[Nut-upsuser] (no subject)

2017-07-05 Thread Andrea de Lutti
2017-07-05 13:32 GMT+02:00 Charles Lepple <clep...@gmail.com>: > On Jul 5, 2017, at 7:05 AM, Andrea de Lutti <adelu...@gmail.com> wrote: > > > > Which are the ups.status I can use with ups in dummy mode? > > I have seen only OB, LB, OL... > > > T

Re: [Nut-upsuser] Help with Elite 800VA usb UPS

2017-07-05 Thread Andrea de Lutti
Thank you lots! Finally I have everything working! Which are the ups.status I can use with ups in dummy mode? I have seen only OB, LB, OL... thank you Andrea 2017-07-04 19:55 GMT+02:00 Charles Lepple <clep...@gmail.com>: > On Jul 3, 2017, at 11:06 AM, Andrea de Lutti <adelu...@gmai

Re: [Nut-upsuser] Help with Elite 800VA usb UPS

2017-07-03 Thread Andrea de Lutti
ccurs (on battery and so on). in chapter 4.2 you mention The NOTIFY events detected by upsmon and flagged as EXEC in upsmon.conf become events for upssched when NOTIFYCMD points to upssched. ​I would like that NOTIFYCMD points to upssched​. Thank you lots, Andrea ​ ___

Re: [Nut-upsuser] Help with Elite 800VA usb UPS

2017-07-03 Thread Andrea de Lutti
3 16:19:15 artu upssched-cmd: Unrecognized command: UPS dummy@artu battery is low I have tried so many commands, but always the same result... PS: this evening I will change the battery, I have some standby/cycle voltage declared by the manufacturer: should I use them? Thank you, Regards A

Re: [Nut-upsuser] Help with Elite 800VA usb UPS

2017-06-29 Thread Andrea de Lutti
> > , but when in battery test I have OL CAL status: it would be good to > have the result. > > "OL CAL" or "OB CAL"? If the UPS is powering the load from the battery > during calibration, it should report "OB CAL". The ONBATT handler in > NOTIFYCMD can check for CAL at that point. > > I don't

Re: [Nut-upsuser] Help with Elite 800VA usb UPS

2017-06-27 Thread Andrea de Lutti
the values of ups.conf? Or do I have to change it manually? Which would be the right procedure for changing the battery for calibrating NUT (over the manufacturer's suggestions)? Thank you lots, Andrea 2017-06-27 14:50 GMT+02:00 Charles Lepple <clep...@gmail.com>: > On Jun 26, 2017, a

Re: [Nut-upsuser] Help with Elite 800VA usb UPS

2017-06-26 Thread Andrea de Lutti
ail.com; Are there no warnings for battery test? Thank you, Andrea 2017-06-16 15:19 GMT+02:00 Andrea de Lutti <adelu...@gmail.com>: > Thanks mates, > as suggested I have added > > runtimecal = 240,100,720,50 > default.battery.voltage.low = 10.4 > default.

Re: [Nut-upsuser] Help with Elite 800VA usb UPS

2017-06-16 Thread Andrea de Lutti
a deep test. Is there a way to add a NOTIFYMSG value for the battery test? Thank you lots Andrea 2017-06-16 14:50 GMT+02:00 Charles Lepple <clep...@gmail.com>: > On Jun 16, 2017, at 2:20 AM, Andrea de Lutti <adelu...@gmail.com> wrote: > > Using 'guestimation' (low: -0.86

Re: [Nut-upsuser] Help with Elite 800VA usb UPS

2017-06-16 Thread Andrea de Lutti
, high: -1.08)! Initial battery charge undetermined Driver failed to start (exit status=1) What should I do? Thanks again, Andrea 2017-06-12 12:34 GMT+02:00 Manuel Wolfshant <wo...@nobugconsulting.ro>: > On 06/12/2017 12:56 PM, Andrea de Lutti wrote: > > > >> > I ha

Re: [Nut-upsuser] Help with Elite 800VA usb UPS

2017-06-14 Thread Andrea de Lutti
, high: -1.08)! Initial battery charge undetermined Driver failed to start (exit status=1) What should I do? Thanks again, Andrea 2017-06-12 17:34 GMT+02:00 Andrea de Lutti <adelu...@gmail.com>: > Thanks a lot, I will do it and keep you informed. > Best regards > > Andrea &g

