RE: Connoisseur

2000-05-03 Thread Amoudi, Ahmad O
In one of our refineries, we installed Connoisseut on a separate stand alone PC . The spec's for this PC is 256 MB memory , PIII 600 MHZ . The communication between the AW50 and the PC is via a communication bridge that was provided by the FOXBORO company . The software when linked to the DCS

RE: save_all.sh update information

2000-05-03 Thread Deen, Ron
Well Stan, fixed it yet??? Just kidding. When I have the time (this is not likely to happen within a few days though) I will look into it over here. We do not have a Spectrum Interface Proccessor (Is this the Spectrum Slave Gateway??) running in the Lab right now. Ron Deen Foxboro Nederland

Disable on GDEV

2000-05-03 Thread Stef Smeur
Hi everyone out there, I have experienced a problem with the GDEV-block: When a GDEV, that is already in stoped/closed status, is disabled it gives for one cycle an error. Has anyone else experienced this before and is there anyone who knows a way of preventing the block going in alarm?

RE: External Horn For Process Alarms

2000-05-03 Thread marci . sewell
Alex- Thanks for the info on the CAG - I definitely misunderstood its use. Manufacturing installed a system that can broadcast voice messages through the building and they want to use it to tell the operators exactly what is in alarm. The system can take a large number of digital inputs (a DO

Re: Integrator 30's vs. AB Stations

2000-05-03 Thread Kevin FitzGerrell
Stan, We are using 6 AB Stations rather than Integrator 30s at my plant. I don't have a basis for comparison, but I can certainly tell you a little about our AB Stations. The main reason to go with these for us was to keep setup fairly simple -- setup and continuing work on the stations is

RE: External Horn For Process Alarms

2000-05-03 Thread Johnson,Alex
You could buy our Event Driven Scripts product. This product receives I/A Series Alarm Messages and applies a filter to the message. If the message passes the filter, a user specified script is run. Thus, you could have a filter line for each alarm or alarm group (the filtering is pretty

RE: FoxDraw Classic historian

2000-05-03 Thread Johnson,Alex
FV may be used with the I/A Series Historian or AIM*Historian. The DM may be used with the I/A Series Historian or AIM*Historian. You may run both FV and DM on the same box at the same time. Regards, Alex Johnson The Foxboro Company 10707 Haddington Houston, TX 77043 713.722.2859 (v)

RE: Integrator 30's vs. AB Stations

2000-05-03 Thread Jones, Charles R. (Chuck)
You have really opened up a can of worms here, Stan. We use Integrator 30s at our plant. They cause a lot of pain in both set up and operator usage. The work is done in the PLC 5s and the I/A is used for operator interface. The Basic Processing Cycle of the AB Gateways is 2 seconds. Our

RE: Re: Scripts to backup CP database and CSA to an alternate sta tion

2000-05-03 Thread Murray, Steve
Hi Ron, I have looked at the OFHA several times and never decided to implement it. I would like to get a copy of your .pdf document if you can send it to me. Thanks in advance, Stephen Murray Asarco [EMAIL PROTECTED] -Original Message- From: Deen, Ron [mailto:[EMAIL

Re: Integrator 30's vs. AB Stations

2000-05-03 Thread Stan Brown
On Wed May 3 11:21:27 2000 Jones, Charles R. (Chuck) wrote... You have really opened up a can of worms here, Stan. We use Integrator 30s at our plant. They cause a lot of pain in both set up and operator usage. The work is done in the PLC 5s and the I/A is used for operator interface. The

Re: FoxDraw Classic historian

2000-05-03 Thread Stan Brown
On Wed May 3 10:35:48 2000 Johnson,Alex wrote... FV may be used with the I/A Series Historian or AIM*Historian. The DM may be used with the I/A Series Historian or AIM*Historian. You may run both FV and DM on the same box at the same time. Thanks, interesting I never thought of

Re: Bcalci and switch blocks

2000-05-03 Thread Kevin Fitzgerrell
Cyrus, I'm glad you got the system working. I checked my SELECT page display and mine does not show a BCALCO parameter, just the BCALCI, BCALC1 and BCALC2 parameters. I am using version 4.3, which version are you on? Regarding SELECT page display problems I just submitted a CAR last week

