Hello Wrenches,
Curious if anyone else is dealing with failed Schnieder XW PRO6848's this year?
In recent months I've had 2 DOA (one producing 180/360VAC; one charger had this
nasty building THD and ugly noise until it tripped out), and 2 fail after few
weeks in service. One charger just
Drake I think you’re right and they’re wrong, as long as the 200A bus is
protected by a 200A breaker, and as long as the Utility meter and utility
conductors remain 400
David
On Thu, Oct 12, 2023 at 5:06 PM Drake Chamberlin via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> We have
We have a design where the conductors will come out of a 400 A meter
base to a junction box. Splices in the box will allow for the PV to feed
the meter.
A maximum of 312 Amps can come from the inverters to feed the grid.
The loads on the existing main service are significantly less than
Wrenches
Anyone have experience/thoughts on the APSystems 2:1 single phase micros. I
don’t see much in the archives and the internet has some mixed reviews. I’m
mostly on the Enphase band wagon, but interested in knowing if APS could be
considered as a more cost efficient option for larger single
Does anyone have a link or picture of the ground anchor in question? I couldn’t find one. ThxJayOn Oct 12, 2023, at 7:07 AM, Dave Tedeyan via RE-wrenches wrote:Jeff, Thanks for the notes and things to look for from the field. I was not aware that there are two versions of their PowerJack out
Jeff,
Thanks for the notes and things to look for from the field. I was not aware
that there are two versions of their PowerJack out there, and I'll make
sure to get the newer one.
Kienan, I'm glad you have had luck with the cordless drill. I am leaning
towards that one, and it does have more
On that subject, what bits are people using to drill holes through
block/concrete (for 1" - 2" conduit)? We have been using some dry diamond
coring bits we buy online, but they don't seem to last. We have had them
break off at the weld. Wet coring seems overkill for the relatively few
holes we