Re: [Nut-upsuser] Help with Elite 800VA usb UPS

2017-06-12 Thread Andrea de Lutti
Thanks a lot, I will do it and keep you informed. Best regards Andrea 2017-06-12 12:34 GMT+02:00 Manuel Wolfshant <wo...@nobugconsulting.ro>: > On 06/12/2017 12:56 PM, Andrea de Lutti wrote: > > > >> > I have also successfully tested the battery... >> >

Re: [Nut-upsuser] Help with Elite 800VA usb UPS

2017-06-12 Thread Andrea de Lutti
of these tests, so that we can add a > more informed report about your device to our library > (http://networkupstools.org/ddl/). > ​Nice, I would like to test it, but if I don't have battery runtime value and / or battery charge, how may I test it correctly? I have seen also some strange va

Re: [Nut-upsuser] Help with Elite 800VA usb UPS

2017-06-11 Thread Andrea de Lutti
about /var/run/nut missing, but haven't find any solution I have also successfully tested the battery... upscmd -uadmin -pups Elit@artu test.battery.start.quick Thank you lots, Andrea 2017-06-11 5:31 GMT+02:00 Daniele Pezzini <hyo...@gmail.com>: > > Starting the driver with d

Re: [Nut-upsuser] Help with Elite 800VA usb UPS

2017-06-10 Thread Andrea de Lutti
> > hmm, apparently the UPS doesn't close the replies to our queries with > the expected CR and we (I) did not consider that case in nutdrv_qx -- > noted: > https://github.com/networkupstools/nut/issues/441 > > But blazer_usb, being less strict on the terminating CR of Q1 replies, > should work

Re: [Nut-upsuser] Help with Elite 800VA usb UPS

2017-06-09 Thread Andrea de Lutti
8299 qx_process_answer: short reply (input.voltage) 3.608313 Device not supported! 3.608319 Device not supported! ​It seems I am not so lucky... Thank you lots, Andrea​ ___ Nut-upsuser mailing list Nut-upsuser@lists.alioth.debian.org http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser

[Nut-upsuser] Help with Elite 800VA usb UPS

2017-06-07 Thread Andrea de Lutti
untime will not be calculated (runtimecal not set) Thank you lots, Andrea ___ Nut-upsuser mailing list Nut-upsuser@lists.alioth.debian.org http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser

Re: [Nut-upsuser] NUT HCL List

2011-11-18 Thread Andrea Soster
Arnaud Quette aquette.dev at gmail.com writes: 2011/6/13 Angela Williams angierfw at gmail.com Hi All! Hi Angela,  Just an update! The snmp driver seems quite happy with an APC AP9618 managment card in an APC Smart-UPS RT 5000 XL UPS. thanks for your report.I've just committed

Re: [Nut-upsuser] UPS Atlantis OnePower - VT12094S

2011-03-30 Thread Andrea
to start UPS drivers! Maybe i'm doing something wrong during compilation of the sources... Thanks in advice, Andrea 2011/3/30 Arjen de Korte nut+us...@de-korte.org: Citeren Andrea krog...@gmail.com: Exactly what benefit can i have using the new driver with this hack? If nothing changes i can

Re: [Nut-upsuser] UPS Atlantis OnePower - VT12094S

2011-03-29 Thread Andrea
drivers with this ups model feel free to contact me. Andrea 2011/3/29 Arjen de Korte nut+us...@de-korte.org: If you're able to build from sources, you can modify line 189 in drivers/blazer.c from        if (blazer_command(cmd, buf, sizeof(buf)) 47) { to        if (blazer_command(cmd, buf

[Nut-upsuser] UPS Atlantis OnePower - VT12094S

2011-03-28 Thread Andrea
detected [  VT12094S].  * Service upsdrv started What can I do to use the new, still supported and developed blazer driver? Many thanks Andrea ___ Nut-upsuser mailing list Nut-upsuser@lists.alioth.debian.org http://lists.alioth.debian.org/mailman

Re: [Nut-upsuser] UPS Atlantis OnePower - VT12094S

2011-03-28 Thread Andrea
Usage Type Data wMaxPacketSize 0x0008 1x 8 bytes bInterval 232 Device Status: 0x0002 (Bus Powered) Remote Wakeup Enabled Many thanks! Andrea 2011/3/28 Arjen de Korte nut+us...@de-korte.org Citeren Andrea krog...@gmail.com