Re: [Slony1-general] Swapping Providers

2012-06-25 Thread Raghav


 Using streaming replication for the DR Master could present a problem.
 Since it is in the same data center the following may seem unlikely. But
 what can happen is that the DR Master is further behind in replication than
 the Slony Slave at the moment, disaster strikes and the Master becomes
 unavailable. We never know ahead what will cause the Master to go down and
 how fast it will be.


What if the death is affecting the network interface of Master first. At
 first it is just losing a few packets and some of them are packets from the
 WAL sender to the DR Master. It will take several seconds for the TCP/IP
 protocol to detect that and retransmit. Time enough for several more
 transactions to commit and Slony to replicate them. And before the DR
 Master can catch up, the motherboard finally fails with a puff of smoke.

 What will happen with your below steps in this situation is that the Slave
 has some changes, that the DR Master doesn't have. The DR Master (now
 Master) will generate new SYNC events and the first (few) will have the
 same event number as ones, that the Slave had replicated from the old
 Master. They will be ignored by the Slave. So at the end the DR Master will
 be missing some changes made to the old Master and the Slave will be
 missing other changes that had been made against the DR Master.


Great Analysis Jan... I thought all of those what you mentioned. All you
mentioned are very true.
But, Thumb rule of all the thoughts is that, Master should be on top in
Events numbering, Slave events should be always lower. For example if
Master current events are in sequence of say '500023', then slave
should be  500023. If your Slave events tops the Master Event Seq
number, then all your efforts go waste, even after promoting DR-Master as
master.

I sticked to this rule only as Steve mentioned. I tried to maintain my
DR-Master (Streaming Replication) to be topper in Events and did not allow
Slave to cross master event number.

Simple test case would be, create master/slave/dr_master on one port with
the rule I mentioned above.

1. Setup replication with two databases master/slave with one table
replication and maintain SYNC.
2. Now Stop Slon on master  slave.
3. Here, assume we are promoting DR-master as Master. So,create new
database as dr-master with template=master on same port, bcoz, its going to
be the same as Master with Events when you stopped Slony in Step 2.

4. Now change the sl_path with store path() function on DR-Master  Slave.
Since, now DR-master would be the provider.

dr_master=# select _myrep.storepath(1,2,'host=127.0.0.1 dbname=dr_master
user=postgres port=5432',10);
 storepath

 500021
(1 row)

On Slave

slave1=# select _myrep.storepath(1,2,'host=127.0.0.1 dbname=dr_master
user=postgres port=5432',10);
 storepath

 500012
(1 row)

See above, my Dr-Master events number is greater than slave.

5. Now start slon process for dr-master/slave and you should see syncs.

-bash-4.1$ psql -d dr_master -c select max(ev_seqno) from _myrep.sl_event;
max

 500025
(1 row)

-bash-4.1$ psql -d slave1 -c select max(ev_seqno) from _myrep.sl_event;
max

 500023
(1 row)

Here onwards any DML's work smoothly.

--Raghav
___
Slony1-general mailing list
Slony1-general@lists.slony.info
http://lists.slony.info/mailman/listinfo/slony1-general


[Slony1-general] Change encoding

2012-06-25 Thread Краев Стас
Hi all.

Can some one tell me plase - is it possible to use slony to change
database encoding, may be piping data via iconv somehow or relay on
server side encoding.
The whole idea is to convert big db from koi8 to utf8 with small
downtime. Slony looks flexible enough but is it really possible ?

Thanks

-- 
Краев С.А.
Системный администратор. Академсофт.

Stanislav A. Kraev
Unix admin at Academsoft
___
Slony1-general mailing list
Slony1-general@lists.slony.info
http://lists.slony.info/mailman/listinfo/slony1-general


Re: [Slony1-general] Swapping Providers

2012-06-25 Thread Jan Wieck
On 6/25/2012 3:36 AM, Raghav wrote:

 Using streaming replication for the DR Master could present a
 problem. Since it is in the same data center the following may seem
 unlikely. But what can happen is that the DR Master is further
 behind in replication than the Slony Slave at the moment, disaster
 strikes and the Master becomes unavailable. We never know ahead what
 will cause the Master to go down and how fast it will be.

 What if the death is affecting the network interface of Master
 first. At first it is just losing a few packets and some of them are
 packets from the WAL sender to the DR Master. It will take several
 seconds for the TCP/IP protocol to detect that and retransmit. Time
 enough for several more transactions to commit and Slony to
 replicate them. And before the DR Master can catch up, the
 motherboard finally fails with a puff of smoke.

 What will happen with your below steps in this situation is that the
 Slave has some changes, that the DR Master doesn't have. The DR
 Master (now Master) will generate new SYNC events and the first
 (few) will have the same event number as ones, that the Slave had
 replicated from the old Master. They will be ignored by the Slave.
 So at the end the DR Master will be missing some changes made to the
 old Master and the Slave will be missing other changes that had been
 made against the DR Master.


 Great Analysis Jan... I thought all of those what you mentioned. All you
 mentioned are very true.
 But, Thumb rule of all the thoughts is that, Master should be on top in
 Events numbering, Slave events should be always lower. For example if
 Master current events are in sequence of say '500023', then slave
 should be  500023. If your Slave events tops the Master Event Seq
 number, then all your efforts go waste, even after promoting DR-Master
 as master.