Re: Integrator 30's vs. AB Stations

2000-05-03 Thread Stan Brown
On Wed May 3 10:33:39 2000 Johnson,Alex wrote... To integrate AB PLCs, we have the following options: ABI30s - Serial I/F to ABDH, slowest option, optionally FT. No PLC Integration blocks. No PID family blocks. AB Station - PLC 5 only, better diagnostics, no redundancy, faster I/O interface,

Re: Integrator 30's vs. AB Stations

2000-05-03 Thread Stan Brown
On Wed May 3 10:07:33 2000 Kevin FitzGerrell wrote... Stan, We are using 6 AB Stations rather than Integrator 30s at my plant. I don't have a basis for comparison, but I can certainly tell you a little about our AB Stations. The main reason to go with these for us was to keep setup fairly

Re:RE: Re: Scripts to backup CP database and CSA to an alter

2000-05-03 Thread Neil_Martin
Would someone mind telling what OFHA is? Thanks, Neil Martin Reply Separator Subject:RE: Re: Scripts to backup CP database and CSA to an alternat Author: Murray; Steve [EMAIL PROTECTED] Date: 05/03/2000 8:57 AM Hi Ron, I have looked at the

RE: Integrator 30's vs. AB Stations

2000-05-03 Thread Johnson,Alex
I'll try to clarify. As you know all computers are bound by CPU cycles, RAM, and I/O bandwidth. Generally, the DI30 is limited by I/O bandwidth. The limit is about 256 bytes per second (or 128 registers per second if you prefer). The AB-Station has DMA access to the I/O, i.e., it reads the

RE: RE: Re: Scripts to backup CP database and CSA to an alter

2000-05-03 Thread Dusing, Lance D.
Here is the last response to that question. Lance -Original Message- From: James Kahlden [SMTP:[EMAIL PROTECTED]] Sent: Monday, May 01, 2000 12:17 PM To: [EMAIL PROTECTED] Subject: Re:RE: Re: Scripts to backup CP database and CSA to an alter Neil, OFHA is Foxboro's

RE: Integrator 30's vs. AB Stations

2000-05-03 Thread Johnson,Alex
Re: Are you saying that all points in teh Inegrator 30 must run at the same BPC? I can't have some at say 0.5 sec, and others at say 2 sec.? Stan, don't confuse BPC with Block Period. The BPC (Basic Processing Cycle) is fixed at system configuration for a particular station. It is the fastest

RE: Integrator 30s vs. AB Stations

2000-05-03 Thread Johnson,Alex
Re: CP40 based AB Station that would let us take our block periods back to 0.5 sec FYI: The hardware is AB hardware. We don't manufacture it; we put software on their hardware. In that regard, the AB-Station is similar to what Honeywell does with ControlLogix (sp?) when they create ProcessLogix

FW: RE: Re: Scripts to backup CP database and CSA to an alter

2000-05-03 Thread Dusing, Lance D.
Here is the last response to that question. Lance -Original Message- From: James Kahlden [SMTP:[EMAIL PROTECTED]] Sent: Monday, May 01, 2000 12:17 PM To: [EMAIL PROTECTED] Subject: Re:RE: Re: Scripts to backup CP database and CSA to an alter Neil, OFHA is Foxboro's

Re: Integrator 30s vs. AB Stations

2000-05-03 Thread Stan Brown
On Wed May 3 12:45:29 2000 Kevin Fitzgerrell wrote... Stan, Regarding loading on AB Stations, you can run a 0.5 sec BPC with the same type of issues you see on a CP30 - although the AB Station will support 1000 block equivalents, you can only use about 100 blocks if you want them all running

Re: Integrator 30s vs. AB Stations

2000-05-03 Thread Kevin Fitzgerrell
On Wed, 3 May 2000 12:27:36 -0400 (EDT) Stan Brown wrote... Stan, We are using 6 AB Stations rather than Integrator 30s at my plant. I don't have a basis for comparison, but I can certainly tell you a little about our AB Stations. The main reason to go with these for us was to keep setup

