a discussion on here
 where
 a list member had success adding a capacitor to his electric service which
 reduced his bill. It was debated for a while.
 
 Anyway, I am wondering if the utility company ever came and replaced the
 spinning disk meters with electronic versions, and if so, what the outcome
 was.
 
 Could the original poster respond either here or privately? I just today
 had
 a similar discussion with another ham who tried essentially the same thing
 with no success - only his was a commercial model, so it cost him
 considerably more.
 
 Chuck
 WB2EDV
 
 
 
 
 
 
 
 Yahoo! Groups Links
 
 
 



Re: [Repeater-Builder] Adding capacitors to lower electric bill

2010-08-20 Thread Chuck Kelsey
That's my take, but someone on here insisted otherwise based on testing he 
had done. I spoke with an electrical engineer who said the same thing, but 
then he wondered out loud if it could be possible if the power factor was 
shifted to an extreme with a spinning disk meter. He opined that an 
electronic meter wouldn't be fooled. Of course shifting the PF to an 
extreme would be a basis for utility company action.

Chuck
WB2EDV


- Original Message - 
From: Gary Schafer gascha...@comcast.net
To: Repeater-Builder@yahoogroups.com
Sent: Friday, August 20, 2010 9:06 PM
Subject: RE: [Repeater-Builder] Adding capacitors to lower electric bill


 You won't see any difference. The electric meter reads true power not VA.

 73
 Gary  K4FMX

 -Original Message-
 From: Repeater-Builder@yahoogroups.com [mailto:Repeater-
 buil...@yahoogroups.com] On Behalf Of Chuck Kelsey
 Sent: Friday, August 20, 2010 8:00 PM
 To: Repeater-Builder@yahoogroups.com
 Subject: [Repeater-Builder] Adding capacitors to lower electric bill

 A while back, maybe a year or two ago, there was a discussion on here
 where
 a list member had success adding a capacitor to his electric service 
 which
 reduced his bill. It was debated for a while.

 Anyway, I am wondering if the utility company ever came and replaced the
 spinning disk meters with electronic versions, and if so, what the 
 outcome
 was.

 Could the original poster respond either here or privately? I just today
 had
 a similar discussion with another ham who tried essentially the same 
 thing
 with no success - only his was a commercial model, so it cost him
 considerably more.

 Chuck
 WB2EDV



 



 Yahoo! Groups Links






 



 Yahoo! Groups Links









No virus found in this incoming message.
Checked by AVG - www.avg.com
Version: 9.0.851 / Virus Database: 271.1.1/3084 - Release Date: 08/20/10 
14:35:00



Re: [Repeater-Builder] Adding capacitors to lower electric bill

2010-08-20 Thread Paul Plack
One company supplying power factor correction capacitors promotes their use on 
inductive loads only, where it might be a legitimate claim:

http://www.greenenergycube.com/index.php?support-documentation

73,

Paul, AE4KR

  - Original Message - 
  From: Chuck Kelsey 
  To: Repeater-Builder@yahoogroups.com 
  Sent: Friday, August 20, 2010 7:00 PM
  Subject: [Repeater-Builder] Adding capacitors to lower electric bill



  A while back, maybe a year or two ago, there was a discussion on here where 
  a list member had success adding a capacitor to his electric service which 
  reduced his bill. It was debated for a while.
  ...


RE: [Repeater-Builder] Adding capacitors to lower electric bill

2010-08-20 Thread Gary
True power (W or KW) is increased by poor PF and high apparent power (VA or
KVA). The resulting increase in current demand raises the true power but the
extra current is usually lost as heat instead of performing work. The bigger
problem (bigger than an inflated utility bill) is the potential for fire
from drawing too much current through a branch circuit that can't handle the
highly reactive load that's been connected to it. Also beware of cyclical
reactive loads on panels that also feed electronics. I recently troubleshot
a commercial 3 phase panelboard feeding both UPS's and across-the-line HVAC
gear (a bad combination). The UPS's were failing and the owner didn't know
why. A quick power quality analysis showed it was due to excessive UPS
transfers caused by the HVAC cycling during the daytime and causing the
UPS's to see voltage dips. Average PF was .67 when we started, .91 when we
moved the HVAC away from the panel and did some load balancing. 
Gary
N6LRV

-Original Message-
From: Repeater-Builder@yahoogroups.com
[mailto:repeater-buil...@yahoogroups.com] On Behalf Of Chuck Kelsey
Sent: Friday, August 20, 2010 6:14 PM
To: Repeater-Builder@yahoogroups.com
Subject: Re: [Repeater-Builder] Adding capacitors to lower electric bill

That's my take, but someone on here insisted otherwise based on testing he 
had done. I spoke with an electrical engineer who said the same thing, but 
then he wondered out loud if it could be possible if the power factor was 
shifted to an extreme with a spinning disk meter. He opined that an 
electronic meter wouldn't be fooled. Of course shifting the PF to an 
extreme would be a basis for utility company action.

Chuck
WB2EDV


- Original Message - 
From: Gary Schafer gascha...@comcast.net
To: Repeater-Builder@yahoogroups.com
Sent: Friday, August 20, 2010 9:06 PM
Subject: RE: [Repeater-Builder] Adding capacitors to lower electric bill


 You won't see any difference. The electric meter reads true power not VA.

 73
 Gary  K4FMX

 -Original Message-
 From: Repeater-Builder@yahoogroups.com [mailto:Repeater-
 buil...@yahoogroups.com] On Behalf Of Chuck Kelsey
 Sent: Friday, August 20, 2010 8:00 PM
 To: Repeater-Builder@yahoogroups.com
 Subject: [Repeater-Builder] Adding capacitors to lower electric bill

 A while back, maybe a year or two ago, there was a discussion on here
 where
 a list member had success adding a capacitor to his electric service 
 which
 reduced his bill. It was debated for a while.

 Anyway, I am wondering if the utility company ever came and replaced the
 spinning disk meters with electronic versions, and if so, what the 
 outcome
 was.

 Could the original poster respond either here or privately? I just today
 had
 a similar discussion with another ham who tried essentially the same 
 thing
 with no success - only his was a commercial model, so it cost him
 considerably more.

 Chuck
 WB2EDV



 



 Yahoo! Groups Links






 



 Yahoo! Groups Links










No virus found in this incoming message.
Checked by AVG - www.avg.com
Version: 9.0.851 / Virus Database: 271.1.1/3084 - Release Date: 08/20/10 
14:35:00







Yahoo! Groups Links





Re: [Repeater-Builder] Adding capacitors to lower electric bill

2010-08-20 Thread Bon Hal
Bill:  

Check this out.  Is It possible that  the device might actually reduce 
electrical usage?

Hal
  - Original Message - 
  From: Paul Plack 
  To: Repeater-Builder@yahoogroups.com 
  Sent: Friday, August 20, 2010 9:27 PM
  Subject: Re: [Repeater-Builder] Adding capacitors to lower electric bill




  One company supplying power factor correction capacitors promotes their use 
on inductive loads only, where it might be a legitimate claim:

  http://www.greenenergycube.com/index.php?support-documentation

  73,

  Paul, AE4KR

- Original Message - 
From: Chuck Kelsey 
To: Repeater-Builder@yahoogroups.com 
Sent: Friday, August 20, 2010 7:00 PM
Subject: [Repeater-Builder] Adding capacitors to lower electric bill


  
A while back, maybe a year or two ago, there was a discussion on here where 
a list member had success adding a capacitor to his electric service which 
reduced his bill. It was debated for a while.
...