 I sticked to this rule only as Steve mentioned. I tried to maintain my
 DR-Master (Streaming Replication) to be topper in Events and did not
 allow Slave to cross master event number.

 Simple test case would be, create master/slave/dr_master on one port
 with the rule I mentioned above.

 1. Setup replication with two databases master/slave with one table
 replication and maintain SYNC.
 2. Now Stop Slon on master  slave.
 3. Here, assume we are promoting DR-master as Master. So,create new
 database as dr-master with template=master on same port, bcoz, its going
 to be the same as Master with Events when you stopped Slony in Step 2.

 4. Now change the sl_path with store path() function on DR-Master 
 Slave. Since, now DR-master would be the provider.

 dr_master=# select _myrep.storepath(1,2,'host=127.0.0.1 dbname=dr_master
 user=postgres port=5432',10);
   storepath
 
   500021
 (1 row)

 On Slave

 slave1=# select _myrep.storepath(1,2,'host=127.0.0.1 dbname=dr_master
 user=postgres port=5432',10);
   storepath
 
   500012
 (1 row)

 See above, my Dr-Master events number is greater than slave.

This analysis is flawed. The two event numbers are from different 
origins and therefore, don't compare to each other. The combination of 
ev_origin,ev_seqno can never be higher on any node, than it is on the 
origin itself.

Your disaster recovery plan assumes, that streaming replication will 
ALLWAYS be faster than Slony replication. But that is only true for 
synchronous streaming replication. If you use asynchronous streaming 
replication, then one tiny network glitch and your DR-master will be 
several seconds behind while the Slony replica may be not. If the master 
blows up in that moment, your plan fails.

To simulate this problem, Steve and I were pointing out, do the following:

1. Create your setup as before.
2. Stop the streaming replication (simulating the network communication 
problem)
3. Update a row on the master and wait for the SYNC to replicate.
4. Stop the slon processes. DO NOT let the streaming replica catch up 
with the now DEAD master. Assume the master and all its data, including 
WAL, have become unavailable.
5. Promote DR-master and do the two store path commands.
6. Start slon processes.
7. Update another row on the new master.
8. Compare table content on master and slave.

You can detect the problem before step 5 by comparing the ev_seqno with 
ev_origin=old-master on the DR-master and slave. Whichever is higher 
should be promoted to master. In the unlikely case that it is the Slony 
slave, you will have to rebuild the DR-master from scratch, though.


Jan

-- 
Anyone who trades liberty for security deserves neither
liberty nor security. -- Benjamin Franklin


___
Slony1-general mailing list
Slony1-general@lists.slony.info
http://lists.slony.info/mailman/listinfo/slony1-general


Re: [Slony1-general] Swapping Providers

2012-06-25 Thread Raghav

 This analysis is flawed. The two event numbers are from different origins
 and therefore, don't compare to each other. The combination of
 ev_origin,ev_seqno can never be higher on any node, than it is on the
 origin itself.

 Thanks Jan. For correcting me, let me recheck thoroughly from my side why
I concluded on the seqno.


 Your disaster recovery plan assumes, that streaming replication will
 ALLWAYS be faster than Slony replication. But that is only true for
 synchronous streaming replication. If you use asynchronous streaming
 replication, then one tiny network glitch and your DR-master will be
 several seconds behind while the Slony replica may be not. If the master
 blows up in that moment, your plan fails.

 Yes, very much true and completely agreed. Aim is to not to have any lag
between Master  DR-Master.
As you said, in any case if Master  DR-Master are not in Sync due to
network or any lag then my whole plan collapses. So, I made my goal clear
here, that I need to STOP slony between Master  Slave long before
promoting DR-master as Master, to make sure nothing is left on Master to
update on DR-master.


 To simulate this problem, Steve and I were pointing out, do the following:

 1. Create your setup as before.
 2. Stop the streaming replication (simulating the network communication
 problem)
 3. Update a row on the master and wait for the SYNC to replicate.
 4. Stop the slon processes. DO NOT let the streaming replica catch up with
 the now DEAD master. Assume the master and all its data, including WAL,
 have become unavailable.
 5. Promote DR-master and do the two store path commands.
 6. Start slon processes.
 7. Update another row on the new master.
 8. Compare table content on master and slave.

 You can detect the problem before step 5 by comparing the ev_seqno with
 ev_origin=old-master on the DR-master and slave. Whichever is higher should
 be promoted to master. In the unlikely case that it is the Slony slave, you
 will have to rebuild the DR-master from scratch, though.


Exactly, these are the steps I followed and succeded, as pointed I never
simulated Step 2,3 in my testing, because If MASTER and newly promoted
DR-Master are not same in any case then the success is nowhere near by
surroundings :) .

I will surely retake the test with the steps mentioned on my two VM's and
update my finding.

Once again, Thank you very much to you  Steve for helping me in this
scenario.

--
Regards
Raghav
Blog: htt://raghavt.blogspot.com/
___
Slony1-general mailing list
Slony1-general@lists.slony.info
http://lists.slony.info/mailman/listinfo/slony1-general


Re: [Slony1-general] Swapping Providers

2012-06-25 Thread Raghav
Also, one more point on step 3, there cannot be any DML's until this
operation is done successfully, because, in step 2 you are stopping SR and
doing DML's on Step 3, which is clearly know fact that your DR-master dont
have any effect made in Step 3.

--Raghav