Re: Integrator 30's vs. AB Stations

2000-05-03 Thread Stan Brown
On Wed May 3 13:14:19 2000 Johnson,Alex wrote... I'll try to clarify. Thanks for the nice concise summary. I geuss I am leaning in the direction of Integrator 30's at this point. Kind of a big diapointment, since I know the limts of them pretty well, and The

Re: Bcalci and switch blocks

2000-05-03 Thread Cyrus W. Taft
Message text written by Foxboro DCS Mail List I checked my SELECT page display and mine does not show a BCALCO parameter, just the BCALCI, BCALC1 and BCALC2 parameters. I am using version 4.3, which version are you on? Kevin, I'm at version 6.1. It sounds like they lost a fix when they went

Disappearing fields on xterminal

2000-05-03 Thread Kevin Fitzgerrell
Now that I have my xterminal in front of me I'll post in a little more detail here. In response to the question posed last night regarding fields disappearing on xterminals (similar to Exceed problems with Backing Store): If you have terminal controls enabled on your xterminals, you can select

RE: Process Alarms

2000-05-03 Thread Johnson,Alex
HH 714 from the CSC explains this I've included it for your reading pleasure. Don't say I never did anything for you. HH#: HH714 IA INFO: maf9506 File: Alarm History Release:

Simple print screen for all you GoGlobal users.

2000-05-03 Thread Schouten, Frits JF
Wouldn't you love to do a I/A printscreen from your PC running GoGlobal AND to your local PS printer too? Well, do I have the answer. Although, I have to admit, it is not entirely mine. But who cares, as long as it works The following scripts are tested and working for the old style DM but

RE: Integrator 30's vs. AB Stations

2000-05-03 Thread Johnson,Alex
Re: Realize that this is a Version 6.2 product and I was told there were not many (any) in the field for what it's worth. Micro I/A has been shipping for years on a number of version of the I/A Series. There are enhancements to the product due in 6.2.1, but I don't know what this comment

Re: Integrator 30s vs. AB Stations

2000-05-03 Thread Stan Brown
On Wed May 3 14:08:09 2000 Kevin Fitzgerrell wrote... Alex, You're right of course, thanks for the clarification. I should have said I'd like an upgrade to the AB Stations similar to what the CP40 gave us over CP30. And I still won't hold my breath waiting. As I recall from the Y2K

RE: Integrator 30's vs. AB Stations

2000-05-03 Thread timothy . ruhland
From: Timothy A. Ruhland Based on some exchanges I have had with Charlie Piper, I think the A-B PLC5E interface is brand new this year, still in beta, and will be released around the end of the second quarter (? best guess ?). Could that be it? Regards, Tim Ruhland Eastman Kodak Company --

NNTP address of list server

2000-05-03 Thread lorent
I am trying to set up a news account in outlook express to gain acces to the list server. Does anyone know the nntp server name or address to use? --- This list is neither sponsored nor endorsed by the Foxboro Company. All

RE: Integrator 30's vs. AB Stations

2000-05-03 Thread Johnson,Alex
The PSS exists. Beats me. Regards, Alex Johnson The Foxboro Company 10707 Haddington Houston, TX 77043 713.722.2859 (v) 713.722.2700 (sb) 713.932.0222 (f) [EMAIL PROTECTED] mailto:[EMAIL PROTECTED] -Original Message- From: [EMAIL PROTECTED] [SMTP:[EMAIL PROTECTED]]

RE: Process Alarms

2000-05-03 Thread Loupe, Rory
I can't seem to get these script to work. This script is the exactly like the script on http://www.csc.foxboro.com http://www.csc.foxboro.com . I can't seem to get either to work. Has anyone cleaned this script up? If so could you please post it? Thanks, Rory Loupe

Re: Re[2]: Integrator 30's vs. AB Stations

2000-05-03 Thread Stan Brown
On Wed May 3 17:51:03 2000 Daren Bishop wrote... Following this discussion, I have noted several things. 1. DH+ is basically, for all intents and purposes, Token Ring (56K). Through a 1770-KF2 CAM (modem) to RS232 Communications to the INT30 to the node. Bad loss of